Insulation Resistance Test Voltage

10/13/2013 2:19 AM

Is it a wrong practice to conduct insulation resistance test for a 450/750V cable with a 1000V insulation tester ?

Register to Reply
Pathfinder Tags: Insulation Resistance Voltage
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User

Join Date: Mar 2010
Location: Islamic Republic of Pakistan
Posts: 124
Good Answers: 14
#1

Re: insulation resistance test voltage

10/13/2013 8:29 AM

1. When D.C Volatge is used

Test Volatge (D.C) = 2 x Name Plate Voltage

2. Cable Rating and DC Test Voltage:

i. For 24 to 50 V ........ D.C Test Volatge 50 V to 100 V

ii. For 50 to 100 V ........D.C Test Volatge 100 V to 250 V

iii. For 100 to 240 V ........ D.C Test Volatge is 250 V to 500 V

iv. For 440 to 550 V ........ D.C Test Volatge 500 V to 1000 V

v. For 2400 V ........ D.C Test Volatge 1000 V to 2500 V

vi. For 4100 V ........ D.C Test Volatge 1000 V to 5000 V

3. Selection of IR Testers:

I.R testers are available in the ranges 500, 1000, 2500 and 5000 VDC.

i. For Volatge level of 650 V, IR Tester of 500 V DC

ii. For Volatge level of 1100 V, IR Tester of 1000 V DC

iii. For Volatge level of 3300 V, IR Tester of 2500 V DC

iv. For Volatge level of 66 kV and above , IR Tester of 5000 V DC

Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#2

Re: insulation resistance test voltage

10/13/2013 9:54 AM
__________________
Julius
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15603
Good Answers: 982
#3

Re: insulation resistance test voltage

10/13/2013 9:56 AM

Actually it is very common to test any attribute at 150% to 200% of the attribute rating. The important thing is that the device producing the over rating attribute is designed to not destroy the device under test should it fail the test. Testing the insulation of a 750V cable at 1000V with an insulation testing instrument is normal. Trying to perform the same test using a 1000V power distribution connection for the source is foolish if not negligent.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#4

Re: insulation resistance test voltage

10/13/2013 10:47 AM

Make it simple

200% of rated operating voltage.

As for acceptable values I still stick to the old UK M&Q value of 1/10,000th FLC

__________________
The reports of my death are greatly exaggerated.
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Mar 2011
Location: oz
Posts: 252
Good Answers: 10
#7
In reply to #4

Re: insulation resistance test voltage

10/13/2013 6:14 PM

G.A. operational voltage is the deciding factor.

Register to Reply
Commentator

Join Date: May 2013
Posts: 66
#11
In reply to #7

Re: insulation resistance test voltage

10/16/2013 6:44 AM

Is that mean if I am using a 450/750V rated cable for 415V 3-phase system, test voltage 415 x 2 = 930V. So 1000V test voltage to be selected, not the 500V which is allowable voltage for cable ? I hope you all dont mind if I always turn around this topic. I just want to clarify all possibilities.

Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#5

Re: insulation resistance test voltage

10/13/2013 3:10 PM

It depends on the electrical test standard you are working to (they vary from country to country and between equipment, site wiring, etc). There is no single right answer and 1000V may be to low.

Do you know what test standard you are supposed to be working to for the wiring you are trying to test in the application it is intended to be used in the country it is to be used in?

__________________
jack of all trades
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15603
Good Answers: 982
#6
In reply to #5

Re: insulation resistance test voltage

10/13/2013 4:34 PM

Standards? Standards? We don't need no stinking standards. We just make up our own rules like any bandit. You stupid gringos think you can come here and tell me how to fleece a customer by using a standard. If I used a standard they might learn something. Then they won't come back to me. Besides I got my answer from a French model I met on the internet.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Commentator

Join Date: May 2013
Posts: 66
#8

Re: Insulation Resistance Test Voltage

10/14/2013 8:47 PM

In our area, contract specification usually specify 600/1000V rating for submain cable. But all the suppliers here are selling 450/750V rating material. For a consultant, they are looking for insulation test using 1000V. Is there technical compliance explaination that we can convince the consultant that using 500V for testing the submain cable rated at 450/750V actually giving the same result as using 1000V test voltage. This has been normal using 450/750V rated cable for submain here, only some consultant not aware.

Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#9
In reply to #8

Re: Insulation Resistance Test Voltage

10/14/2013 9:21 PM

If the consultant would accept a 1000V test to allow you to supply the lower voltage cable then just test it and send them the test results/report. I would be very surprised if the 450/750V cable fails a simple 1000V insulation test.

The mains-rated power cable should be more than capable of handling this voltage because cable suppliers over-rate the cables to allow them to handle high voltage impulses, spikes, etc that they will undoubtedly see when installed in the real world power network.

__________________
jack of all trades
Register to Reply
Member

Join Date: Sep 2013
Posts: 5
#10

Re: Insulation Resistance Test Voltage

10/15/2013 6:01 AM

hi, It's not wrong, Because 450/750V cable is rated with 1.1KV Grade, so you can test IR Values with 1000V IR Tester.

Register to Reply
Register to Reply 11 comments