Liquid Resistance Soft Starter

10/11/2013 2:19 AM

Hi There,

Can anyone shed some light on this, it is a soft starter for a chiller and one of the containers appears to be leaking, as far as I can gather it is filled with some kind of saline solution but no one can confirm this.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Liquid resistance soft starter

10/11/2013 3:15 AM

It sounds as though its repair or replacement is overdue.

Does the facility have comprehensive fire insurance cover?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Commentator

Join Date: Aug 2008
Posts: 82
#2

Re: Liquid resistance soft starter

10/11/2013 9:13 AM

That may be a Battery ?

Register to Reply Score 1 for Off Topic
2
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#3

Re: Liquid resistance soft starter

10/11/2013 9:41 AM

Looks like a form of Statormatic. Statormatics use a caustic solution.

Have a look for a company called AOIP, they are based in France but like most companies they have a wide network.

__________________
The reports of my death are greatly exaggerated.
Register to Reply Good Answer (Score 2)
4
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#4

Re: Liquid Resistance Soft Starter

10/11/2013 11:04 AM

Yes, I've seen this kind of thing only once before about 20 years ago on a slip ring motor, that's called a Vapormatic starter, but I was told the same concept on a squirrel cage motor is called Statormatic and I investigated it.

The working concept is the varying resistance of an electrolyte as it heats up. So instead or relying on electrodes moving up or down in an electrolyte as a more traditional liquid resistance starter does, these are fixed but the electrolyte heats up or boils as current flows, which lowers the resistance. In the slip ring version the liquid resistance is used to change the rotor circuit resistance, which alters the torque as it accelerates. But typically it's used just as a soft starting method for slip ring motor because its difficult to maintain a specifit electrolyte temperature for something like varying speed or torque, which is what the liquid immersion types can do.

In the squirrel cage version, it's just like a reduced voltage primary resistor starter but the resistance is variable, lowering as the motor accelerates, giving more voltage to the stator as it does. Then once at speed, the bypass contactor closes. It would provide a softer start than a primary resistor starter would though because of the varying resistance.

All in all though, all of these technologies were used when there were few alternatives. Electronic soft starters are a quantum leap better, safer and less expensive now. I'd hazard a guess that you will be able to buy a complete new solid state starter unit for what it will end up costing to repair this one.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 4)
2
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#5
In reply to #4

Re: Liquid Resistance Soft Starter

10/11/2013 9:09 PM

Vapourmatic and Statormatic are made by the same company. Both work very well if maintained correctly.

The big difference is the Vapourmatic has multiple three pole electrodes in the same tank where the Statormatic has three separate tanks.

The biggest failure is due to not maintaining the electrolyte level. The bottom of the electrodes burn and starting becomes erratic. The bigger units have low electrolyte level built in to them that prevents starting.

I'm just advising on renovating two much neglected Vapourmatics. The spares are salvaged from units I installed as an apprentice. Spares are still available, why buy new when you can get serviceable parts within the company.

New spares are going to be ordered to keep as company stores stock.

It's been a weird involvement with this renovation, three companies involved. Two of the companies I worked for in the past, the other company was a rival but they knew me.

I'm retired so really it doesn't involve me, but life being what it is I got involved. I'll be lucky to get a couple of bottles of malt out of it.

But what the hell, it's been fun helping out, and I haven't had to shift off my backside or get my hands dirty!

__________________
The reports of my death are greatly exaggerated.
Register to Reply Good Answer (Score 2)
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#6
In reply to #4

Re: Liquid Resistance Soft Starter

10/17/2013 2:56 AM

Agree with the electronic retrofit idea.

OP didn't say whether the unit was malfunctioning or just showing signs of leakage.

If it is out of service then less than $500 will bring this into the current century and outlast the chiller it's starting.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply