1500A 3 Phase 4 Wire + Integral Housing Grounding Aluminium Busduct

09/17/2013 11:00 AM

Hi Guys,

Recently,i have this 1500A busduct install at a warehouse.This busduct runs from the LT Main SwitchBoard to 7th storey via electrical riser. Estimated length of the busduct is about 160m from the switchboard.(The busduct had been installed for a year)

After all the 20 tenant from 7th storey have move in(Supply of the each tenant is 60A 3phase via tap off unit from the busduct)it started to trip the protective device about twice per week.

The protective device that trip off is the Earth Fault Relay(set at 80A at 0.3s),we have change the Earth Fault relay and perform a secondary injection test to ensure the Earth fault relay is in working condition.

I refer the case to a Electrical Engineer who proposed to me that i should shut down the supply of the busduct and perform a insulation resistance test,he suspected that a high leakage between Phase & earth may occur.

I wonder if anyone out here have a similar cases and can advise me what should i do next.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: 1500A 3 Phase 4 wire + integral housing grounding Aluminium Busduct

09/17/2013 11:07 AM

Chase-out the location of the neutral/earth cross-over point, and eliminate the fault.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Anonymous Poster #1
#3
In reply to #1

Re: 1500A 3 Phase 4 wire + integral housing grounding Aluminium Busduct

09/17/2013 11:41 AM

Thanks..

Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#2

Re: 1500A 3 Phase 4 wire + integral housing grounding Aluminium Busduct

09/17/2013 11:21 AM

If there were no trips before the tenants moved in and now you're getting trips, I'd be looking at what equipment your tenants are using, maybe it'll be obvious which piece of equipment (old, dirty, no maintenance done, frayed wiring, etc.) might be "leaky".

If not you'll need a recording power analyzer that will allow you to capture the time, residual/neutral/harmonic currents, relay operations and whose equipment is starting and causing the trip. Good old observation will help too, like wiggling cord sets, sequential unplugging of equipment until the problem stops, etc.

There may be someone who has a particularly "noisy" or harmonic generating piece of equipment; sheathed resistance heating elements can also get leaky as the element insulation starts failing at a bend and leaking to the sheath. Let us know what you find.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Reply
Anonymous Poster #1
#4
In reply to #2

Re: 1500A 3 Phase 4 wire + integral housing grounding Aluminium Busduct

09/17/2013 11:41 AM

Thank you...

Reply
Guru

Join Date: Jun 2013
Location: Central Canada
Posts: 677
Good Answers: 28
#5

Re: 1500A 3 Phase 4 Wire + Integral Housing Grounding Aluminium Busduct

09/17/2013 7:04 PM

20 tenants trip an 80A fault relay, so each tenant theoretically faults 4A. Isolate the returns if you can, and find out what faults you are getting on which supply, or protect each tenant separately. Other than that, I go with PWSLACK for the GA. You should be able to use a current clamp meter to read the fault currents without disturbing any tenant suppy. You will need to measure each and every supply branch to determine the most likely tenant. Some are probably quite small and others are probably much worse. Can you inspect tenants to set down guidelines for maximum fault currents ? I once knew of a computer system that faulted almost every friday at 13:00 and it took personal monitoring to discover that friday was the staff tea day and the water kettle tripped the breaker. Do your tenants need your appoval before installing equipment ?

__________________
Smart as a post and twice as fast.
Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#6

Re: 1500A 3 Phase 4 Wire + Integral Housing Grounding Aluminium Busduct

09/17/2013 10:00 PM

I hardly think a E/L trip set at 80A is going to be operated multiple faults in 20 flats.

Shut the supply off and do IR tests on the bus-duct.

Remember to isolate each tap off point including the neutral from the bus otherwise you'll be paying for a lot of TV's and other household items you've blown up.

__________________
The reports of my death are greatly exaggerated.
Reply
Commentator

Join Date: May 2013
Posts: 86
Good Answers: 2
#7

Re: 1500A 3 Phase 4 Wire + Integral Housing Grounding Aluminium Busduct

09/18/2013 2:30 AM

You have not specified where the earth fault relay is provided. Is it in the incomer of the main panel or in the 1500 Amps busduct feeder. The location of the CT for Earthfault relay is important. In Indian context, the CT is placed in the neutral bus and this is fobbed of as earthfault protection. In your case I suspect this, as you have indicated that the problem started after the 7th floor got occupied. As the loads will mostly be single phase, the unbalance current in the neutral would have setoff the relay. If this is the case (most probably is, as the installation is tripping intermittently) you just need to increase the relay setting at the cost of sensitivity.

