09/24/2013 10:25 AM
I am testing ABB SAB-1 CT, 2.5L400, ratio 2000:5.
The ratio test result is good, with in 0.1% error, but when I tested for saturation the CT excitation knee point is about 200V. from the nameplate 2.5L400, I was expecting about 400V to saturate. am I missing something here?
appreciate your help
Re: CT Saturation
09/24/2013 2:14 PM
Yes.
Good Answers: 116
Re: CT Saturation
09/24/2013 5:43 PM
You will have to look at the ABB specification.
2.5L400 might mean 2.5% error at 400VA secondary load and 2000A primary.
I do not recall a standard which gives saturation voltage in a type code, but that does not prove much.
Re: CT Saturation
09/25/2013 8:41 AM
The spec is for under loaded condition, did you measure in loaded condition (loaded as spec) or open circuit. If measured open cct, it will saturate much earlier.
Sharing knowledge is one thing that defies basic arithmetic logic --- the more you share, the more you get!
Good Answers: 444
Re: CT Saturation
09/25/2013 11:30 AM
Never test a CT with its secondary open circuited!! You must have a burden or a short on its terminals, otherwise you risk deadly voltages and/or destruction of the device.
Here's a good reference with pictures for you to follow.