Anonymous Poster #1

I.S and Non-I.S Cable Separation

10/08/2013 2:51 AM

In my understanding , I.S blue cable can be laid with NON-I.S cable by keeping minimum 2" spacing or metallic partition between I.S cable and Non-I.S cable according to NEC.

On my plant, ALL tray (for main cables) with two section by using metal separator has been applied from different Field area upto DCS rack room. Some of Trays from different sources are intersected ( eg. Tee or Cross tray section ) in several of area etc….in this case I.S cable/Non-I.S cable should be unavoidably mixed in cross area to be routed upto required destination….

I could not find any explanation per Code/standard, and could anybody please let me know if this is ok and inform the specific any reference from Code/standard….

Reply
Pathfinder Tags: cable separation
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: I.S and Non-I.S Cable Separation

10/08/2013 11:42 AM

Just don't lay any I.S blue cable close to any orange cable. The colors may bleed over.

(humor)

Reply
Anonymous Poster #1
#2
In reply to #1

Re: I.S and Non-I.S Cable Separation

10/08/2013 7:41 PM

Thanks for reply....As explained, overally keeping separation is followed, but only very short area in tray fitting due to different direction of each cable have mixed case unavoidably...and I try to find kind of justification.

Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3
In reply to #2

Re: I.S and Non-I.S Cable Separation

10/08/2013 9:28 PM

Without knowing where your plant is located, or what code requirements are in effect, it's hard to say.

Reply
Guru

Join Date: Jun 2011
Location: Mossel Bay, SA
Posts: 777
Good Answers: 21
#4

Re: I.S and Non-I.S Cable Separation

10/09/2013 2:51 AM

If the "blue" cable is in fact a twisted pair, or if the "blue" cable is properly shielded and earthed, then there is no problem. The reason for the spacing and / metal barrier is to prevent electro-magnetic induction in the IS cable.

Sometimes, practical and cost considerations override standard practice on an evaluated risk basis. Is your plant running, or is this a new installation ?

Reply Score 1 for Good Answer
Anonymous Poster #1
#6
In reply to #4

Re: I.S and Non-I.S Cable Separation

10/10/2013 7:47 PM

Dear Mr.Hiton,

Thanks for your clear explanation..

Based on this, I also found the description through IEC which shows "No segregation is required if metal sheaths or screens are used for the intrinsically safe or non-intrinsic safe circuit.", and I reallized that some of customer do not need separation even whole run of cables due to such reason.

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5

Re: I.S and Non-I.S Cable Separation

10/09/2013 3:35 AM

British Standard 5345 and its ISO equivalent.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Reply to Forum Thread 6 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); Hilton (1); lyn (2); PWSlack (1)

Previous in Forum: Cable Gland and Plug Application on I.S Application   Next in Forum: Difference In Increased Safety & Intrinsic Safety

Advertisement