What is the Reason For 16A Type B and 2A Type C MCB Tripping Simultaneously

10/30/2013 11:09 AM

What is the reason for a 16A type B and 2A type C tripping simultaneously. The circuit is 240v with 100m of 2.5mm² cable from 2A type C to where short circuit occurred. Cable length from 16A type B to 2A type B 4m of 6mm.² The 16A type B should be replaced with a type C ?

UK wiring reg graphs for disconnection times have been checked and they are certain it should not occur.

I believe its because maximum fault current occurs quicker in the 16A type B at the same time with maximum fault current in the 2A type C resulting in both tripping simultaneously.

My manager cannot understand why the fault would not occur if a 16A type C fitted.

Any suggestions of a better way of explaining it would be helpful.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User
Engineering Fields - Control Engineering - Control Engineering Technical Fields - Education - Industrial Training Engineering Fields - Manufacturing Engineering - Manufacturing Training Engineering Fields - Electrical Engineering - Electrical engineering Training Engineering Fields - Instrumentation Engineering - Instrumentation Engineering United States - Member - New Member Engineering Fields - Energy Engineering - Become part of the larger group, change your world.

Join Date: Apr 2005
Location: Las Vegas, NV
Posts: 266
Good Answers: 1
#1

Re: What is reason for 16A type B and 2A Type C MCB tripping simultaneously

10/30/2013 11:23 AM

Is the 2A circuit load part of the 16A circuit load? If so, what is the peak load currently going through the 16A? The results may be what your manager needs to see to convince him to upgrade to type c.

__________________
AB PLC Training onsite, On-Line, training software and more. BIN95.com
Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2
In reply to #1

Re: What is reason for 16A type B and 2A Type C MCB tripping simultaneously

10/30/2013 11:30 AM

That would explain it, though the original poster would be better advised to look for the location of the short circuit and prevent its recurrence first. GA

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Jan 2009
Posts: 18
#4
In reply to #2

Re: What is reason for 16A type B and 2A Type C MCB tripping simultaneously

10/30/2013 2:54 PM

Retraining of technician involved to dead test before cutting cable.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8
In reply to #4

Re: What is reason for 16A type B and 2A Type C MCB tripping simultaneously

10/31/2013 4:22 AM

...before the individual becomes eligible for a Darwin Award? Good idea. Also, have a Permit To Work system in place so that there is due rigour to the assurance of safety before carrying out all work.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Active Contributor

Join Date: Jan 2009
Posts: 18
#3
In reply to #1

Re: What is reason for 16A type B and 2A Type C MCB tripping simultaneously

10/30/2013 2:52 PM

Peak load measured 9.5A

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#5

Re: What is the Reason For 16A Type B and 2A Type C MCB Tripping Simultaneously

10/30/2013 5:59 PM

Why is the 2A a type C?

BTW 100M of 2.5 will not meet UK regs for volt drop or disconnection time.

Time for a rethink.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#6

Re: What is the Reason For 16A Type B and 2A Type C MCB Tripping Simultaneously

10/31/2013 2:18 AM

One explanation here.

I think Google will be your best advocate and coach.

What's the ambient (cabinet) temperature at the 16A location?

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Participant

Join Date: Oct 2013
Location: Santa Ana, CA
Posts: 3
#10
In reply to #6

Re: What is the Reason For 16A Type B and 2A Type C MCB Tripping Simultaneously

11/01/2013 2:28 AM

People like us are the objects of google. If we know something about the question, and we share them here, google will provide our answer to people. So, we should never say google has all the answers. Hope you dont take it in a pessimistic way. :)

__________________
www.circuitbreakercity.com
Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#11
In reply to #10

Re: What is the Reason For 16A Type B and 2A Type C MCB Tripping Simultaneously

11/01/2013 3:33 AM

Not at all PK.

I totally dig what you are saying.

I wasn't trying to flick the OP off... I did throw in my two bob's worth as well.

The OP said or implied that he needs to convince his boss of what is required and probably even needs to get his own head around the problem too.

When educating my bosses (clients) I find that a third party citation(s) helps to get the point across (advocate) and also helps me to perform solo sanity checks (coach) as well.

Have a good weekend mate.

We've just created yet another object for Google.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Nov 2011
Posts: 286
Good Answers: 15
#7

Re: What is the Reason For 16A Type B and 2A Type C MCB Tripping Simultaneously

10/31/2013 3:45 AM

Although it looks as though they should discriminate it sounds as though one of the breakers might have gone off spec. I've seen 100A breakers coming out out at 70A on thermal and RCBOs where the RCBO part didn't work. Oddly enough the same manufacturer. Suggest renewing both MCBs with the same rating and type.

Register to Reply
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#9

Re: What is the Reason For 16A Type B and 2A Type C MCB Tripping Simultaneously

10/31/2013 12:39 PM

These MCBs have a limit current upto which the coordination is ensured. If the fault current happens to be more than the limit current, both the MCBs tend to operate for a fault downstream.

Vendors generally provide coordination tables for MCBs which will give more specific information.

__________________
Raghunath
Register to Reply Score 1 for Good Answer
Register to Reply 11 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

BIN95 (1); PeterKnauf (1); PWSlack (2); raghun (1); silverfox (1); TonyS (1); Wal (2); woobster1 (2)

Previous in Forum: How Can A PLC Reset The Actual Value Of An Absolute Encoder Of A Servomotor   Next in Forum: Alternator Voltage Frequency Change

Advertisement