Thanks to "Electric Power Systems" by Weedy and Cory, John Wiley & Sons page 456-7. ISBN0 47197677 6
Example 11.1
Determine the time of operation of a 1 A, 3 s overcurrent relay having....
a plug setting of 125 per cent
and a time multiplier of 0.6.
The supplying CT is rated 400: 1 A and the fault current is 4000 A.
Solution
The relay coil current = (4000/400) x 1 = 10 A.
The normal relay coil current 1 x (125/100) = 1.25A.
Therefore the relay fault current as a multiple of the plug setting = (10/1.25) = 8.
From the relay curve (Figure 11.16), the time of operation is 3.3 s for a time setting of 1.
The time multiplier (TM) controls the time of operation by changing the angle through
which the disc moves to close the contacts. The actual operating time = 3.3 x 0.6 = 2.0 s.
But note this is not a CDG61 curve. By memory, it may be very inverse time.