Inrush Current of 45 MVA Transformer

10/18/2013 10:22 AM

We hv transformer capacity of 45 MVA - 132 Kv/11 Kv in our substation. Current at HV - 196 A, LV - 2361 A. We want to back charge this transformer with 11 KV at secondary. As we have power plant and TG capacity is 14 MW, can we charge this transformer with no-load. what will be the inrush current and it's effect on TG. (Generator-11Kv,1329 A)

Register to Reply
Pathfinder Tags: inrush current transformer
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Inrush Current of 45 MVA Transformer

10/18/2013 12:45 PM

It depends on three things:

1) Is the 14MW TG (acronymectomy?) adequately protected against overload?

2) Is the cabling from there to the transformer adequately protected against overload?

3) Is the transformer adequately protected against overload?

If the answer to all three questions is "yes", then try it. If it works, then fine. If it doesn't, then though it is a non-starter, nothing got damaged and one can consider alternatives.

Did the local, tame HV Electrical Engineer get asked for advice at all?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Guru
India - Member - Sensors Technology Popular Science - Cosmology - Dream, Think and Act United Kingdom - Member - New Member United States - Member - New Member Canada - Member - New Member

Join Date: Aug 2006
Location: AM-51, Deen Dayal Nagar, Gwalior, Madhya Pradesh, MP 474001, India
Posts: 3418
Good Answers: 32
#2

Re: Inrush Current of 45 MVA Transformer

10/19/2013 12:28 AM

spghadei:

132 (kV) * 196 (A) = 25.872 MW @ primary side

// It appears that the transformer is over rated @45MW

11 (kV) * 2361 (A) = 25.971 MW @ secondary side

// It looks like it has not taken care of losses in the core hence can't be used for full 25.972 MW at the output.

For 14 MW this transformer should be adequate as you are using it at 56% of the rated power level. Just make sure that cables are OK and Transformer in good condition. Make sure you load less than 14 MW, taking care of losses adequately. Use some inrush current limiter to match the capacity of the Generator you are using.

Good luck.

__________________
Prof. (Dr.) Shyam, Managing Director for Sensors Technology Private Limited. Gwalior, MP474001, India.
Register to Reply Score 1 for Off Topic
Active Contributor

Join Date: Nov 2012
Posts: 21
#4
In reply to #2

Re: Inrush Current of 45 MVA Transformer

12/05/2013 3:29 AM

not over rated MVA rating=current*voltage*1.732 * 1(let pf=unity)(for 3 ph tr)

Register to Reply
2
Power-User

Join Date: Jul 2013
Location: Faridabad Near New Delhi India
Posts: 240
Good Answers: 34
#3

Re: Inrush Current of 45 MVA Transformer

10/19/2013 2:56 AM

There has been earlier discussion on this topic pl see below link

http://cr4.globalspec.com/browse/showtag?tn=transformer%20inrush%20current

You run a greater risk of damaging Overhang winding of stator for the reason that yours may be 3000rpm 2 pole machine which has bell shape overhang with long unsupported coils for this type of application.

Hence it is very likely that in first attempt you may cause cracks in overhang portion of stator winding.

Safe solution for you is , Stop TG, close its 11kV VCB, Close 11kV VCB of 45MVA transformer, all other loads on TG and 45MVA transformer bus disconnected, Set Voltage set point on AVR of TG to minimum, Start TG with excitation kept on, the transformer will energise slowly following voltage build up of TG thus avoiding any inrush. Once at steady rated speed set AVR of TG to nominal value.

Register to Reply Good Answer (Score 2)
Register to Reply 4 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

avra.setcl (1); powersolutionsFBD (1); PWSlack (1); Shyam (1)

Previous in Forum: Current   Next in Forum: Relay Switching on Delay

Advertisement