Over Current & Earth Fault Relay

09/29/2013 3:11 AM

In low voltage system, if there is already over current and earth fault relay in main switchboard, is it still necessity to provide the same at the downstream sub board ? What is the minimum requirement in using over current and earth fault relay ?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User
Engineering Fields - Electrical Engineering - New Member Engineering Fields - Power Engineering - New Member

Join Date: Mar 2012
Location: the sandbox
Posts: 341
Good Answers: 6
#1

Re: over current & earth fault relay

09/29/2013 6:48 AM

what is the voltage and current involved, and under which code are u working?

__________________
BSEE but always learning
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: over current & earth fault relay

09/29/2013 9:12 AM
Register to Reply Score 1 for Off Topic
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#3

Re: over current & earth fault relay

09/29/2013 10:08 AM

Electrical wiring codes are different from country to country. They also change depending on the type of location within that country. Consult your regional code standards. CR4 is not the provider of your code standards.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: Over Current & Earth Fault Relay

09/30/2013 4:33 AM

...nor does it provide training with those standards and certification of competence.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#5

Re: Over Current & Earth Fault Relay

09/30/2013 10:51 AM

Yes, if you want proper co-ordination

Register to Reply
Power-User

Join Date: Jul 2013
Location: Faridabad Near New Delhi India
Posts: 240
Good Answers: 34
#6

Re: Over Current & Earth Fault Relay

09/30/2013 1:28 PM

The O/C and E/F relay in Main Board is provided

1. To suit rating of the switch board

2. Protect Distribution transformer or Feeder from Over load.

3. Protect cables from Transformer secondary to the Board or Feeder cable.

The O/C and E/F relay for down stream feeders is provided:

1. To protect cables supplying that feeder.

2. To ensure power to remaining loads connected to same Board is not disrupted for fault on a particular downstream feeder or consumer.

3. The probability of phase to earth fault is always higher than phase to phase fault - hence a properly set E/F relay will

3.1 Provide desired discrimination.

3.2 Avoid subjecting downstream cables and equipment to longer duration of fault.

So depending upon ratings (where HRC fuse is not feasible). it is preferred that all downstream feeders have suitable O/C and E/F protection.