Flow Hunting Problem

09/14/2013 1:02 AM

Dear Friends,

Greetings.

In one of the application involving very temp (40 deg c), a Fisher make V-300, 6", 300#, 1100 CV, rotary valve has been installed with Fisher's actuator, model no 1052-40. The valve is equipped with DVC-6020 positioner. The installation of the valve is such that the controller of the positioner (side mounted) is under high temp and as a result gets failed. We carried out an in-house modification and installed a smart Metso make 9102 positioner (on the front side with a gap of 30 mm from the body). The valve is tuned and put to service. However it is seen that at a delta opening of 0.1%, the flow gets varied by 30TPH (even though the opening after new arrangement is in the range similar to the old arrangement i.e. at 36%). We had cross checked the new arrangement and found that:

1. There is no back lash error.

2. Physically there is almost no movement in the valve on varying the input by 0.1%.

3. Flow readings confirmed by two transmitters.

May please help by informing, what can be the other causes of such a behavior.

__________________
Neeruvti
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Popular Science - Weaponology - New Member United Kingdom - Member - New Member

Join Date: May 2007
Location: Harlow England
Posts: 16512
Good Answers: 670
#1

Re: Flow hunting problem.

09/14/2013 2:43 AM

What is flowing?
What rate is it flowing at?
What shape of pipe work is it flowing through?
What is the temperature (you say40, then you say high temperature... these don't tally).
What range of flow are you trying to achieve?
What is the nominal position if the valve . E.G is it working nearly fully open, fully closed, in the middle.

You say the flow in hunting... over what range?
And over what timescale/frequency? That may tell you a lot.

When you say varying the input by 1%... do you mean 1 degree of angular position? Or if you mean 1%.... 1% of what?... my shoe size?

Simply adding a long straight pipe run filled with smaller pipes to linearise the flow may help.
How do you know the hunting is in the actual flow and not a function of the flow sensors or their position, installation,software etc.
I'm sure someone who knows more about this stuff will ask some more pertinent questions, but these few are a good start.
Whew... nuff for now... time for tea and toast.
Del

(There is no backlash error. Statements like that worry me)

__________________
health warning: These posts may contain traces of nut.
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: Flow hunting problem.

09/14/2013 10:37 AM

This sounds whacky to me. A 0.1% delta gives 30 TPH variation?? What is 30 TPH?

Tons per hour? Throughput per hour? Tadpoles per hour?

You must have one gigantic flow if 0.1% is 30 TPH?

Whacky, whacky, whacky by cracky!

Register to Reply
2
Guru

Join Date: Jul 2010
Posts: 669
Good Answers: 176
#3

Re: Flow Hunting Problem

09/14/2013 1:37 PM

Does the replacement Metso positioner have a remote mount position sensor so that the electronic controller box can be mounted away from the heat?

Your problem is not clear to me.

It appears that when you apply a demand/control signal of 36.0% (9.76mA) and change the demand/control signal by +/- 0.1%, 0.016mA, to 35.9% or 36.1%, then something happens, but what?

You say the valve does not change position, as indicated by the flowmeter. How did the flowrate change with the 0.1% test with the Fisher positioner?

You mention 30tph. Is 30tph the flow rate at 36%, or the change in florate with a 0.1% control signal change?

You need to state

- what readings (with eng units) you expect under specific conditions and why (that's what the Fisher did)

- what you actually get under those same conditions.

Hunting is a back and forth, oscillating movement. How does 'hunting' apply to this situation?

Register to Reply Good Answer (Score 2)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: Flow Hunting Problem

09/16/2013 3:26 AM

Fisher.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Associate

Join Date: Sep 2007
Location: Panipat, Haryana
Posts: 36
#5

Re: Flow Hunting Problem

09/16/2013 5:35 AM

Thanks a lot for the responses.

Well, answers to queries raised are as below:-

1. Range of Flow is 200 ton/hr.

2. The liquid is DTA-dowtherm-A (Therminol-VP), boiling point of 257 deg C, freezing point of 12 deg C.

3. Normally we need to maintain the flow of 140 TPH with a low-low set point of 111 TPH.

4. Temperature is of the order of 400 deg C.

5. The flow is through a horizontal pipe of 6" dia.

6. The installed valve is Fisher's V-300 (rotary type with 90 deg of rotation) with actuator type 1052-40 and CV of 1100.

7. The original positioner was DVC6020.

8. The valve generally opens around 36 to 37 % to get the flow.

Problem faced after installation of new positioner:-

1. The valve is kept in manual mode and the flow is around 150 TPH at opening of 36.3%.

2. When we reduce the opening to 36.2%, (linear output from DCS in terms of 4-20 ma, which is converted into angular movement at positioner side) the flow after sometimes drops to 125 TPH. This abnormality is what I am looking forward for your suggestions.