However if your REF protection of main incomer is operating (provided the system is properly designed), then you will need to investigate the problem more seriously and Insulation resistance test of the complete installation and/or physically verifying the system for any insulation failure should be undertaken. Again you have not mentioned which feeder, Main incomer or the 1500 Amps bus duct feeder, is tripping.

Please revert to the forum with your findings.

Reply
Anonymous Poster #1
#10
In reply to #7

Re: 1500A 3 Phase 4 Wire + Integral Housing Grounding Aluminium Busduct

09/18/2013 4:47 AM

Its the earth fault relay protecting the 1500A busduct...the incomer earth fault relay is set a 120A 0.5s

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#11
In reply to #10

Re: 1500A 3 Phase 4 Wire + Integral Housing Grounding Aluminium Busduct

09/18/2013 5:04 AM

The earth fault relay is insufficient to prevent electrocution of users. All it is doing is showing-up that there is a neutral-to-earth connection somewhere in the building.

It needs detection and correction before someone gets hurt/killed. Do it now/this morning/within the hour.

Please let the forum know what and where the fault was, as it will be a learning exercise for its readers.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply Score 1 for Good Answer
Anonymous Poster #1
#13
In reply to #11

Re: 1500A 3 Phase 4 Wire + Integral Housing Grounding Aluminium Busduct

09/18/2013 6:21 AM

The shut down is arrange on coming sunday...I will post the finding after the shut down.

Reply
Commentator

Join Date: May 2013
Posts: 86
Good Answers: 2
#12
In reply to #10

Re: 1500A 3 Phase 4 Wire + Integral Housing Grounding Aluminium Busduct

09/18/2013 6:14 AM

Then like I said earlier, the relay and CT are most probably wired to measure the neutral current. If you can reproduce the wiring schematic, we should be in a position to confirm.

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8

Re: 1500A 3 Phase 4 Wire + Integral Housing Grounding Aluminium Busduct

09/18/2013 3:11 AM

If in doubt, consult a qualified Electrician.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#9

Re: 1500A 3 Phase 4 Wire + Integral Housing Grounding Aluminium Busduct

09/18/2013 4:18 AM

If the installation has been installed and tested correctly, then the cause is two-fold:

  1. There is a connection between neutral and earth somewhere in the building
  2. There is too much reliance placed on a building-wide trip device whereas there needs to be a lower-rated one at each tenant's distribution board, so that a fault on one branch doesn't take out the whole building, thereby narking off the other tenants.

...so the installation cannot have been wired and tested to the latest edition of British Standard 7671. If it had been, then the fault would appear at an individual user's dis-board, making the cause easier to detect and rectify.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply Score 1 for Good Answer
Anonymous Poster #1
#14
In reply to #9

Re: 1500A 3 Phase 4 Wire + Integral Housing Grounding Aluminium Busduct

09/18/2013 6:31 AM

Hi Sir,

I believe the connection between the netural and earth happens along the busduct, reason is that the busduct conductor format as such (E, N, L3, L2, L1)...as such I believe is connected somewhere there.

we are arranging a shut down this coming sunday..will keep you posted on the findings.Thanks

Reply
Commentator

Join Date: May 2013
Posts: 86
Good Answers: 2
#15
In reply to #14

Re: 1500A 3 Phase 4 Wire + Integral Housing Grounding Aluminium Busduct

09/18/2013 8:57 AM

In standard, commercially available busducts as described by you in header, it is not possible to tie the neutral and earth conductors even accidentally along the length of the busduct. If at all it can happen, it will only be near or after the tap off point at each floor level. I can only wish you "Happy Hunting".

Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#16
In reply to #14

Re: 1500A 3 Phase 4 Wire + Integral Housing Grounding Aluminium Busduct

09/20/2013 9:04 AM

Check each taping at the floors to make sure there was no mistake by taping the 'E' as neutral for any of the floors or within the floor area. If the load is small, it might not trip, but as more faulty connections are activated, the accumulated current will trip the unit . This might be the reason it does not trip all the time.

Reply
Reply to Forum Thread 16 comments

"Almost" Good Answers: