Does it Cost More to Generate at Leading or at Unity Power Factor

09/24/2013 10:08 AM

There are several articles on this site and others stating that it take more fuel to produce reactive power than it does when at unity power factor. Many of these articles talk about losses in the generator which are more than when the generator is at unity power factor. I have read many of these articles and I somewhat agree that reactive power factor will increase the generator current and therefore increase the generator losses. However, many of these articles also state that reactive power increases the torque angle of the generator which affects the prime mover. I really don't see how this can happen. In addition, none of these articles talk about the energy losses in the rotor which can be significant at over-excitation operation as opposed to being minimal energy loss at under-excitation. In may opinion, the MW output and the torque angle are constant for a given output of a prime mover. The losses of the generator will increase at either under-excitation or over-excitation due to the increased current but when the losses of the excitation system are included, the overall effect will be that under-excitation operation of the generator will be the most economical operation of the generator over unity power or over-excitation operation. Is this a correct assumption?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Does it Cost More to Generate at Leading or at Unity Power Factor

09/24/2013 10:23 AM

The losses in the cabling increase with lower-than-unity power factor. As utility companies incur additional costs for this that don't appear as kWh, the temptation is to impose a tariff that encourages the power user to operate close to unity power factor.

Power factor correction is one of CR4's more common topics, which has been covered ad nauseam before. Try entering "power factor correction" into the "Search all of CR4" box on the right→.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#2

Re: Does it Cost More to Generate at Leading or at Unity Power Factor

09/24/2013 11:13 AM

DF is asking about fuel savings not power factor correction. I agree with his overall premise which I'll simplify as "...all other things being equal, since the rotor draws less excitation current when the generator operates underexcited, the losses are lower than operation at the same load and with the numerically identical but overexcited power factor ...".

Sure, but it ignores the typical operational constraints about operating underexcited, which can lead to machine damage, system instability, loss of voltage control, and loss of synchronization.

So while technically correct, operationally it is fraught with problems that can cause a lot more additional costs than the potential fuel savings.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Score 1 for Good Answer
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#3

Re: Does it Cost More to Generate at Leading or at Unity Power Factor

09/24/2013 1:23 PM

Ooops! I must need new glasses, the title of the question has to do with going from unity pf to underexcited but the post said that it was a comparison between same pf over/underexcited.

The answer is a bit different under when going from unity to over/underexcited primarily because the for constant MVA the MW are greatest at unity, therefore more fuel is consumed to supply the higher MW. Conversely as we move the pf away from unity the MW goes down so less fuel is consumed.

The magnitude of the current, and therefore the losses, does not change, except for the DC power consumed in the field which does go down as the machine gets more underexcited.

In theory the changes in reactive power have no effect on the real power, and changes in the fuel consumption have no effect on the reactive power. In real life they are slightly interrelated since these are not ideal machines, and the changes have to do with the fact that as the excitation changes so does the terminal voltage and its effect on load current.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#4

Re: Does it Cost More to Generate at Leading or at Unity Power Factor

09/24/2013 6:48 PM

You discuss cost of generation.

When the power factor goes leading, the watts that a synchronous generator can absorb drops like a stone. With zero excitation current, the power to push it out of sync is only about 30% rated - and there is zero stability margin for sudden load changes.

It is not economic to operate a plant at 30% rating. In fact, system operators have to pay generators a premium to operate part load, because they would get less kW earning less at higher unit cost otherwise.

Part-load operation is kept to the minimum needed to cover sudden loss of a generator or generating station without too much frequency drop. Grid Systems are managed mostly by skillful adjustment of number /size of generators (on-line, at full rating) at 15 minute intervals according to predicted load, modified by reality.

You have forgotten the "engine". Diesels lose ~10% efficiency at 75% load. Gas turbines lose efficiency seriously below full load, say 20% drop at 80% load for free turbine type, worse for single shaft. I have little knowledge on steam turbines, but I think they may be similar to diesel figure. Any serious Grid electric generator, 30MW up has >=98.5% efficiency, so its loss variations are minor compared to engine efficiency.

Finally, systems must have that lagging generator output to magnetise all the transformers and motors in the system.

Register to Reply
2
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#5
In reply to #4

Re: Does it Cost More to Generate at Leading or at Unity Power Factor

09/24/2013 10:34 PM

67,

"You discuss cost of generation." Actually the discussion was about the cost of fuel, the cost of generation has many other components such as maintenance, labor, taxes, life of plant, market conditions, etc. which were not part of this hypothetical discussion.

"...When the power factor goes leading, the watts that a synchronous generator can absorb drops like a stone..." Generators push watts out based on the amount of HP pushed in by the prime mover and the strength of the net magnetic field coupling the rotor to the stator. If the net MMF falls below the minimum excitation level the effect is the same as a hydraulic coupling losing its fluid.

"...With zero excitation current, the power to push it out of sync is only about 30% rated - and there is zero stability margin for sudden load changes..." the discussion was not about operating a generator while reducing the excitation below safe operating limits. At zero excitation current it is likely that most units would have slipped poles long before zero was reached. Stability margin is dependent upon system conditions and where the generator is installed in the grid relative to large load centers and other generation.

"...It is not economic to operate a plant at 30% rating..." The economics depend upon the type of unit, some plants are specifically designed to operate efficiently at partial load with a heat rate that is not too far from the most efficient loading point. A good example of this is a combined cycle plant where a Heat Recovery Steam Generator (HRSG) recovers the heat from the turbine exhaust, yielding overall cycle efficiencies in excess of 60%.

"...In fact, system operators have to pay generators a premium to operate part load, because they would get less kW earning less at higher unit cost otherwise..." Not necessarily, the rates are negotiated in real time if system conditions warrant. There are also times when it is more economic to run a plant at partial load rather than pay the shutdown/startup fuel costs that generate no revenue, it's better sell the energy at an off-market rate then eat the fuel costs entirely.

"...Part-load operation is kept to the minimum needed to cover sudden loss of a generator or generating station without too much frequency drop...." It 's the other way around, a partially loaded generator is in a better position to respond to sudden unplanned load increases due to the loss of another generator or transmission circuit. Stability problems typically occur when there is no reserve; i.e., every bit of generation is running at its maximum capability.

"...Grid Systems are managed mostly by skillful adjustment of number /size of generators (on-line, at full rating) at 15 minute intervals according to predicted load, modified by reality..." Actually the systems are highly automated and run according to set dispatch rules, with human input for variances as needed. The 15 minute interval is the balancing period to determine if it is necessary to incrementally change the internal frequency to accommodate the dispatch/wheeling requirements as set by the SO's (System Operators) and TSO's (Transmission System Operators)

"...You have forgotten the "engine". Diesels lose ~10% efficiency at 75% load. Gas turbines lose efficiency seriously below full load, say 20% drop at 80% load for free turbine type, worse for single shaft..." This is one of the reasons why cost of fuel is just one piece of the the economics of generation puzzle. Combined cycle plants with HRSGs are one way to capture the waste heat and increase the overall cycle efficiency.

"...I have little knowledge on steam turbines, but I think they may be similar to diesel figure..." They're not, steam turbines are relatively high efficiency in converting steam into shaft power, subject to the operating limitations of the particular design. Most of the inefficiency in a conventional fossil fuel plant goes off to the boiler and combustion processes, with the overall efficiency limited to the Carnot Cycle.

"...Any serious Grid electric generator, 30MW up has >=98.5% efficiency, so its loss variations are minor compared to engine efficiency..." True, the generator and transformer are the most efficient components in a power plant, they have a combined efficiency of 94-95% and their max efficiency point is below the combined rating of the two.

"...Finally, systems must have that lagging generator output to magnetise all the transformers and motors in the system..." This is only true when the load is only inductive, most likely in small isolated systems. As an example, very long transmission overhead lines appear capacitive (the Ferranti Effect), as do systems that have large underground cable installations, plus many systems now have switchable reactors and capacitor banks as part of their overall VAR/voltage control strategies.

Modern grid connected (non-diesel) generators are fully capable of leading (underexcited) power factor operation, and in order to maintain the desired voltage profile (which varies with time of day) most systems have a mix of generator leading and lagging power factors. There are extremes when underexcited operation becomes a stability issue, either during lightly loaded conditions at night when many factories and businesses are closed and the system voltage profile starts rising at most busses, or during peak demand periods when every bit of voltage support is required.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Good Answer (Score 2)
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#12
In reply to #5

Re: Does it Cost More to Generate at Leading or at Unity Power Factor

09/26/2013 8:27 AM

The OP had Cost in the title, Fuel in the middle and Economical at the end. He seemed to me to have already convinced himself, correctly, that between equal leading and lagging power factors at the same real power, generator losses are least for leading.

So I tried to briefly mention the constraints that require synchronous generators to operate off the loss optimum, without "ifs, buts and depends" , and thank you for the erudite additions, for which I give you a Good Answer.

The "30% load" was a clumsy attempt to bring in stability limits. But I note the OP's "In m(a)y opinion, the MW output and the torque angle are constant for a given output of a prime mover." which seems an error because rotor angle/torque increases with weakening field, but was not commented upon.

I take issue with your comment on "skillful adjustment", I never meant "not automated". Are you really saying that skill is in hardware and silicon integrated circuits, not in designers, programmers, consultants, weather forecasters, market analysts etc. who have a hand in prediction and procedures?

