Unearthing of VFD Transformer Star Point

09/24/2013 7:53 AM

A 300 KW, 690Volt six pulse VFD had been provided with a Dry type input transformer of 800 KVA, 6600 Volts / 690 Volts, the primary being Delta and Secondary Star connected. Here the star point is left unearthed. Why is it so? Can any one suggest the possible reasons?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Unearthing of VFD transformer star point

09/24/2013 8:51 AM

Not without knowing the use of the building in which it is installed, no.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User
Engineering Fields - Electrical Engineering - New Member Engineering Fields - Power Engineering - New Member

Join Date: Mar 2012
Location: the sandbox
Posts: 341
Good Answers: 6
#2

Re: Unearthing of VFD transformer star point

09/24/2013 9:01 AM

if the VFD requires a neutral, how do you intend to provide its neutral?

from this floating star point? this is - imho - installer error.

__________________
BSEE but always learning
Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#7
In reply to #2

Re: Unearthing of VFD transformer star point

09/25/2013 5:32 AM

Yes he can use the star point as neutral! it is the neutral point here!

(That is if the VFD requires a Neutral ! not necessary so).

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: Unearthing of VFD transformer star point

09/24/2013 9:09 AM

Is there a qualified Electrician dealing with this locally or is it all home-brew stuff?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
5
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#4

Re: Unearthing of VFD transformer star point

09/24/2013 9:49 AM

Generally it would be a bad idea to leave the star point unearthed. You want the phase-to-earth voltage to be as low as possible to give any common mode noise an easy path to earth. In addition, most VFD front-ends include MOVs and/or common mode capacitors that come from the factory with an earth reference connection in star form. If your secondary of the transformer is floating, those devices attempt to become the earthing point of the star for the entire transformer, so the first fault burns them out. Most VFD mfrs will give you instructions on how to remove the earthing connection, which prevents that, but leaves the drive exposed to common mode noise.

But without knowing all of the details of what is involved in your installation, we don't know if there was some legitimate reason for doing this. Sometimes, for instance if there is a neutral resistance connection elsewhere to limit earth fault energy, this must be done. We just don't know.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 5)
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#6
In reply to #4

Re: Unearthing of VFD transformer star point

09/25/2013 2:31 AM

GA.

We used to use ungrounded Y secondaries with DC drives to allow for fault tolerance of one phase to ground. We originally provided some rather simple pilot lights Connected referenced to ground, so if a phase did ground 2 lights where bright and one dim.

Code here does not allow that any more. It has a strong preference for hard grounding -especially in residential and commercial applications. In industrial applications where full time electrical personnel are present they may opt for high resistance grounding, with ground fault detection and ground fault protection systems. This allows for orderly planned shutdown to clear the fault - imagine a molten ladle of steel - you tolerate the fault until it is safe to shut down the line.

As you state, the manufacturer may give you the option of removing the Y connected protection.

Register to Reply
Power-User
Engineering Fields - Electrical Engineering - New Member Engineering Fields - Power Engineering - New Member

Join Date: Mar 2012
Location: the sandbox
Posts: 341
Good Answers: 6
#5

Re: Unearthing of VFD Transformer Star Point

09/25/2013 12:11 AM

And if the neutral isnt earthed elsewhere its voltage will float because it isnt referenced to earth

__________________
BSEE but always learning
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8

Re: Unearthing of VFD Transformer Star Point

03/21/2024 8:23 AM
  • Are there any drawings?
  • Are there commissioning records?
  • Are there periodic inspection and testing records?

Who did them?

Those are the people to ask.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply