Anonymous Poster #1

Difference Between Earth Leakage & Ground Fault?

11/25/2013 12:40 PM

Dear Friend

Please explain me the difference bw earth leakage & ground fault ; IS this 2 are same or different...what is the difference....?

Thanks

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Difference between Earht leakage & Ground fault?

11/25/2013 12:55 PM

Leakage can be unavoidable or unintentional. Faults are always unintentional.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Difference Between Earht Leakage & Ground Fault?

11/25/2013 2:26 PM

...and the difference between ground and earth in an electrical sense is the Atlantic Ocean, though this has been mentioned here before.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
5
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3

Re: Difference Between Earht Leakage & Ground Fault?

11/25/2013 2:49 PM

Earth leakage is a volcano. Ground fault is an earthquake.

Reply Good Answer (Score 5)
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#5
In reply to #3

Re: Difference Between Earht Leakage & Ground Fault?

11/25/2013 10:51 PM

Nice one!

I'm not having a good time but you've made me laugh :-)

__________________
The reports of my death are greatly exaggerated.
Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#6
In reply to #5

Re: Difference Between Earht Leakage & Ground Fault?

11/25/2013 10:54 PM
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8
In reply to #3

Re: Difference Between Earht Leakage & Ground Fault?

11/26/2013 2:31 AM

That's clever. GA (for cheek!).

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Active Contributor
Engineering Fields - Power Engineering - Thermal Power Plant Electrical Engineer

Join Date: Sep 2010
Location: INDIA
Posts: 18
#4

Re: Difference Between Earth Leakage & Ground Fault?

11/25/2013 10:11 PM

Hi,

- Earth leakage is few milli amps of current flowing to ground.Due to aging of insulation, dust deposited on insulation. Earth is leakage do not cause any tripping of protective devices.

- Ground/ Earth fault is few to hundreds of amps current flowing to ground.Due to Failure of Insulation, direct conduction of carbon dust on insulator. Ground/Earth fault cause immediate tripping of protective devices.

Reply Score 2 for Off Topic
Participant

Join Date: Feb 2011
Posts: 1
#9
In reply to #4

Re: Difference Between Earth Leakage & Ground Fault?

11/26/2013 11:42 AM

thanks !

For low voltage panel system earth leakage which is mA can be detected by ELR+Toroid+Shunt trip ;

But how can we detect earth fault which is hundreds of Amps(KA).....

Reply Off Topic (Score 5)
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#7

Re: Difference Between Earth Leakage & Ground Fault?

11/25/2013 11:03 PM

Same difference.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#10

Re: Difference Between Earth Leakage & Ground Fault?

12/10/2013 10:33 AM

Magnitude.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Reply
Reply to Forum Thread 10 comments