3. The valve is physically checked and position marked by marker and noticed that there is no abrupt physical movement in valve, so why does the flow (which is measured by two FT's) get varied.

4. Just for information, I get the same flow at 36% opening, which I use to get with Fisher positioner. But when I vary 0.1% in new case, there is large variation in flow, which is next to impossible but is being observed.

5. I need suggestions what can be the probable reasons of such a behavior.

__________________
Neeruvti
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6
In reply to #5

Re: Flow Hunting Problem

09/16/2013 8:57 AM

<...boiling point of 257 deg C...Temperature is of the order of 400 deg C...>

One of them could be that the liquid is boiling as it goes through the valve.

<...carried out an in-house modification and installed a smart Metso make 9102 positioner (on the front side with a gap of 30 mm from the body)...>

Was this modification approved by Fisher? If not, why not?

<...The valve is tuned and put to service....>

How odd. Normally, automatic control loops are tuned, and yet this loop is in manual. How abstruse.

How did the telephone call with Fisher go? Do tell.

How does the flow measuring device respond to boiling liquid passing through it? What sort of flowmeter is it?

If the flow low-low is so low, then why is the fluctuation of any immediate concern?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#7
In reply to #5

Re: Flow Hunting Problem

09/16/2013 9:13 AM

...and why is anyone twiddling with the valve position in any case?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#10
In reply to #5

Re: Flow Hunting Problem

09/16/2013 2:27 PM

I expect the downstream pressure to matter in this case. You appear to be far above the boiling point for this Dowtherm, and maybe you have misapplied the fluid to the situation. Make sure the valve positioner output 4-20 mA signal matches what is going on with the valve. You should also install a microphone and record various sounds that take place, and thereby gain some insight.

Dowtherm-A has a vapor pressure of approximately 10 bars (Engineer's Toolbox data) at 400 C. It sounds to me like a session at the chalk board is in order.

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#8

Re: Flow Hunting Problem

09/16/2013 9:24 AM

first problem: insufficient definition of the exact nature of what is the process involved, and the magnitude. 30 ton/hr (is that metric) = ~500 L/m, or is that English ton/hr = ~1000 L/m (assuming water density) and that is the peak-peak variance off the control point? Have you considered this could be the wrong type valve for your application? If the system pressure to the valve is high (300#), and downstream pressure is low, then perhaps your control position is not really 35% open, but is only 35% rotation, and the seat is not well cleared. IF turbulent conditions exist at the valve orifice, this could set up vibrations which could "chatter" the valve position.

Second problem: valve controller fails due to local heat. Here's your sign. If the controller is no good for the environment, then there's your problem. Change the environment, and the controller.

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Mar 2008
Location: Houston, Texas
Posts: 101
Good Answers: 6
#9

Re: Flow Hunting Problem

09/16/2013 9:56 AM

Something does not look right.

You say boiling point is 275 DEgc and normal temp is 400 Degc .

If the flow is showing a change of around 10% (140-125)/140 when you change the signal by 0.1 % something is not correct about your flow measurement.

If you are using an orifice plate you may be double extracting the square root .

Check the change in signal directly by connecting a manometer when you move the valve slightly.

__________________
If you don't know where you are going,you are bound to get there
Register to Reply
Guru

Join Date: Jul 2010
Posts: 669
Good Answers: 176
#11

Re: Flow Hunting Problem

09/17/2013 1:40 PM

While one might expect a constant flow when a positioner is in manual mode and the valve position is fixed, that's true only
- if all other flow conditions remain constant, and
- if you're not operating on a edge of the flash point at which liquid vaporizes to gas

PWSlack: <...boiling point of 257 deg C...Temperature is of the order of 400 deg C...>
One of them could be that the liquid is boiling as it goes through the valve.
James Stewart: Dowtherm-A has a vapor pressure of approximately 10 bars (Engineer's Toolbox data) at 400 C

I think these suggestions warrant serious consideration. I suspect that the temperature is higher than the operating pressure (or the operating pressure is lower than the temperature) needed to remain below the flash point.

Dowtherm's spec sheet gives the vapor pressure at 400°C as 10.62bara.

- What is the line pressure at the valve and at the flow meter?

- Are you recording the temperature and pressure so that you can track those with respect to the liquid's flash point?

- Is there some addtional load downstream that can come on-line which would reduce the line pressure which would drop the line pressure below flash point?

- Is there a diverter valve downstream that can alter the load conditions/line pressure?

Did this temp control loop have a history of working properly, or are you debugging a newly commissioned loop?

Register to Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#12
In reply to #11

Re: Flow Hunting Problem

09/17/2013 2:58 PM

Certainly all of these questions are pertinent. It makes a huge difference to flow transmitters if the flow is single liquid phase, or two phase vapor and liquid.

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Register to Reply 12 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Iris (2); James Stewart (3); lyn (1); NEERUVTI (1); PWSlack (3); srini (1); user-deleted-1105 (1)