Electrical Protection

11/08/2013 3:18 AM

We running a Generator 3 phase, 6.3 KV,10 MW. There is phase current difference of 40 Amperes among 3 phases due to loads, i.e if R and y phases are at 1200 A then B Phase is at 1160 A. we have all protection relays active in system such that Negative Phase Sequence fault protection, Zero sequence Fault protection etc. My Question is, with this unbalance of 40 Ampere is there any harm to Generator. The negative phase sequence protection is not detecting this and system is normal running. The Negative phase sequence setting is 0.4 A (Alarm at 0.5 Sec and Trip at 5 sec). With the normal Ground fault or two phase fault this relay detects. So please resolve my confusion.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
2
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Electrical Protection

11/08/2013 3:46 AM

The difference in currents between phases is indicative of single phase loads being connected downstream. Provided the circuit protection devices are set correctly, and everything in the thread so far suggests that they are, then this is a normal occurrence and no harm would occur to the generator. If a fault were to occur, then the circuit protective devices would operate, and still no harm would occur to the generator or the wiring; that is why they are there.

"Don't worry; be happy."

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Good Answer (Score 2)
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: Electrical Protection

11/08/2013 3:57 AM

40/1200 ≈ 3.3%. Not too bad.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Apr 2012
Posts: 732
Good Answers: 17
#3

Re: Electrical Protection

11/08/2013 11:53 AM

Calculate your PF, measure your THD and be happy that you only have that much imbalance.

It's pretty good in my eyes.

__________________
common knowledge...less common than common sense
Register to Reply
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#6
In reply to #3

Re: Electrical Protection

11/09/2013 10:36 AM

It is difficult to comprehend single phase loads at 6kV level.

I would like to believe that the unbalance is due to harmonics in the system owing to variable frequency drives etc. as you mentioned.

Another possibility is long single core cables laid in flat formation (as another poster mentioned).

__________________
Raghunath
Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#4

Re: Electrical Protection

11/08/2013 11:23 PM

Stop worrying. All is good.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
3
Power-User

Join Date: Jul 2013
Location: Faridabad Near New Delhi India
Posts: 240
Good Answers: 34
#5

Re: Electrical Protection

11/09/2013 1:05 AM

Permissible Negative sequence capability of 3 phase machines is governed by following relation

I22 x t = 20

Based on the CT ratio and secondary current, calculate I2, check that Negative Sequence relay is adjusted correctly. For setting protection relay we use value of 15 instead of 20 (leaving some margin for CT error and safety factor)

40A of unbalance in one phase for 10MW rating appears within limit. But must investigate whether it is actual unbalance load, or Turn Ratio error in that phase CT or wrong instrument.

I am sure protection CT and measuring CT must be different - so as a first check take a Clip on Am meter (Tong Tester) and check secondary currents in all 3 CTs and current wiring to relay -

If the currents in all 3 phases of Protection Relay are same whereas there is a difference in currents of ammeter - then it is a CT error.

If Currents in secondary circuit are balance then it is measuring instrument error.

If unbalance is confirmed by both protection and metering CT then check individual feeders for the cause of unbalance.

If particular phase (B) in all feeders has lower current then it can be:

1. Higher voltage drop in cable connections of B phase -check for any heating joint or connection.

2. Or may be that you are using single phase cables and there are not laid in Trefoil shape or if the length is long, cores are not inter-transposed.

3. Worst can be if inter-turn fault in stator coil of phase B (I hope that is not the case).

Register to Reply Good Answer (Score 3)
Participant

Join Date: Nov 2013
Posts: 2
#7

Re: Electrical Protection

11/12/2013 6:29 AM

Thanks to all my well wishers, i will follow the instruction and reply again

Register to Reply
Register to Reply 7 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

powersolutionsFBD (1); PWSlack (1); raghun (1); Shafqat Javed (1); The.Tinkerer (1); Tornado (1); Wal (1)

Previous in Forum: Merlin Gerin NS400N   Next in Forum: What is Equalization of "Load Cells"

Advertisement