Frequency Converter

10/01/2013 5:04 AM

I have requirement of frequency converter for load of 1MVA.

60hz to 50 hz.

My question is that whether it is advisable to run all your motor loads dependent on a frequency converter.As all my motors are suitable for 50hz power supply but grid supply available is 60hz.

Please give your valuable suggestions.

Thanks in advance.

Register to Reply
Pathfinder Tags: frequency converter
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: frequency converter

10/01/2013 5:20 AM

How come motors for 50Hz were selected, if the grid supply is 60Hz?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Active Contributor

Join Date: May 2012
Posts: 12
#2
In reply to #1

Re: frequency converter

10/01/2013 5:39 AM

It was lack of information from the client at proposal stage...

Please suggest if there is any solution?

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3
In reply to #2

Re: frequency converter

10/01/2013 5:53 AM

There are plenty of solutions, depending on the numbers and sizes of motors, which information is missing from the original post.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Jun 2010
Posts: 1296
Good Answers: 104
#5
In reply to #2

Re: frequency converter

10/01/2013 9:44 AM

Pretty basic information. Did you get lucky on the voltage guess?

Register to Reply
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#14
In reply to #5

Re: frequency converter

10/01/2013 10:46 PM

To be fair, I am currently working with a client that is in the process of converting 1/3 of their paper mill from 50 Hz to 60 Hz.

The mill is just over 100 years old. When it was built 50 Hz was standard. They put in a dam and ran their own generators.

Over the following years the utility companies standardized on 60Hz, leaving this small pocket of 50Hz.

The plant expanded and the new machines went on a 60Hz grid.

The mill could make money selling power to the now established utility company so they installed a frequency converter - rotating style, so they could swap power back and forth.

90 years later, the hydro power plant was sold off to raise capital.

Another few years later the 50 HZ turbine goes up in smoke and the power agreement with the new owners of the hydro electric plant has lapsed, so now the mill uses the freq converter to run the remaining pocket - but the AC machines are now getting long in the tooth, about 50 years old, and starting to have issues.

So - my project is to see what is required to change the remaining pocket from 50 Hz to 60 Hz -- but it is not going anywhere because the $ involved are too much for a newsprint machine. (I suspect they will shut down the machine first.)

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#4
In reply to #1

Re: frequency converter

10/01/2013 8:08 AM

I'm still impressed with the stealth of those power grid engineers. The way they're able to sneak into a location and change frequencies, voltages, and outlet connector styles is impressive. Particularly since they never get caught. I think they must have been trained by Santa.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Off Topic (Score 6)
Power-User
Engineering Fields - Electrical Engineering - New Member Engineering Fields - Power Engineering - New Member

Join Date: Mar 2012
Location: the sandbox
Posts: 341
Good Answers: 6
#6

Re: Frequency Converter

10/01/2013 10:45 AM

he's the best / simplest/ most reliable/ most efficent frequency converter:

take a 60 hz prime mover, use it to power a 50 hz generator on a straight shaft.

what are the alternate solutions? get 60 hz motors?

__________________
BSEE but always learning
Register to Reply
2
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#9
In reply to #6

Re: Frequency Converter

10/01/2013 11:15 AM

This is the simplest engineering approach. One must be careful in the selection of the 60 Hz induction motor to try and minimize slip if frequency accuracy is really needed. (I doubt this but...) A good idea is to include a freewheel on the shaft.

There is a few legal business questions that should also be looked at by the OP. If the contract was originally designated to use 50 Hz power then the customer should be charged for the conversion. Similarly if the location that this machine will be used has changed from a 50 Hz region to a 60 Hz region then the customer must again foot the conversion bill. If the site of use was never specified by the customer but the OP clearly specified it to be used in a 50 Hz region then the customer should foot the bill. If the customer clearly specified the location this machine will be used but the OP never noticed that this is a 60 Hz region then the OP deserves a dope slap and should convert to 60 Hz for free.

I would change the motors and their controller circuitry to 60 Hz operation if 60 Hz causes a stall with the motors trying to spin faster.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Good Answer (Score 2)
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#12
In reply to #9

Re: Frequency Converter

10/01/2013 10:30 PM

no, no use synchronous machines! 10 and 12 pole machines.

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#13
In reply to #12

Re: Frequency Converter

10/01/2013 10:43 PM

You're wasting your time.

The OP has no concept of what you just said.

One look at his previous posts will show that he is not qualified to work with electricity. Especially high voltage.

He's a candidate for a Darwin award.

Register to Reply Score 1 for Off Topic
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#11
In reply to #6

Re: Frequency Converter

10/01/2013 10:29 PM

I would use synchronous machines for the freq conversion - then the frequency conversion is dead nuts on.

