Our Boiler tempr 500°C with 45kg/cm2 WC6 600Class Valve is suitable or not
Good Answers: 104
Re: WC6 600 Class Valve Regarding
11/24/2013 1:14 PM
Probably. What does valve manufacturer say? Do you have access to B31? If not . . .blah, blah, the usual.
Good Answers: 102
11/25/2013 2:10 AM
Here. Do your own imperial to metric conversions.
11/25/2013 3:43 AM
What did the valve vendor say during the telephone call?
11/25/2013 4:08 AM
In B 16.34, A 217 WC6 comes in Group 1.9 material.
At 500 Deg C, WC6 can take a maximum pressure of 51.5 bar for Standard # 600.
So yes 45kg/cm2 is not a problem.
Cheers.
Good Answers: 102
11/25/2013 4:14 AM
You're too generous sport.
Let the punters do some of the work themselves.
11/25/2013 4:53 AM
I get the point !
11/25/2013 10:23 AM
5 off-topic points, apparently.
11/25/2013 10:21 AM
That response is for the original poster, then?