Lockout Relays

10/09/2013 12:02 AM

Hi all.

why do we use high impedance lock-out relays like RXMVB4 in circuits?

In tripping circuit of HV & EHV circuit breakers.

though the fast tripping can be achieved through low impedance relays, why do we use high impedance relays?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Member

Join Date: Oct 2013
Posts: 5
#1

Re: Lockout relays

10/09/2013 7:08 AM

dear lyn, the question is not about "why not?"

In my industry RXMVB4 is what we are using.

But is there any specific reason to go for high impedance relays?

Register to Reply Off Topic (Score 6)
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#2
In reply to #1

Re: Lockout relays

10/09/2013 9:43 AM

Low impedance relays are generally current-operated. For lockout relay applications, especially breaker tripping for transformer protection, high-speed operation is vital, and this can be more consistently and accurately achieved with a voltage-operated (high impedance) relay. Read the descriptive bulletin you referenced - it explains the function pretty clearly.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply Score 1 for Good Answer
Member

Join Date: Oct 2013
Posts: 5
#5
In reply to #2

Re: Lockout relays

10/10/2013 2:31 AM

But high speed operation can be achieved through high current, i.e. low impedance relays.

Register to Reply
Anonymous Poster #1
#3
In reply to #1

Re: Lockout relays

10/09/2013 9:48 AM

Have you asked the engineers in "your industry"?

Register to Reply Off Topic (Score 5)
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#4

Re: Lockout Relays

10/09/2013 6:58 PM

because the design engineer golfs once a week with the high impedance relay sales guy

Register to Reply
Commentator

Join Date: May 2013
Posts: 86
Good Answers: 2
#6

Re: Lockout Relays

10/10/2013 6:24 AM

The lockout relays are short time rated voltage operated relay, i.e if auxiliary voltage is 110 volts, the continious relay rated voltage will typically be 50%. This is to acheive high speed of operation. For the same reason, the voltage to the coil will be cutoff through its own contact once the relay operates to prevent burnout of the coil.

Register to Reply
Power-User

Join Date: May 2013
Posts: 351
Good Answers: 22
#7

Re: Lockout Relays

10/10/2013 8:08 AM

The relays must operate on the DC battery banks (usually 125VDC or 250VDC) as other relays do for protection of circuits. Sometimes the distance from the relay may be quite a long distance within a large utility or plant. This is the way it WAS done. It worked so why change it? They are designed so that the various transients within the system do not cause false trips or no trips at all. I remember when some battery company tried to sell NiCad batteries for these systems. The voltage was there, but the natural transient absorbing action of the old lead acid batteries was not. Lots of false trips. The only choice was to remove the new batteries and put the old type back. A protective circuit must be reliable, fast, and not error prone. It is possible for changes to be made but the research for those changes must be flawless and extensive. I have no idea whether low impeadance relays would answer all criteria, but I question the motive for using them. What is the advantage? Change for change sake is not an advantage unless there is an improvement that is gained. We are talking multiple millions of dollars in most electrical system with lives at stake if errors are made. Not to be taken lightly without proper investigation.

Register to Reply
Register to Reply 7 comments

"Almost" Good Answers: