Hello Every One - Question About Transformers

09/25/2013 12:25 AM

hi guys... i always have a doubt regarding the rating of transformer .. why it is always is KVA instead of watts ..

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User
Engineering Fields - Electrical Engineering - New Member Engineering Fields - Power Engineering - New Member

Join Date: Mar 2012
Location: the sandbox
Posts: 341
Good Answers: 6
#1

Re: hello every one

09/25/2013 12:33 AM

because a power source (xfmr or genset) supplies KVA, a load uses KW, the diffference is the reactive power (in general, but this is a general question)

__________________
BSEE but always learning
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: hello every one

09/25/2013 3:39 AM

There shouldn't be any doubt, because transformers are always rated in kVA. It's got something to do with the maximum current flowing in the windings. For more information, the transformer class is down the corridor, third door on the right. No, not that one, the next one. Hurry up because the lecturer is due any minute. Oh, that's all right. Sort the course fees out afterwards. Enjoy the class.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Participant

Join Date: Sep 2013
Posts: 2
#3

Re: hello every one

09/25/2013 4:16 AM

Because Transformer is independent to power factor, transformer is distributing power by Kilo-volt-ampere so we can't tell in kw, unless calculate with pf.

Reply Off Topic (Score 4)
4
Guru

Join Date: Mar 2011
Location: Sebastopol, California
Posts: 1205
Good Answers: 54
#4

Re: Hello Every One - Question About Transformers

09/25/2013 10:44 PM

A Transformer is not a load, so it is not rated in Watts, which is a measure of power consumption. A transformer is a transmission device and so it's rating is based on the amount of power it can transfer. That power transfer is measured in kVA. The transmission of power in a transformer has two limits, the breakdown voltage of the insulation of the windings and the current carrying capacity of the windings. kVA sets the limit of both. Inductive loads and high-current loads put different stresses on the transmission circuit. So, by using a rating that limits both the current and the voltage, a safe opperating range can be applied with one number.

__________________
Most people are mostly good most of the time.
Reply Good Answer (Score 4)
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#6
In reply to #4

Re: Hello Every One - Question About Transformers

09/26/2013 8:53 AM

A good answer, but the voltage applied to the common type of transformer with a magnetic core is limited by magnetic saturation before insulation limits.

Reply
Guru

Join Date: Mar 2011
Location: Sebastopol, California
Posts: 1205
Good Answers: 54
#7
In reply to #6

Re: Hello Every One - Question About Transformers

09/26/2013 8:57 AM

This is true, but not all transmission devices are magnetic, I should have made that more clear.

__________________
Most people are mostly good most of the time.
Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#5

Re: Hello Every One - Question About Transformers

09/26/2013 4:35 AM

If the load is purely resistive, the KVA is equal to the watts.Since the designer of the transformer does not know the application or power factor of the load,it is rated for KVA, which considers the power factor to be 100%.
Actual wattage will depend on the type of load applied to the transformer.
Google power factor for more information.

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Reply Score 1 for Good Answer
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#8

Re: Hello Every One - Question About Transformers

09/26/2013 11:16 AM

The Transformers I think you mean are alternating voltage and current devices.

This means you could load them with an (almost) no-loss capacitor or inductor which would draw their maximum rated current while drawing negligible net watts power over a cycle.

But that would still heat up the transformer windings to their limit.

Giving transformers a Volts x Amps VA rating is a convenient way of specifying how much power they can supply and gives an immediate idea of how big or costly they are.

A "system overall plan" drawing can just have voltage values at each level and KVA ratings for transformers between levels to reduce superfluous distraction.

It is rather like saying you need a "40 ton" truck for a job, without the speed or volume/length/height carried - it still encapsulates the need usefully.

Reply
Power-User

Join Date: Jan 2008
Location: kuwait
Posts: 132
Good Answers: 2
#9

Re: Hello Every One - Question About Transformers

09/28/2013 4:15 AM

copper loss of transfer depend on current and iron loss on voltage.hence,total transformer loss depend on volt-ampere (VA) and not on phase angle between

voltage and current .it is independent of load power fector.that,s why rating of transformer is in kva not in kw.

__________________
love4everyone
Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#10
In reply to #9

Re: Hello Every One - Question About Transformers

09/28/2013 8:34 AM

Please do research before giving invalid information.

The following reiterates what I stated above.

http://www.differencebetween.net/science/difference-between-kva-and-kw/

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Reply
2
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#11

Re: Hello Every One - Question About Transformers

09/28/2013 9:09 AM

A primer on KVA,and KW.

1:KVA is apparent power.2:KW is real power, or power used to perform actual work.3.In a Direct current Circuit, KVA is equal to KW.4.In an AC circuit, they are seldom equal,and the Power Factor must be considered.5.The power factor is a measure of the phase relationship between current and voltage.6.If you have a Power Factor of 80%,then 20% of the KVA is basically being used to maintain the magnetic field of the inductive load, and is not performing any actual "work". However, the current must still be supplied regardless, and this means that everything supplying the circuit must be capable of supplying and carrying this (non working) current.Generators must be large enough to handle this inductive load, transformers must also be sufficiently large.This means larger generators, transformers,and conductors.A typical power meter can only measure the KW of a circuit,which in a normal house situation is nearly 100%. The small difference is usually corrected by pole mounted capacitors at a central distribution point for an entire neighborhood.Utility companies charge industrial users for KW and KVAR,and low power factors are penalized by a higher rate,because of the extra facilities required to generate and carry this extra burden,which does not produce any actual work.Industries will install large capacitors to bring the power factor closer to unity,to minimize the charge.KVAR is Killovolt Amps Reactive,which means the current is lagging the voltage.A leading current (KVAC) is rarely seen.So in effect, a transformer and generators are rated in KVA, instead of KW because the designers do not know what the current/voltage relationship will be in the application.The KVA will equal the KW if the circuit is purely resistive, such as a resistive heater load.If you add an inductive load, such as an A/C motor,the Power Factor of the motor must be considered.The reactive current is merely circulating without producing any real "work",but it must still be there.Now ..Clear as mud?

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Reply Good Answer (Score 2)
Reply to Forum Thread 11 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

1capybara (1); 67model (2); Deefburger (2); deepanpuliyur (1); HiTekRedNek (3); PWSlack (1); sohail0110 (1)

Previous in Forum: CT Saturation   Next in Forum: UPS Battery to Install in MCC/Distribution Board Room

Advertisement