We are adding on to an existing building that has a very extensive grounding system. Each cassion has a bare copper wire attached to the rebar, this is attached to the rebar in the slab and ties in to building steel in multiple locations. I have suggested to repeat this for the addition but they may want to save money and reduce it. The addition will be used the same as the original building. My reasoning is we paid for the original design and have not had any issues. Also, if we omit anything in concrete it would be very expensive or impossible to correct. Can anyone help with pro's and con's for this approach? I do not see a full design or study happening. Thanks Greco
Good Answers: 104
Re: Building Ground
09/13/2013 2:47 PM
Who's in charge of this project - you or 'they'?
Do you know why the existing building was grounded this way - what is the building used for?
Good Answers: 44
Re: Building Ground
09/13/2013 4:34 PM
Welded rebar structure, welded wire fabric reinforcement, reinforcing steel, and other miscellaneous connections should all be welded together providing electrical continuity.
Pro: Eliminates need for excessive and expensive copper, durable, long-lasting, essentially maintenance free.
Con: Also very expensive, time consuming, extra testing and inspection required.
Good Answers: 42
Re: Building Ground
09/14/2013 4:51 AM
See:IEEE-142/2007 ch.4.2.3 Concrete encased electrodes.
Our experience - in some of power station buildings-main building and auxiliary- it is as follows:
In all footing columns a single vertical steel rebar of minimum 1/2" diameter -depth underground of about 100 ft.[the most of power stations are located near sea shore and the soil is soft and the footing goes deep]is bounded to all the rebar by steel wire .At the top of footing this rebar is welded to the steel column foot screw .The connection between column is realized through the steel horizontal beam.
If there is a continue- all around- foundation it may be employed as horizontal link between footing groundings .The steel rebar for grounding segments have to be well welded-minimum 2" length of the welding.
The power station grounding grid is made of 4/0 stranded tined bare copper conductors. The connection to the foundation grounding through steel column by exothermic welding.
I would not recommend to use copper in concrete and not in connection with rebar.See[for instance]:
http://www.copper.org/applications/plumbing/techcorner/pdf/corrosion_nonferrous_metals_contact_concrete.pdf
Julius
Good Answers: 181
Re: Building Ground
09/14/2013 8:25 AM
Look up Ufer Earth on Google.
Good Answers: 140
Re: Building Ground
09/14/2013 9:47 AM
You are looking at this from the wrong end. You first need to clearly understand the power distribution system in the existing building and how the new area will be fed. once these things are known, a decision on how to ground the new area into the existing system can be made.
Anything other than this is only talking about methods of grounding the new area, not whether or not a given method is the correct choice.
Of course... this is IMHO.
Good Answers: 44
Re: Building Ground
09/16/2013 11:14 AM
The method of grounding may be paramount to keeping the noise down.
Having to necessitate design modifications afterwards adds cost.
All of the different grounding methods available in the NEC (BS/IS) meet the safety ground requirements, however not all meet other requirements. That is why there are so many variants.
Good Answers: 140
Re: Building Ground
09/16/2013 11:26 AM
Yes... and because there are so many variants on how the grounding system may be implemented, he must first understand the current power system and how the new area will mesh with the existing power system. Once he has come to that understanding, he can then identify the best methodology to use to ground the new system extensions.
Implementing any grounding methodology without knowing if what is to be implemented is proper for the current and new systems is not appropriate if you ask me.
To my way of thinking... a design should always start at the beginning and work towards the desired end state and not from the end state back to the beginning. But... hey, that is just to my way of thinking.
Good Answers: 44
Re: Building Ground
09/16/2013 3:55 PM
We are very sensitive to noise on our grounding system.
When we constructed our building, that noise floor came first during the planning phase.
When we found that the existing power did not meet our restrictions, we landed a new feeder designed to match our needs.
If we had tried to patch our system around what was delivered it would have ended up in excessive costs in workarounds.
Any new construction must still meet the wickets required by our quiet ground. If it doesn't/won't, the idea is canned.
Good Answers: 140
Re: Building Ground
09/16/2013 4:15 PM
Hey there CP... I just noticed you were talking about your building and not that of the OP.
You make my point for me. You, and any designer, needs to know his base requirements and go from there, which is what you appeared to do. There was no indication of the OP having done that nor does there appear to be any effort towards that as he mentioned a full review is not likely to take place. A possibly error prone approach if you ask me.
Good Answers: 44
Re: Building Ground
09/17/2013 11:14 AM
I cannot speak to the OP's project. I can only provide procedures based on my requirements (past/ongoing experience) and those of the IEEE, NEC, etc.
Since we don't really know the base requirements of the OP's issue (and very rarely do, since we are not the consultants, engineers, or project managers) then the entire purpose of this forum appears to be moot.
Re: Building Ground
09/16/2013 3:16 AM
One could always blow the dust off British Standard 7671, open it at page 1, and start reading.