Mechanical Design of Transmission Line

12/05/2013 11:40 PM

Hi,

Mechanical parameters are also important in the design of transmission lines. What all are to be determined. I think the following are sufficient.

1. Max sag (at 75oC, and no wind? , or considering wt of ice, conductor and wind?)

2. Max tension (assuming suitable factor of safety of 2.5 (IEC))

3. Stretched and unstretched length of transmission line (eg for everyday temp and max temp of 75oC).

4. Sag and tension under erection conditions from worst weather conditions.

Any others to be determined?

Regs,

sks

CR4 ADMIN - thread closed

This thread has been closed because it is a duplicate. Please add your comments to the original thread.

Register to Reply
This discussion was "closed" on 12/06/2013 9:38 AM. No new comments are allowed.
Message from admins:
duplicate thread
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Mechanical Design of Transmission Line

12/05/2013 11:53 PM

Anonymous Poster #1

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#2

Re: Mechanical Design of Transmission Line

12/06/2013 12:02 AM

In reply to both posts:

Lyn is correct. Simply stating max sag isn't enough, you have to specify the operating conditions. Like everything else in electric power engineering, it's part of a system, and there are considerations that go beyond the electrical aspects.

There's max sag when the transmission line is being strung, when it's being operated under no, light, normal, and emergency loading conditions, under varying weather conditions, when crossing over highways, railway tracks, vegetation, different combinations of some or all of the above, and ultimately the point at which the line will have been stretched beyond its ability to return to normal when the overload is removed.

You pick the condition, there's a formula or a rule for it, and it's as much an art as it is a science.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#3

Re: Mechanical Design of Transmission Line

12/06/2013 9:01 AM

How many times have you been told "do your own homework!"

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Register to Reply 3 comments
This discussion was "closed" on 12/06/2013 9:38 AM. No new comments are allowed.
Message from admins:
duplicate thread
Copy to Clipboard

Users who posted comments:

lyn (1); RAMConsult (1); TonyS (1)

Previous in Forum: Max Sag on TL   Next in Forum: Corona Loss for 132 kV Single CKT Line.

Advertisement