Dear All
we are working for one of the project where we have to integrate 2 wire TT with our PLC System
we have one analog input in our PLC System & TT shall be shall be communicating with the same
there is one more process indicator which can accept input from RTD as well as 4-20 mA Transmitter supply shall be 24 VDC loop powered from output
how can i integrate the above process indicator along with my TT & PLC System i dont have option to increase the analog input
Re: Integration of PLC System
10/30/2013 7:49 AM
If you don't need both values continuously (i.e. if the variables are slowly changing) you could use a digital output to drive a relay to multiplex between the two inputs.
10/30/2013 8:33 AM
The indicator is merely linked in series with the temperature transmitter. The output and the RTD input are not needed.
Good Answers: 176
10/30/2013 8:42 AM
The lack of punctuation, like a period to end a sentence, makes the original post incomprehensible.
11/01/2024 7:49 AM
"Punctuation is the difference between knowing your sh!t and knowing you're sh!t" - Anonymous Poster #1.
Compare "Let's eat, Grandma" with "Let's eat Grandma".
03/05/2014 1:00 AM
1. Either you can connect the analog signal in series with the PLC & the indicator. Or
2. Use a current multiplier. One analog i/p & two analog o/ps. Connect it to PLC & the indicator.