Anonymous Poster #1

CT Saturation

09/26/2013 1:52 PM

Thanks for the reply

on 2.5L400

is the 400 is the voltage or VA?

when we calculate the Ipedance, why we use it as a voltage

V = IR

assume during the fault the current will be expected 20 times higher than the normal CT operation, i.e. current during fault on the secondary (20 x 5A) = 100A

Then to find the max Burden, R=V/I = 400V/100A = 4 ohms

in this case we use 400 as a vault not as a VA.

and I was assuming 400V is the saturation voltage

Is this wrong?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: CT saturation

09/26/2013 2:02 PM

What reply? You are anonymous.

Tips for Posting on CR4:

Do your own homework. CR4 is not a homework cheat site; however, if you have questions about understanding concepts or how a portion of a problem is derived, these types of questions will be accepted.

Do your own homework. CR4 is not a homework cheat site; however, if you have questions about understanding concepts or how a portion of a problem is derived, these types of questions will be accepted.

Reply
2
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#2

Re: CT Saturation

09/28/2013 7:59 PM

I told your previous anonymous avatar that I did not know what the L400 means.

If it was me, I would look in the manuals, drawings and data archive of the plant [Schedule of equipment, Data Sheets??] to see if there is any information about the item. There might be a test magnetisation curve, which would be compared with periodic tests in service.

If this fails, speak to the local Brown Boveri dealer, tell him you have this CT, give him all type numbers and serial numbers which are marked on it and ask him if he recognises the 2.5L400 and knows what it means and if he could provide more data.

You now write of protection service.....in European practise, protection CTs are usually specified as 5P10 or 5P20. P means protection, while 5 means 5% error at the number of times rated continuous current which follows the P.

http://en.wikipedia.org/wiki/Current_transformer

gives an example of a current transfo with 2.5L400 designation, its specification is that it will give 400V into its secondary load at 20 times rated continous current. Note this 400V is not a saturation voltage. The definition of 2.5L400 would suggest that the magnetising current was over 2.5% x 100 amps = 2.5 amps with 400V applied to the secondary "on the test bench" for a 5 amp secondary current at rated primary current.

As you write, this means that the maximum burden would be 4 ohms for the specified accuracy. This would mean the rated [continous] VA would be 5 amps x 5 Amps x 4 ohms = 100VA [I2R], for a 5 amp secondary.

Knee-point saturation voltage is defined in the above Wikipedia reference.

There are problems in calculating any relation between knee point and the 400V secondary voltage...

  1. Roughly, magnetising current will have a 90 degree lag to a resistive secondary current. A simple vector diagram suggests magnetising current is about 0.2 x 100 = 20 amps for 2.5 amps magnitude error at 100 amps secondary.
  2. Secondary burden current will not be purely resistive in phase due to leakage reactance (the CT has its own resistance and inductance in the secondary current path). So it will not be at 90 degrees to magnetising current.
  3. While the secondary current may be reasonably sinusoidal, the magnetising current will be very "peaky". So a vector diagram assuming sinusoidal values is not reliable.
  4. The ratio testing is done with r.m.s value reading instruments. Summing a near sinusoid current with a peaky one at about 90 degrees lag and estimating the rms current is not an easy calculation.
  5. The degree of saturation at 400V is not known.

So, you would be wrong to assume 400V is the saturation voltage.

Reply Good Answer (Score 2)
Anonymous Poster #1
#3
In reply to #2

Re: CT Saturation

09/30/2013 10:18 AM

Thank you for the detailed explanation. you don't call your self "Guru" like the other commentator, but you are a true Guru, who knows the subject.

Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#4
In reply to #3

Re: CT Saturation

09/30/2013 4:01 PM

Thanks for writing you found the explanation helpful.

"Guru" is allocated by CR4, according to number of posts and "good answer ratings", Lyn did not allocate himself any accolades.

It is best not to criticise responders for a grouchy reply, responders have been students, have known fellows who want "cribs", recognise examination questions from a painful personal experience and run out of patience with those who seem to want a "free lunch". I have done it myself. I try to remember my own "Google" searches, which usually bury any factual answers to a technical question deep in a bog of sales offers.

You are not "entitled" to an answer, no-one is being paid on your behalf here.

Getting a proper registration to CR4, with a name, will help to show you have made an effort yourself before asking a question (and are not hiding rudeness behind anonymity).