Minimum Insulation Resistance

09/29/2013 3:23 AM

Is there a minimum acceptable value of insulation resistance test in low voltage system ?

Register to Reply
Pathfinder Tags: cable Insulation Resistance
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User
Engineering Fields - Electrical Engineering - New Member Engineering Fields - Power Engineering - New Member

Join Date: Mar 2012
Location: the sandbox
Posts: 341
Good Answers: 6
#1

Re: minimum insulation resistance

09/29/2013 6:57 AM

it depends on your customers requirements in the SOW. for example, typical is a

megger test at 1 or 2 MΩ

__________________
BSEE but always learning
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: minimum insulation resistance

09/29/2013 9:08 AM

Yes.

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#3

Re: minimum insulation resistance

09/29/2013 10:16 AM

Yes. Depending on the signal and current levels of your instrumentation it can be surprisingly high. I worked on a low voltage system once that 10^9 ohms of insulation leakage current was too small.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Power-User
Engineering Fields - Electrical Engineering - New Member Engineering Fields - Power Engineering - New Member

Join Date: Mar 2012
Location: the sandbox
Posts: 341
Good Answers: 6
#5
In reply to #3

Re: minimum insulation resistance

09/30/2013 2:52 AM

WOW! ive never seen a megger that could read 10^9 Ω. the megger would put out, for ex., 1 KV and measure an current below 10^(-6) amps ??? that must be one expensive megger.

__________________
BSEE but always learning
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#6
In reply to #5

Re: minimum insulation resistance

09/30/2013 7:57 AM

I wasn't using a megger. It was the custom multiple channel instrumentation circuitry we were using. It was probably much more expensive than any megger. I still have the one giga-ohm load resistor we used to verify testing.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#11
In reply to #5

Re: minimum insulation resistance

10/04/2013 9:14 AM

Then you haven't looked at the state of the art in megohmeters lately. There are relatively inexpensive meters that measure up to GΩ and even TΩ at 1000V, 5kV, and up to 10kV. Many of them run off a handful of standard batteries - our 5kV meggers use 12 AA cells. Check these out for example:

http://www.aemc.com/products/index.asp

Megger® must have similar offerings as well, and other manufacturers. They've come a long way from the days of the old hand-crank 500V megger.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#12
In reply to #11

Re: minimum insulation resistance

10/04/2013 9:27 AM

That was about twelve years ago that I used a 1G test load for quick testing. I was also limited to 100V due to ionization break down for all of my tests. Besides the OP is asking about low voltage insulation measurements not measurements at 10kV.

Oops, you were replying to Kapy not me.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#4

Re: minimum insulation resistance

09/29/2013 12:23 PM

Insulation resistance depends on material, on temperature, on ambient medium, on length and.. so on. For thermoplastic insulation 600 V power and control cable see UL 83.For thermoset- insulation see UL 44.In IEC World cables see IEC 60502-1 standard [it has to be calculated using volume resistivity of the insulation and conductor diameter and insulation thickness].

__________________
Julius
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#7

Re: Minimum Insulation Resistance

09/30/2013 10:50 AM

Vide the Indian Electricity Rules, 1956, Rule No. 48 (i): The minimum insulation resistance for systems/equipments below 650V, when tested with a test voltage of 500V DC, should be one mega ohm.

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#8
In reply to #7

Re: Minimum Insulation Resistance

09/30/2013 11:33 AM

That will probably work fine in India for most applications. The OP has not told us where the circuitry lies or the application. So it is still anybodies guess.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Power-User

Join Date: Jul 2013
Location: Faridabad Near New Delhi India
Posts: 240
Good Answers: 34
#9

Re: Minimum Insulation Resistance

09/30/2013 1:11 PM

It depends upon the equipment.

Thumb rule in maintenance industry is designed voltage +1 Mega ohm.

Minimum design voltage of LV system or equipment is 1kV. Hence desirable value is 2 Mega Ohm (measured with 500V DC megger)

As said before it depends upon equipment. For examples:

1. If it is long length of cable, you may find insulation value between phases or phase to earth a few Kilo Ohms. In such cases after testing IR, to make sure that insulation is intact - immediately after disconnecting megger we check the charge voltage and rate of decay. If it shows almost full megger voltage and discharges very slowly (may take up to few minutes, depending upon length) - it is considered that insulation is good and cable can be charged.

2. Certain equipment, for example rotor of magnetic field of a medium or large size turbo generator or even salient pole machine is tested very carefully for IR value.

I have been always using a megger with 50V, 100V, 250V and 500V multiple range and have been recommending to my colleagues.

To avoid damage - or causing a carbon track, always in case of rotor of a used generator, first I check with multi meter between terminal and earth - if value is found in few mega ohms, next I apply 50V DC, If value is same as of multi meter increase to 100V and never above 250V DC.

If IR value of multi meter is doubtful - dry out and check again after drying.

If IR drops at any step to half or lower of previous step stop applying further voltage - clean, dry out, varnish and then test again. In most machines even test at 100V DC most of time is OK as working voltage of field seldom exceeds this value.

Similarly, we take IR before and after High Pot test. We all know that IR after high pot shall not drop below before the test - specially with DC high pot. (we ground +ve of test set or the megger).

Reaon for grounding Positive of Megger or DC Test is that Conductor being at negative potential with respect to earth - any moisture in insulation during testing will travel towards the conductor (osmosis effect), resulting in lowering its IR value. AND GIVING US SIGNAL THAT INSULATION MUST BE TREATED BEFORE TAKING IN SERVICE.

Hence if there is little reduction in IR after Hi pot test - probably there are conductive impurities (like moisture). Winding requires good cleaning and dry out and treatment with impervious resin to protect moisture absorption.

If there is considerable reduction of IR after Hi Pot test - insulation is week and probably damaged during hi pot - requires careful investigation.

The basic reason to carry out Polarising Index measurement of Insulation before subjecting it to Hi Voltage, is to avoid any damage during high voltage test due to moisture or otherwise week insulation.

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#10

Re: Minimum Insulation Resistance

10/03/2013 9:10 AM

The method I was taught as an M&Q apprentice was the total leakage current should not exceed 1/10,000th of the FLC.

1MΏ on an old large machine is often impossible, I would have been changing motors every five minutes had we stuck to a simple "one size fits all" value. The plants were mainly cold and damp so a motors insulation value would fall during shutdowns. A few hours running the IR value would back up again.

Re Megers reading high values. My 5000V model will read in tetra Ώ, on 1000V you're stuck with just gigΏ

PS it hurts when it bites you!

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Register to Reply 12 comments

"Almost" Good Answers: