Surge Protection Device

12/20/2013 10:02 AM

we need to install a surge protection device on an electronic control card.the card has an input port supplied directly from transformer at 230vac single phase for sensing the mains voltage. but problem is that the supplier of the card gave us a 3phase type 3 SPD (model :PT 4-PE/S-230VAC/FM , make:pheonix contact) with Uc=355vac (L-N). and Uc=255vac (N-PE). can we use this 3 phase s.p.d for our single phase 230vac application.the stated Uc=355VAC seems too higher for our single phase application.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Surge protection device

12/20/2013 11:35 AM

Why don't you get the correct device and do the installation properly.

If you ordered the incorrect part, the supplier will probably exchange it for the correct one.

If you don't have anybody on staff who knows the answer, then you should hire a knowledgeable electrician. (based on your historical record, this must be the case)

So far, you have been extremely lucky not to have killed anyone.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#2

Re: Surge protection device

12/20/2013 1:52 PM

Uc - does that mean clamp voltage??

There has to be a good margin above normal voltage for a so-called surge suppressor to cover short term voltage rises without getting burnt out. 355 volts for 240 volts normal does not seem unusual to me. Usually, they are clamping "spikes" not attempting to be a voltage regulator.

Register to Reply
Commentator
Engineering Fields - Power Engineering - New Member

Join Date: Feb 2009
Location: Tamil Nadu
Posts: 66
#3

Re: Surge protection device

12/21/2013 3:26 AM

This is insulation protection co ordination for indoor low voltage system. Pl.do take support from a field person.

__________________
Better not count the cent if the risk is many many dollars.
Register to Reply
2
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#4

Re: Surge protection device

12/21/2013 6:15 AM

I "googled" your part number. It came up immediately, fortunately. You could have written it was a Phoenix Contact product!

http://www.phoenixcontact.com/local_pdf/he_IL/PxC_-TT_-selection_for_POWER.PDF

They do not appear to make a two pole version - so if you wanted live and neutral protected, the 3 pole/3 phase version could be used.

It is a lightning protection device, commonly specified as 1.2 microsecond rise time and 50 microsecond fall.

There is no problem with this device for 230V two pole use, except two single pole devices might cost less and use less space.

The data sheet per web reference above indicates voltage is clamped to <= 1.5 kV.

If this electronic card is just sensing voltage it is probably OK with 1.5kV spike. If you do not think that is good enough, then a filter may be added.

You have not given the current consumption of the protected equipment, relevant to any further filter or spike suppressor, if needed.

67model

Register to Reply Good Answer (Score 2)
Register to Reply 4 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

67model (2); Jans (1); lyn (1)

Previous in Forum: Electric Motors   Next in Forum: A Switch that Can be Controlled by Wi-Fi

Advertisement