3 compartment floor box, one with 6 nos single sockets, my doubt is for load calculation do we consider 400w for each single socket ie. 6*400=2400w? & same with 3 nos dual sockets ie 3*400w=1200w?. please clarify
The image shows 3 compartment floor box with 3 dual socket equals to 6 nos single socket.
Every minute is a learning curve.
Re: Load calculation for floor box
09/24/2013 8:50 AM
The loading on the box will be limited by the wiring and its protective devices that form the fixed installation in the building.
09/24/2013 9:03 AM
Ask a local electrician: hire a local electrician: consult local code book:
Google "electrical load calculations"
How to Search the Internet
Re: Load Calculation for Floor Box
09/24/2013 11:29 PM
Apart from connected load factors like diversity(simultaneous load)too should be considered to arrive at running load.
pnaban
09/25/2013 1:44 AM
you have to consider 2 Nos. of single sockets in each compartment for load calculations if the load is continuous. if your load is intermident you can consider half of the value of above said.
Shaju Khan
09/25/2013 2:14 AM
Should we consider load characteristics like continuous,intermittent,periodical, fluctuating too?.
pnaban
09/25/2013 5:15 AM
yes we have to consider continuous & intermident load.
Shaju Khan
09/25/2013 6:44 AM
I remember BS7671 or "Onsite guide" describing cable sizing for a fluctuating load(electric lift or elevator).
pnaban
09/26/2013 1:05 AM
thanks shajahan
Engineering Fields - Electrical Engineering - New Member Engineering Fields - Power Engineering - New Member
09/26/2013 12:19 AM
It depends what code your using.
For ex., in US code the load is 3 x 180w =540w.
BS7671 says you consider maximum possible connected load, which would be limited by wire and breaker size.
If each of these floor boxes is on a 15A/1p breaker,
maximum load could be (for ex.) 15A x 230v x .8= 2760w on a 2.5mm^2 wiring system.
And then adjust for diversity, voltage drop, temperature, conduit fill.....etc.
BSEE but always learning
09/26/2013 12:31 AM
wheather a 2 wire of 2.5sq.mm will manage to flow a 15A current?
Shaju Khan
09/26/2013 1:05 AM
Thanks 1capybara
09/26/2013 1:29 AM
"wheather a 2 wire of 2.5sq.mm will manage to flow a 15A current?"
i dont have BS7671 in front of me, but yes, it can.
using BS7671 or IS equivalent is an important skill you must practice please,
you will find it constantly helpful in your career