Load Calculation for Floor Box

09/24/2013 7:55 AM

3 compartment floor box, one with 6 nos single sockets, my doubt is for load calculation do we consider 400w for each single socket ie. 6*400=2400w? & same with 3 nos dual sockets ie 3*400w=1200w?. please clarify

The image shows 3 compartment floor box with 3 dual socket equals to 6 nos single socket.

__________________
Every minute is a learning curve.
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Load calculation for floor box

09/24/2013 8:50 AM

The loading on the box will be limited by the wiring and its protective devices that form the fixed installation in the building.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: Load calculation for floor box

09/24/2013 9:03 AM

Ask a local electrician: hire a local electrician: consult local code book:

Google "electrical load calculations"

How to Search the Internet

Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#3

Re: Load Calculation for Floor Box

09/24/2013 11:29 PM

Apart from connected load factors like diversity(simultaneous load)too should be considered to arrive at running load.

__________________
pnaban
Register to Reply
Active Contributor

Join Date: Oct 2010
Location: Hyd - IND
Posts: 21
#4

Re: Load Calculation for Floor Box

09/25/2013 1:44 AM

you have to consider 2 Nos. of single sockets in each compartment for load calculations if the load is continuous. if your load is intermident you can consider half of the value of above said.

__________________
Shaju Khan
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#5
In reply to #4

Re: Load Calculation for Floor Box

09/25/2013 2:14 AM

Should we consider load characteristics like continuous,intermittent,periodical, fluctuating too?.

__________________
pnaban
Register to Reply
Active Contributor

Join Date: Oct 2010
Location: Hyd - IND
Posts: 21
#6
In reply to #5

Re: Load Calculation for Floor Box

09/25/2013 5:15 AM

yes we have to consider continuous & intermident load.

__________________
Shaju Khan
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#7
In reply to #6

Re: Load Calculation for Floor Box

09/25/2013 6:44 AM

I remember BS7671 or "Onsite guide" describing cable sizing for a fluctuating load(electric lift or elevator).

__________________
pnaban
Register to Reply
Associate

Join Date: Jul 2013
Location: Middle East [Bahrain]
Posts: 33
#10
In reply to #4

Re: Load Calculation for Floor Box

09/26/2013 1:05 AM

thanks shajahan

__________________
Every minute is a learning curve.
Register to Reply
Power-User
Engineering Fields - Electrical Engineering - New Member Engineering Fields - Power Engineering - New Member

Join Date: Mar 2012
Location: the sandbox
Posts: 341
Good Answers: 6
#8

Re: Load Calculation for Floor Box

09/26/2013 12:19 AM

It depends what code your using.

For ex., in US code the load is 3 x 180w =540w.

BS7671 says you consider maximum possible connected load, which would be limited by wire and breaker size.

If each of these floor boxes is on a 15A/1p breaker,

maximum load could be (for ex.) 15A x 230v x .8= 2760w on a 2.5mm^2 wiring system.

And then adjust for diversity, voltage drop, temperature, conduit fill.....etc.

__________________
BSEE but always learning
Register to Reply
Active Contributor

Join Date: Oct 2010
Location: Hyd - IND
Posts: 21
#9
In reply to #8

Re: Load Calculation for Floor Box

09/26/2013 12:31 AM

wheather a 2 wire of 2.5sq.mm will manage to flow a 15A current?

__________________
Shaju Khan
Register to Reply
Associate

Join Date: Jul 2013
Location: Middle East [Bahrain]
Posts: 33
#11
In reply to #8

Re: Load Calculation for Floor Box

09/26/2013 1:05 AM

Thanks 1capybara

__________________
Every minute is a learning curve.
Register to Reply
Power-User
Engineering Fields - Electrical Engineering - New Member Engineering Fields - Power Engineering - New Member

Join Date: Mar 2012
Location: the sandbox
Posts: 341
Good Answers: 6
#12

Re: Load Calculation for Floor Box

09/26/2013 1:29 AM

"wheather a 2 wire of 2.5sq.mm will manage to flow a 15A current?"

i dont have BS7671 in front of me, but yes, it can.

using BS7671 or IS equivalent is an important skill you must practice please,

you will find it constantly helpful in your career

__________________
BSEE but always learning
Register to Reply