67model

Register to Reply
Power-User
Engineering Fields - Electrical Engineering - New Member Engineering Fields - Power Engineering - New Member

Join Date: Mar 2012
Location: the sandbox
Posts: 341
Good Answers: 6
#6

Re: Does it Cost More to Generate at Leading or at Unity Power Factor

09/25/2013 12:56 AM

RAMconsult said:

""...Finally, systems must have that lagging generator output to magnetise all the transformers and motors in the system..." This is only true when the load is only inductive, most likely in small isolated systems. As an example, very long transmission overhead lines appear capacitive (the Ferranti Effect), as do systems that have large underground cable installations, plus many systems now have switchable reactors and capacitor banks as part of their overall VAR/voltage control strategies."

Ferranti effect is a long transmission line effect, I have never seen it is distribution systems, where the loads are almost always inductive.

__________________
BSEE but always learning
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#8
In reply to #6

Re: Does it Cost More to Generate at Leading or at Unity Power Factor

09/25/2013 1:50 PM

My guess is that you're more familiar with small local generation and that you've never been to any built up city like NY, LA, Boston, etc. where most of the subtransmission/distribution is underground cable which is highly capacitive, but you're right, on the customer side of the meter the loads tend to be net inductive.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#7

Re: Does it Cost More to Generate at Leading or at Unity Power Factor

09/25/2013 6:14 AM

It Costs more at leading P.F.

That is if you want to generate the same kW or MW ! But the issue is how do you do that? At leading P.F., there will be problems of stability. usually, you use this method to produce compensating kVARs on a grid and not kWatts. Tricky business if you are not in the business...

Logically, 1 kVA = 1kW is the minimum cost at P.F.=1. At leading or Lagging P.F. you are producing kW but consuming (or producing) something else in addition.How much more, ...?

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#9
In reply to #7

Re: Does it Cost More to Generate at Leading or at Unity Power Factor

09/25/2013 2:09 PM

The "something else" is the reactive current, but that does not come out of the fuel, it comes out of the magnetic field. No additional fuel is used except for the power to run the excitation system.

As long as you hold the real power constant you add VARs by adjusting the excitation level, so if you measure the current at 0.9 pf overexcited it will be exactly the same as 0.9pf underexcited, therefore the I²R losses are identical, except for the the losses in the excitation system. This assumes that the terminal voltage doesn't change, an unrealistic assumption in the real world, but in theory that's how it works.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#10
In reply to #9

Re: Does it Cost More to Generate at Leading or at Unity Power Factor

09/25/2013 2:31 PM

Point Taken.

Since the P.F. depends on the load connected to the Generator, and since the reactive power is supplied to the load, and then there are losses on the transmission lines if the P.F. is lagging at the consumer point, surely, that is going to cost the generating utility.

Now, I think that the OP is trying to say that maybe if the generator is made to produce under a leading P.F. setting, in order to still supply the same Kw power, will this be cheaper for the generating unit than just correcting the load end to unity P.F. only?

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#11
In reply to #10

Re: Does it Cost More to Generate at Leading or at Unity Power Factor

09/25/2013 9:45 PM

Well, it's really a theoretical "what-if" question, but it has validity since the excitation system is a parasitic loss and someone has to pay for that DC power consumption, and it's not small.

A midsize 500 MVA generator uses about 0.5% of its output power to provide the full load field current, that's 2.5 MW!!! 1,000Vdc x 2,500Adc is a nontrivial amount of power that has to be produced from somewhere and controlled by the excitation system.

So OP's question takes on a new meaning, after all if we can cut that 2.5MW down to 1.25MW by running underexcited, why not do it? Let's see, 1,250kW x 1 hr = 1,250kWh, at 0.30 $/kWh that's 375 bucks per hour x 24hrs = $9,000/day saved. The difference in fuel cost adds up quickly.

In reality we can't get a 2:1 turndown or we'd likely slip poles so the number is somewhat less, and it does go down kind of linearly with the MVA load on the generator. So yes, if the pf at the machine's terminal goes from overexcited towards unity the amount of energy going into the field goes down too.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Power-User

Join Date: Mar 2010
Location: BHOPAL, INDIA
Posts: 201
Good Answers: 20
#13

Re: Does it Cost More to Generate at Leading or at Unity Power Factor

09/27/2013 10:50 AM

Here I give a typical capability diagram of Turbo-generator. On under excited oparating conditions the limit could be minimum excitation (or in other terms load angle) which affects its steady state stability (with modern solid state voltage regulators the theoretical transient limit shifts from delta equal to 90 degrees to 135 degrees. But there is another aspect which needs to be consider. This is end zone heating of the generator. Under leading power factor operation of the generator, the flux distribution changes (the armature reaction is magnetizing) and it results in over heating of the end structure (generator casing, core clamping plate etc.). Therefore generator manufactures put a limit on the MVA that is permitted at different leading .power factor. So one should not assume that any amount of MVA could be drawn under leading power factor condition. In most of the cases, this end zone heating limit is more critical than stability limit

Register to Reply
Register to Reply 13 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

1capybara (1); 67model (2); LAA_Lucke (2); pcchatur (1); PWSlack (1); RAMConsult (6)