Transformer Neutral Earth Pit Problem.

12/06/2013 10:08 AM

Dear all

Today we face a problem in our 33/6.3/.415Kv Transformer.

Earth pit for Neutral solid grounding of secondary(.415KV) both Earth pit & its surroundings got too much heated,when we checked Neutral to Body earth voltage that is 230v & R-Y-E=415V WHILE B-E=0V.so that we take a cable & touches the neutral to another earth pit then a spark will come & after that everything is ok.mean Neutral to earth voltage is 0V.& also B-E=230V.

we still not understand what actually...is it neutral disconnection problem?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#1

Re: Transformer Neutral Earth Pit Problem.

12/06/2013 11:30 AM

If everything has "...got too much heated..." then it's time to find out why so much current is flowing. You may have a severely unbalanced system, a low-level earth fault somewhere, and/or are in need of additional earthing pits and a way to keep them wet enough to keep on "earthing" for you.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#2

Re: Transformer Neutral Earth Pit Problem.

12/06/2013 1:11 PM

Your post is confusing. I will make the assumption that you have a wye connected secondary with the neutral point connected to your earth pit. The voltage between phases RB, RY or YB should be 415 volts. The voltage from R,B or Y to neutral/earth should be 230 volts. Neutral to E should be zero. In your post you say"B-E = 0 volts." The only way that could happen is if you had a delta connected secondary with B grounded. Your statement R-Y-E = 415 volts can not be right. What do you mean by "touching the neutral to another earth pit" ? You can have a difference in potential between earth pits. You may have sparking occur in this situation. Please add some additional information.

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#3

Re: Transformer Neutral Earth Pit Problem.

12/06/2013 5:06 PM

Given the figures you state you've lost the neutral star point earth connection and now have a phase to earth fault. Is the neutral solidly bonded or via a NER? Failure of the NER followed by a phase to neutral will give the figures you quote.

As for getting sparks when you connected the two pits, I surprised you didn't get a big bang!

__________________
The reports of my death are greatly exaggerated.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#4

Re: Transformer Neutral Earth Pit Problem.

12/07/2013 8:58 AM

I think the same as TonyS in the "first pit"case the neutral was not grounded but phase B was.

In the second case "pit no.2" a short-circuit occurred between phase B and the neutral through the Ground , the connection to ground of phase B burnt out and delivered phase B from its earth connection.

__________________
Julius
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#5

Re: Transformer Neutral Earth Pit Problem.

12/07/2013 1:08 PM

Typical "Indian" way of problem solving?

Register to Reply
Commentator

Join Date: Apr 2009
Location: CG
Posts: 64
#6
In reply to #5

Re: Transformer Neutral Earth Pit Problem.

12/08/2013 10:02 AM

Absolutely not

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#9
In reply to #6

Re: Transformer Neutral Earth Pit Problem.

12/09/2013 4:33 PM

"so that we take a cable & touches the neutral to another earth pit then a spark will come & after that everything is ok".

Then what? Rather than analysing the problem, you brag that you touch the neutral to another earth pit & gosh! spark will come????

Had it been a site with inflammable or explosive materials, what your 'spark' could have created?

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#10
In reply to #9

Re: Transformer Neutral Earth Pit Problem.

12/09/2013 11:13 PM

A well deserved Darwin Award....

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Commentator

Join Date: Apr 2009
Location: CG
Posts: 64
#11
In reply to #9

Re: Transformer Neutral Earth Pit Problem.

12/10/2013 9:39 AM

As we think neutral is disconnected from its pit so we just connect one pit with another and a very little spark came just like we discharge a fan capacitor.

Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#7

Re: Transformer Neutral Earth Pit Problem.

12/08/2013 2:05 PM

both Earth pit & its surroundings got too much heated

Do you mean that the ambient temperature got really high, the ground dried up and the earth pit resistance increased?

__________________
jack of all trades
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8

Re: Transformer Neutral Earth Pit Problem.

12/09/2013 1:04 PM

The solution is to isolate the installation from all sources of power on the basis of danger to life and property, and to hire a qualified HV Electrician to put things right. Wasting time on CR4 only increases the chances of hurting/killing someone. So do it now/this morning/immediately.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 11 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

7anoter4 (1); electricalexpert65 (2); jack of all trades (1); lalit_nawada (2); PWSlack (1); RAMConsult (2); TonyS (1); wareagle (1)

Previous in Forum: Electric Furnace   Next in Forum: Rotor Current (Induction Motor)

Advertisement