Can somebody help me with the mathematical analysis of 1. Contactors 2. Breaker 3. Overload Relay 4. Timer 5. Cable size needed to design a Star Delta starter for a 7.5 kw maximum load induction motor.
Re: Component Rating of a 7.5 kW Induction Motor Star Delta Starter
11/28/2013 10:33 AM
1. Sizing for Fuse , Breaker , Contactor and Overload relay for an Induction motor of 10 kW is given in this presentation.
http://www.slideshare.net/salehkhan/motor-control-centre
You can size equipment for 7 kW Motor Control Center (MCC) .
2. Select the Timer based upon the load condition. Generally switching take place (from Star to Delta) when motor reaches 70 to 80 % of its rated speed.
3. Select the Cable size keeping in mind 125 % of Motor Full Load Current
11/28/2013 12:38 PM
Yep. Somebody who has access to British Standard 7671 and knows how to use it can. In the meantime, wait until this person shows up. The job role is Electrical Engineer.
Good Answers: 170
11/29/2013 7:06 PM
send me ur mail id thro this forum'a mailbox so that i could send you a presentation on type-2 co-ordination for motor starters