10 pole and 12 pole synch motors.

Register to Reply
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#23
In reply to #6

Re: Frequency Converter

10/02/2013 11:05 AM

I agree with the 60HZ prime mover driving a 50 HZ generator - but you must choose the correct number of poles for the machines. Typically synchronous machines are used and the 60HZ machine will have twelve poles, and the 50HZ machine will have 10 poles. The connecting shaft speed will be 600 RPM, and the frequency conversion is exact.

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#7

Re: Frequency Converter

10/01/2013 10:54 AM

Consider changing jobs.

You don't seem to be well suited for working with electricity.

Register to Reply Score 2 for Off Topic
3
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#8

Re: Frequency Converter

10/01/2013 11:11 AM

The simplest solution where possible would be to change the drive pulleys on the motors to ones 5/6th's the present diameter and run the motors on 60 hz.

Years ago I worked at a pasta plant where almost all of the systems came from overseas and were designed to work with 50 Hz power. All they did was change all of the drive pulleys to smaller ones.

The machinery never had a problem with it.

Register to Reply Good Answer (Score 3)
4
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#10

Re: Frequency Converter

10/01/2013 11:52 AM

This is not a simplistic issue, there are several challenging aspects and given the lack of thinking and detail that went into this already, I fear there is nobody involved who is qualified to address them all.

But here is a grossly simplified synopsis:

You don't state the service voltage, but you might get lucky. AC induction motors produce torque, a primary selection criteria, based on the ratio of voltage and frequency applied to the windings. As long as you stay within +-10% of that ratio, the motors will work fine, but in your case, spin 20% faster (60/50). More on the speed below. So if for example your motors are designed for 400V 50Hz, the ratio is 8:1 and if you apply 480V 60Hz power to it, the ratio is 480/60 = 8:1, so the motor is happy, it just spins faster.

In machinery where speed is not important, you may not need to do anything, but that will need the attention of a qualified Mechanical Engineer. But in CENTRIFUGAL machines like pumps and fans, the 20% higher speed will result in an increase in LOAD on the motor to 173% of design, because the Affinity Law states that in Centrifugal machines, load increases at the cube of the speed change (aka "quadratic"). So at 120% speed, the load increases to 1.2 * 1.2 * 1.2 = 1.73. That means your motors, even if over sized by 20%, will overload trying to drive the pump or fan. On those, you must either be able to change drive sheaves, or you must use VFDs to change speed by providing only 50Hz at whatever the motor voltage is on the nameplate.

If there are loads that are not AC induction motors, you have a lot more issues to contend with, such as saturation of and transformers and voltage tolerances of any power supplies for servos, etc. etc. Plus either way, someone will need to thoroughly investigate the control system.

If that is all too complicated for you (as I suspect), then you need a different solution. Any large scale frequency conversion scheme is going to cost you a lot of money over time in increased energy costs, because you are going to have parasitic losses no matter what you do. I would rather change out all of the 50Hz equipment with 60Hz equipment and force the people who made the mistake to bear the costs.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 4)
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#15

Re: Frequency Converter

10/01/2013 11:09 PM

Adjust the transformer tap to 480V so that V/f is same(400/50 &480/60).

__________________
pnaban
Register to Reply
2
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#16

Re: Frequency Converter

10/01/2013 11:40 PM

having read your first 10 posts, it would seem that you are designing a small electrical installation, lighting layout, bus bar sizes, fault loads, generator loads and now this latest question!

You, it would seem, have dug yourself a BIG hole with no way out. Hire someone that can do the job, and design properly, following the local codes and practices, before you kill yourself or some poor innocent person.

__________________
The square root of nothing is what you make it!
Register to Reply Good Answer (Score 2)
Power-User

Join Date: Jul 2013
Location: Faridabad Near New Delhi India
Posts: 240
Good Answers: 34
#17

Re: Frequency Converter

10/02/2013 12:40 AM

Navneet,

Why do not you install VFD (Variable Frequency Drives). You will have to install one VFD for each motor.

VFD are easily available in the market. Not only 50HZ, you can set each motor to desired speed to optimize output.

Advantage of VFD shall be:

1. Better efficiency than a large common frequency convertor (say motor generator set).

2. Better reliability.

3. Easy to find (ABB, Siemens, Rockwell Automation, Mitsubishi, Hitachi and many more brands at competitive prices are available).

4. It may be possible that even after going to common 50Hz frequency convertor some of drives may not produce the desired output - but if you are using individual VFDs, you can set the speed of each auxiliary anywhere upto 60HZ to get desired output from the plant.

