Participant

Join Date: Oct 2013
Posts: 1

About Amp

10/13/2013 10:59 AM

i have one main breaker having 50 amp so how many sub-breakers can i use in the board

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: about amp,

10/13/2013 11:00 AM

No particular limitation other than the number of spaces actually in the DB.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2
In reply to #1

Re: about amp,

10/13/2013 11:28 AM

And as long as the combined amperage rating of the individual breakers does not exceed the capacity rating of the main breaker.

Register to Reply
3
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#4
In reply to #2

Re: about amp,

10/13/2013 11:32 AM

Not remotely true.

The new panel I put in our house has a 100 amp main and spaces for 24 breakers of which have a combined amp capacity of something like ~300+ amps.

Register to Reply Good Answer (Score 3)
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#5
In reply to #4

Re: about amp,

10/13/2013 11:35 AM

Of course, not for you in BFE.

I'm talking about what sane people do when complying with local codes.

Register to Reply Off Topic (Score 4)
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#6
In reply to #5

Re: about amp,

10/13/2013 11:50 AM

Actually all you need to do is look at any main breaker or fuse panel and do some simple math.

The odds are even the one in your house has a combined amp rating of all of the smaller sub circuits that is way higher than the one primary set is.

Go have a look and let me know what you find.

I would give you the exact quote from my NEC code book as to why it's acceptable but my wife put it someplace I will likely never find again.

Register to Reply Score 1 for Good Answer
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#7
In reply to #6

Re: about amp,

10/13/2013 12:03 PM

Indeed. Diversity factors, demand factors, and nonconcurrent loads may be considered.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#8
In reply to #6

Re: about amp,

10/13/2013 12:17 PM

I'll stick with my statement, given the obvious lack of knowledge of the OP, knowing it will be ignored, anyway.

(Don't do as I do, do as I say)

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#11
In reply to #8

Re: about amp,

10/13/2013 12:38 PM

My concern is that if you tell someone who doesn't understand the implications, that it's OK to put 150 AMPs worth of breakers in a 50 AMP box, they will assume that the 50 AMP box can carry 150AMP loads.

I'm done here.

Register to Reply
Guru

Join Date: Aug 2010
Posts: 687
Good Answers: 21
#21
In reply to #2

Re: about amp,

10/14/2013 5:34 AM

Sorry Lyn, but your wrong on this one. Main protects the incoming wiring. Main will trip when load exceeds value of breaker. Does not matter on number of secondary breakers. But, most manufactures limit spaces to a certain number.

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#22
In reply to #21

Re: about amp,

10/14/2013 10:06 AM

OK, not the first time.

Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#10
In reply to #1

Re: about amp,

10/13/2013 12:37 PM

actually NEC says max 42 "switches"

Register to Reply Score 1 for Good Answer
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#12
In reply to #10

Re: about amp,

10/13/2013 1:05 PM

This may come into play if the OP's DB has more than 42 spaces in it.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3

Re: about amp,

10/13/2013 11:30 AM

sreeharir.86,

Since the forum can have no idea where you really are:

Consult the local regulatory boards and your insurance underwriter.

Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#9

Re: about amp,

10/13/2013 12:21 PM

you shouldn't be as worried about how many as you should be concerned about how many amps in total can you safely add(think %)

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#13

Re: about amp,

10/13/2013 2:25 PM

Don't diversity calculations apply in the USA?

BS7671Am1 OSG has quite a large section devoted to it.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#14
In reply to #13

Re: about amp,

10/13/2013 5:14 PM

Please see #7↑.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#17
In reply to #14

Re: about amp,

10/13/2013 7:55 PM

Sorry kid. Time to get my eyes tested :-)

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#18
In reply to #17

Re: about amp,

10/13/2013 8:41 PM

I don't know about the "kid" stuff; at 65 I'm probably not too much younger.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#15
In reply to #13

Re: about amp,

10/13/2013 5:24 PM

Judging by the name of the OP, I doubt that we are talking about the USA.

I concede that my instructions may not apply to residential electrical wiring in the USA.

But.............................

Register to Reply
3
Power-User

Join Date: Mar 2011
Location: oz
Posts: 252
Good Answers: 10
#16

Re: About Amp

10/13/2013 6:07 PM

The breaker is to protect the cable, you can have many sub breakers as you like as long as each cable is protected by a breaker.

Register to Reply Good Answer (Score 3)
Participant

Join Date: Oct 2013
Posts: 4
#19

Re: About Amp

10/14/2013 12:28 AM

What is your load requarment depand on that... Just be care full that load should not exceed 50A putt tripping ckt with protection on abow 50A then put sub breaker as u want..

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#20

Re: About Amp

10/14/2013 3:29 AM

The breakers are related to the cable sizes. As no-one here can see the distribution board and the number, type and diversity of the loads and doubt has been posted here, the full answer is "consult a qualified local Electrician".

Make sure the installation is compliant with local wiring codes, or a measure of unpopularity with the facility's fire insurance company is sure to result.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Participant

Join Date: Nov 2009
Posts: 2
#23

Re: About Amp

10/15/2013 2:54 AM

Depends on the segment of the DB u were using, moreover the actual main incomer MCB will be designed of 1.8 times for the total load shared by the DB.

Register to Reply Score 1 for Off Topic
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#24
In reply to #23

Re: About Amp

10/15/2013 3:13 AM

Nonsense.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Member

Join Date: Sep 2013
Posts: 5
#25

Re: About Amp

10/15/2013 6:17 AM

Hi, To Deside the Breaker rating of the Distribution board Incomer,first you calculate your connected loads on the DB with Divercity factor, then only you can find the correct rating of the Incomer.

Register to Reply
Participant

Join Date: Nov 2009
Posts: 2
#26

Re: About Amp

10/15/2013 6:40 AM

but dude, is there an 50amps breaker? the breaker comes in the rating of 5A/10A, 16A/20A, 32A, 40A, 63A, 100A and goes on. first check whether there is an 50A breaker!

Register to Reply Score 2 for Off Topic
Power-User
Engineering Fields - Electrical Engineering - New Member Engineering Fields - Power Engineering - New Member

Join Date: Mar 2012
Location: the sandbox
Posts: 341
Good Answers: 6
#27

Re: About Amp

10/15/2013 9:05 AM

FWIW, NEC had the 42 switch limit in the 2008 code, its gone from the 2011 code and 2014 code. Its now no problem getting 54 and 60 space panels. But one of the limiting factors is, how many holes do you have room to punch in the panel for conduit.

__________________
BSEE but always learning
Register to Reply
Guru

Join Date: Apr 2012
Posts: 732
Good Answers: 17
#28

Re: About Amp

10/16/2013 11:40 AM

Read up a little at this link.

Maybe it will jog something loose from your electrical engineering school days.

__________________
common knowledge...less common than common sense
Register to Reply
Register to Reply 28 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

1capybara (1); eltech (1); fixitorelse (1); Fredski (2); Kedarnathsingh (1); kirankk (1); lyn (7); PWSlack (2); santho (2); tcmtech (2); The.Tinkerer (1); TonyS (2); Tornado (5)

Previous in Forum: Insulation Resistance Test Voltage   Next in Forum: Big Fault at Power Transformer 550Mva

Advertisement