Lag Length VS Extension Length for Thermowell

10/04/2013 1:44 AM

Hi

CA anyone explain to me the difference between lag length and extension length. I know that we use extension length to isolate a head mounted transmitter from high temperatures where the thermowell is installed but does the lag length also serve this purpose.

One more thing is there a rule of tumb for deciding extesion lenght for a certaing process temperature. I have to install a couple of emerson 1097 thermowells at a 900-1000 deg C service.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Lag Length VS Extension Length for Thermowell

10/04/2013 3:17 AM

No joy with Emerson over the phone, then?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Associate

Join Date: Jan 2013
Posts: 40
#2
In reply to #1

Re: Lag Length VS Extension Length for Thermowell

10/04/2013 9:00 AM

i am not sure what you mean by that but yes they are not very cooperative.

Register to Reply Off Topic (Score 4)
Guru
Hobbies - DIY Welding - New Member

Join Date: Sep 2007
Posts: 1601
Good Answers: 58
#4
In reply to #1

Re: Lag Length VS Extension Length for Thermowell

10/05/2013 12:55 PM

Our rule of thumb is that the thermowell must be at least 10 diameters long.

Register to Reply
3
Power-User

Join Date: Nov 2009
Posts: 335
Good Answers: 63
#3

Re: Lag Length VS Extension Length for Thermowell

10/04/2013 3:46 PM

1) This diagram shows lag and extension as the same thing. What source do you have that says they're different?

2) There's a lot of unsubstantiated oral tradition out there about temperature drop through a metallic extension/impulse line . I heard a foot of steel tubing/pipe drops 100 deg F per foot 35 years ago. Experience showed that temperature drops more rapidly than that for exposed (uninsulated) impulse or extension piping.

There's a 4 year old discussion on this topic here: http://www.control.com/thread/1240831095

Kulite has an app note with the equations and graphs

http://www.kulite.com/docs/technical_papers/AN8401HeatTube.pdf

Their key sentence is the summary at the end:

"As a rule of thumb, one foot of steel tubing, any diameter, will isolate a transducer from any temperature."

I have to add that one foot (300mm) of steel tubing drops conductive heat. Instruments are still exposed to radiant heat from the heat source and convective heat from the surrounding air. Those radiant and convective sources still have taken into account.

Register to Reply Good Answer (Score 3)
Associate

Join Date: Jan 2013
Posts: 40
#5
In reply to #3

Re: Lag Length VS Extension Length for Thermowell

10/07/2013 3:01 AM

Dear CarlWhat i am asking is the difference between a simple lagging extension and a nipple union based extension.

For the lagging extension in your paseted diagram i have found different purpose stated by different manufacturers. Mostly they say the purpose for lagging extension is to install thermowells on insulated lines. this extra length gets the transmiiter side of the well out of insulation.but this configration suggested by ashcroft (page 2 point 3) for example will keep the process connection trapped in the insulation.

http://www.ashcroft.com/tech/upload/AshThermWell8Steps.pdf

But emerson says that this length helps the temperature to drop on the transmitter side. so i am confused on the actual purpose of lag length??

The normal practice at where i work is in order to get the thermowell out of the insulation we increase the U-length(insertion length) this gets the flange out of the insulation. We dont rely on the lag length for this purpose.we keep a fixed 50mm lag length and a varying nipple union extension for the temperature drop.

P.S i hope the attachment can be read, if not let me know. Also Can you please explain what does emerson mean by the term "uninsulated distance from the process".

thanks

Register to Reply
Power-User

Join Date: Nov 2009
Posts: 335
Good Answers: 63
#6

Re: Lag Length VS Extension Length for Thermowell

10/10/2013 5:03 PM

I don't quite understand your statement, 'getting the flange out of the insulation'.

Isn't your thermowell flange mating to a tank nozzle flange, where the tank nozzle is welded to the tank and fixed at some distance from the tank?

If you're not mating your thermowell flange to a tank nozzle flange, why use a flange?

If your thermowell flange is mating to the tank nozzle flange, the U length only determines how far into the tank the well extends. So I'm confused.

Most installations I've seen do what (I think) you do - the thermowell has a fixed lag length (relatively short, like yours) and nipples/pipe and a union are used to bring the wiring and the mounting point for the transmitter head out beyond the insulation. The reason I've heard is that the extension distance can be custom adjusted for whatever the insulation thickness is.

I assume Emerson's statement "uninsulated distance from the process" means how far the nipples and union extend the head/transmitter beyond the insulation, which allows for cooling.

Register to Reply
Associate

Join Date: Jan 2013
Posts: 40
#7
In reply to #6

Re: Lag Length VS Extension Length for Thermowell

10/14/2013 4:39 AM

may be i didnt say it right..

lets say i have a line of 14", i take out a nozzle from the line with length about 6" and then weld flange to that nozzle. the insulation on the line is 4".

Now what i will do is keeping an immersion length of about 6"(length of thermowellthat goes in the pipe) i will go for a U-length of about 12"(immersion length + nozzle length). And depending upon the high temperature i can select a nipple union extension or lag length that will keep my transmitter at a cooler temperature.

I think you agree to most of what i will do.

But have a look at what ashcrost says page 2 point 3

http://www.ashcroft.com/tech/upload/AshThermWell8Steps.pdf

"LAGGING EXTENSION & INSTALLATION WRENCH FLATS

is shown as "T" on engineering drawings when applicable. This is used when the

vessel or pipe into which the thermowell is inserted is insulated. This is the extra

length between the process connection and the instrument connection of a thermowell,

which is determined by the insulation thickness."

Ashcroft is using this lag length for a different purpose from the above one for the above line what they can do is keep a 6" immersion length (part that goes in the pipe) they can reduce the nozzle length to say 2" (even if the insulation is 4"). So with Ashcroft i can select a thermowell with U-length of 8"(immersion length +nozzle length) [note that the flange will be covered by the insulation]

and in order to get the other end out of insulation for mounting a remote transmitter i will select a lag length of 4" this will bring the transmitter at the same level as the 1st method but whats the use of doing this..i mean i will have to cut open the insulation for dismounting the thermowell..The only plus i can see is that by this scheme Ashcroft thermowell requires a reduced U-LENGTH. My scheme required 12" of U-lenght while the second scheme requires only 8".

Any thoughts on this.

Register to Reply
Register to Reply 7 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Carl_E (2); PWSlack (1); SArsalan (3); welderman (1)