Alternator Voltage Frequency Change

10/31/2013 2:56 AM

We are using a six pole alternator coupled directly to induction motor of 2 pole to generate voltage at 150 Hz from 50Hz supply. Motor rating 5kW, Alternator (Generator) 5 KVA.

Syn. speed of motor = 120 f / P = 120 x 50 / 2 = 3000 rpm

Freq of voltage generated = 3000 x 6 /120 = 150 Hz.

The speed of rotation of motor / alternator(generator) is 2980 rpm.

Now we require supply with 100 Hz. If I de-couple the motor - alternator and drive the above alternator with pulley at approx 2000 rpm, will I get 100 Hz supply from this alternator.?? What will be new rated voltage and current of this alternator.??

Freq. of voltage required = 2000 x 6 / 120 = 100 Hz.

Thanks in advance

V.N.Prajapati

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#1

Re: Alternator Voltage Frequency Change

10/31/2013 9:07 AM

The 5KVA rating was given for the nominal speed of the alternator. Ideally, it should provide 5KVA at any frequency. As to the open circuit voltage at any any frequency, you would have to refer to the manufacturers documentation or determine it experimentally.

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#2

Re: Alternator Voltage Frequency Change

10/31/2013 12:04 PM

Easy homework problem that has been circulating around the web since 2009, last seen in Spanish 4 days before it appeared here.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Power-User

Join Date: May 2009
Location: CORDOBA ARGENTINA
Posts: 157
Good Answers: 4
#3

Re: Alternator Voltage Frequency Change

11/01/2013 12:06 AM

Usually this array is, seldom, used to generate High voltage to test transformers isolations at high frequency, so to avoid iron over saturation.

We use the same array , but with a variable frequency controller . No problem as it is used for a short time and low current.

Our array is a 20 Kva brush less generator, and a 4 pole motor, we use 20 Kva , is due to is the smallest we can get.

Our standard frequency is 50Hz

We use it at 50 , 100 ,and up to 120 Hz.

__________________
devitg
Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#4

Re: Alternator Voltage Frequency Change

11/01/2013 8:58 AM

You will get the 100Hz

Voltage: This is going to depend on the excitation circuit setting.

You probably want to know what should be the limit(!?) when you change the frequency. This is going to depend on the generator winding insulation and the allowed maximum current.