Neutral Cable Size

10/12/2013 9:53 PM

What is the situation where a neutral cable can be sized half the phase cable ? What is the concept behind ?

Register to Reply
Pathfinder Tags: cable size neutral cable
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: neutral cable size

10/12/2013 10:08 PM
Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#2

Re: neutral cable size

10/12/2013 10:56 PM

Depends upon the system in use.

For example, in a 3 wire 120/240V residential service in Canada (and I am pretty sure in the US as well) the neutral needs only be sized to handle the maximum line to neutral load. If you have a 200 amp service and only 50 amps of line to neutral load on one line, then the neutral need only be sized to handle the 50 amps as it will never see more than that.

Remember that... neutral current is off set. If you see 50 amps on L1 to the neutral and 30 amps on L2 to the neutral, the neutral only sees 20 amps.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Commentator

Join Date: May 2013
Posts: 66
#4
In reply to #2

Re: neutral cable size

10/13/2013 2:47 AM

If 50A on L1 to neutral, 30A on L2 to neutral and 60A on L3 to neutral for a 4 wire 415V system, what would be the neutral current ? In designing a system, is there way to size the neutral cable without actual measuring on site ?

Register to Reply
2
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#7
In reply to #4

Re: neutral cable size

10/13/2013 10:49 AM

That is a complicated question... in three phase systems, you need to consider phase angles and the power factor of the loads.

Given the price of conductors and not knowing the nature of the loads... I would just go with a full size neutral. In some conditions you may even want to consider up sizing the neutral because of non-linear loads.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply Good Answer (Score 2)
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#10
In reply to #7

Re: neutral cable size

10/13/2013 11:34 AM

No!

The neutral wire gauge size is established by the local wiring code. It does not matter what load is presently on the three phases. This load will change over time. The neutral wire is part of the location infrastructure and must meet these local codes. Now if and only if the neutral wire in question is part of the short line cord going to this load and it was impossible for a failure mode of the load to exceed the stated currents then one could make an argument for under sizing a conductor from code.

The local code is not based on normal operating conditions, it is based on failure mode conditions that history has presented. The code prevents a failure from becoming a bigger disaster.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#12
In reply to #10

Re: neutral cable size

10/13/2013 11:49 AM

So why do you presume it is not ok for him to do what he has asked about? Do you know what code he operates under?

Code takes into consideration the design of the system at installation and assumes that if an when the load changes, the changes will force changes to the system. Codes are minimum based. Otherwise... we would be forcing people to install systems that far out weigh their needs.

Besides... I recommended to him that he go with a full size neutral and perhaps, may want to upsize based on the nature of the load.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#13
In reply to #12

Re: neutral cable size

10/13/2013 12:40 PM

I have absolutely no idea which local code the OP should be following and neither do you. So just because he might happen to be following code if he's lucky, should we encourage him to not bother knowing his local code? No. CR4 is not the relevant authority here and we should not pretend to be either.

If our OP identified the code that they thought was ambivalent for their application then we can advise.

You are correct that code is a minimum standard and not an optimum guide. You are also correct that it is usually best to size the neutral wire the same gauge and insulation as the phase wires. However, without knowing the relevant code and installation conditions then the correct wire cannot be known.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#14
In reply to #13

Re: neutral cable size

10/13/2013 12:55 PM

To your point... Yes... I agree he needs to undertand the rules around neutral sizing in his particular wiring regulations.

But... as to his 2nd question... I think you are missing the point. The OP asked about the "concept" behind downsizing neutrals, which is what I replied to.

I do not see any comments presented in this thread that appear authoritative in nature.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#16
In reply to #4

Re: neutral cable size

10/14/2013 3:33 AM

<...there way to size the neutral cable ...>

Every qualified Electrician in these islands uses British Standard 7671.

If the cable were to be sized on site, then every installation would be wrong. So it's best to do it beforehand.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
2
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#3

Re: neutral cable size

10/13/2013 12:28 AM

Follow your local electric codes. If you don't know what is your local code, hire somebody who does. Remember people literally died to make your code. Respect their deaths.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Good Answer (Score 2)
Commentator

Join Date: May 2013
Posts: 66
#5

Re: neutral cable size

10/13/2013 3:24 AM

What would be the direction flow of a neutral current ?

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#6
In reply to #5

Re: neutral cable size

10/13/2013 10:08 AM

Downhill, half the time.

Register to Reply Score 1 for Good Answer
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#8
In reply to #6

Re: neutral cable size

10/13/2013 10:51 AM

LOL...

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#15
In reply to #5

Re: neutral cable size

10/14/2013 3:32 AM

Oh, it's simple. It depends upon the instantaneous loads on the phase currents, none of which can be seen from here, and all of which vary with time.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#9

Re: neutral cable size

10/13/2013 10:55 AM

For normal resistive loads

In = √((Ia²+Ib²+Ic²)-((Ia*Ib)+(Ia*Ic)+(Ib*Ic)))

Once you start to introduce harmonics, screw that up and go for a full size neutral.

__________________
The reports of my death are greatly exaggerated.
Register to Reply Score 1 for Good Answer
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#11
In reply to #9

Re: neutral cable size

10/13/2013 11:38 AM

This is the correct method to calculate how much current will reside on the neutral for a particular load. Please see my previous comment.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Commentator

Join Date: May 2013
Posts: 66
#17

Re: Neutral Cable Size

10/14/2013 6:40 AM

Thanks all.

Register to Reply
2
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#18

Re: Neutral Cable Size

10/14/2013 10:24 PM

Here copied from one of my previous post (http://cr4.globalspec.com/comment/791151) and hope it will help:

The selection of neutral conductor depends on the nature of loads, such as the load harmonics (more than 20% loads are electronic) or the load balancing (most of the loads are 3 phase motor) etc. So, there are few cases to consider here:

(1) If the loads are almost balanced and there is no significant electronic loads, you can select 3.5 (3 + 0.5)

(2) If the loads are not balanced and there is no significant electronic loads, you can select 4 (3 + 1)

(3) If the loads are balanced and there is significant electronic loads, you can also select 4 (3 + 1)

(4) If the loads are not balanced and there is significant electronic loads, you need to select even higher size for neutral (3 + 1.5)

For more detail, see these links:

http://cr4.globalspec.com/thread/52474/Suitable-Cables-for-high-harmonic-THD-generating-machines

http://cr4.globalspec.com/thread/43708/Harmonic-Current

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply Good Answer (Score 2)
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#19

Re: Neutral Cable Size

10/17/2013 12:20 AM

If the designer didn't know the nature of loads to be connected to the wiring, use a datalogger & record harmonics & neutral current and use an appropriate size of neutral conductor which may sometimes be as big as twice the phase conductor.

__________________
pnaban
Register to Reply
Register to Reply 19 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

cckla (3); lyn (2); msamad (1); North of 60 (5); pnaban (1); PWSlack (2); redfred (4); TonyS (1)

Previous in Forum: Liquid Rotor Starter   Next in Forum: Insulation Resistance Test Voltage