Only disadvantage will be:

1. Lot of Harmonics in Power Supply from VFDs. To minimize harmonics, when you select VFD, ensure that these are with 12 pulse rectifiers.

2. get information on harmonics from VFD manufacturer or use standard IEEE curve for 12 pulse rectifier, depending upon maximum load current of all motors and value of Direct Axis Sub-Transient Reactance (Xd"), calculate distortion at Terminals of alternator. If it below 7% - no problem. It it works out to more than 7% Install Harmonic Filters to limit distortion.

As these Filters are generally capacitive will improve PF and thus efficiency of your power plant up to 2%.

Additionally you may have to order a 3 phase low pass filter (will not cost more that $100) in the sensing supply of AVR of the alternator for stable operation of AVR.

Best of luck

Ramesh

Register to Reply Score 1 for Good Answer
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#21
In reply to #17

Re: Frequency Converter

10/02/2013 9:22 AM

Re: putting VFDs on everything.

A). This concept is assuming all of the loads are AC induction motors

B). No VFD is better than 97% efficient. So unless there is some other energy saving advantage to running at varying speeds (such as process control in centrifugal machines), using a VFD solely as a frequency converter will cost a MINIMUM of 3% more in energy consumption, PERMANENTLY, as in forever. That adds up to a LOT of money over time.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Power-User

Join Date: Jul 2013
Location: Faridabad Near New Delhi India
Posts: 240
Good Answers: 34
#24
In reply to #21

Re: Frequency Converter

10/02/2013 12:37 PM

What do you think is the efficiency of a motor generator set (Frequency converter of the rating of few MW for a Paper Mill)? Best efficiency of motor is 96% and of alternator of another 96%.

Hence the net Efficiency of converter is .96 x .96 = 92%.

Which is better, a frequency converter of 92% or using VFD or 97%?

Above efficiency is at load between 75% and 100% which may not be the situation always - so overall efficiency of power source by using frequency converter can be still poorer.

Further when you are running a plant which was designed for 60HZ straight at 50% you may not be able to balance or achieve an equilibrium as efficiency and performance of all auxiliaries will not be in same proportional as 60HZ.

Then to achieve balance and steady unattended operation, the Plant engineer may end up in adding either orifices or regulating valves to match the performance of device in series with that of one behind it and another upstream.

To avoid all above and achieve efficient operation - VFD is a better option than Frequency Converter.

I have seen many power plants saving power by using VFD for Feed water Pumps and Induce and Forced Draft fans for boilers than waisting power in throttling of pump flow by orifice or increasing restriction in dampers.

Thus in all respect a VFD is better answer that Frequency Converter.

Intention is not to heart anyone but to express my experience in front of forum, it may benefit somebody.

Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#22
In reply to #17

Re: Frequency Converter

10/02/2013 10:45 AM

While taken at face value, it would seem a VFD (Variable Frequency Drive) would be the solution, but its a drive that varies the Hz to control the motor RPM. As stated this will cost lots of money over time and NEVER give any ROI, if the correct calculations are done now it will be proven to be to expensive over time and not to be cost effective.

That is just for the drive... what about the effect the drive will have on the motors, are the motors VFD rated? What about harmonics? what about run life of the motor.

Here is a solution... sack the guy that did the design and get someone who knows what he is doing!

__________________
The square root of nothing is what you make it!
Register to Reply
Guru

Join Date: Dec 2007
Location: Mumbai, India
Posts: 1983
Good Answers: 25
#18

Re: Frequency Converter

10/02/2013 6:25 AM

Is your client Essar Steel? similar thing happened when we recd. order from them for Hoists. They have installed German Briquetting plant at Hazira.

__________________
"Engineers should not look for jobs but should create jobs for others" by Dr.Radhakrishnan Ex President of India during my college graduation day
Register to Reply Off Topic (Score 5)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#19
In reply to #18

Re: Frequency Converter

10/02/2013 6:42 AM

According to this, the supply in India is 50Hz.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Dec 2007
Location: Mumbai, India
Posts: 1983
Good Answers: 25
#20
In reply to #19

Re: Frequency Converter

10/02/2013 6:56 AM

Yes, you are right being ex-British Colony we have 415V/50hz supply.

__________________
"Engineers should not look for jobs but should create jobs for others" by Dr.Radhakrishnan Ex President of India during my college graduation day
Register to Reply Off Topic (Score 5)
Register to Reply 24 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

1capybara (1); bigg (1); brich (2); GW (4); JRaef (2); lyn (2); navneet311 (1); pnaban (1); powersolutionsFBD (2); PWSlack (3); redfred (2); suresh sharma (2); tcmtech (1)