Thanks for the reply
on 2.5L400
is the 400 is the voltage or VA?
when we calculate the Ipedance, why we use it as a voltage
V = IR
assume during the fault the current will be expected 20 times higher than the normal CT operation, i.e. current during fault on the secondary (20 x 5A) = 100A
Then to find the max Burden, R=V/I = 400V/100A = 4 ohms
in this case we use 400 as a vault not as a VA.
and I was assuming 400V is the saturation voltage
Is this wrong?