Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73

Burnt Outlet Revisited

01/06/2014 1:09 PM

Thank goodness for electrical inspectors. They have probably done more to protect people than could be measured.

The issue came up because of a space heater. Most hair dryers use nearly the same amount of power, just not long enough to see problems that are clearly the result of poor quality control in a factory. I know this because my space heater cord was always warm to the touch after about 20 minutes.

I went to the hardware store, bought a new plug, and replaced the one on the end of my cord. Now the cord never gets warm. When I cut open the original plug I saw the problem. On the offending side of the plug, fewer than half of the strands were clamped to the brass blade. Well, no wonder it got so hot.

All of the comments to the previous thread meant well and beat all around the bush. I did agree with the good information regarding the proper use of the electrical code. It is interesting that the electrical code was developed by the fire department. It tells you about who was the most motivated to stop sloppy practices. But, I don't think anybody mentioned the root cause. And that was, poor quality control at the factory that molded the original heater plug.

Just pointing out a problem with too much information. It usually causes the same (wrong) problem to be addressed over and over again. Appliance cords should never get hot. Ever!

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#1

Re: Burnt Outlet Revisited

01/06/2014 2:12 PM

no one mentioned the cause? "a loose connection regardless of age will do all the damage you describe. it could have simply been a bogus plug that would have cooked in any receptacle"<my quote

Register to Reply Score 1 for Good Answer
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#2

Re: Burnt Outlet Revisited

01/06/2014 2:54 PM

Along with a multimeter and a jiggler every toolkit should have a non-contact infrared thermometer, for under 30 bucks you can easily spot and isolate this type of failure in less time than it takes to post (and repost) on CR4.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru

Join Date: May 2009
Location: Wolfe Island, ON
Posts: 1357
Good Answers: 109
#3

Re: Burnt Outlet Revisited

01/06/2014 3:24 PM

In the original Burnt Outlet thread Oscarphilips posed:

"OK, the only reason I responded is because I feel this point is important ... how do the code writers expect the general public to know not to plug a cord connected heater of this size into a 15 ampere outlet, and how does the general public even recognize a 15 ampere outlet?"

I agree the manufacturer (aside from product quality) should be more liable for their product and assure the public it cannot be used where it should not be used. In the case of the heater, Oscar pointed out that the heater was a continuous duty product and would draw significant amperage while on. I think these units should be equipped with a 20 amp plug (you know them as looking like a standard 3 pronged 120v plug but one of the prongs will be sideways. A 20 amp plug will have a T receptacle than could accommodate either 20 or 15 amp devices plugged into it. A 15 amp receptacle will look like a standard 3 prong receptacle and accept those devices that do not have high amp continuous operation (like a lamp).

Oscar is right, there is a flaw in the rules of making devices and they should be corrected before people get hurt. The onus should be squarely put on the manufacturer of devices that exceed a level of continuous duty that would be unsafe for the standard 15 amp plug. Home owners will not make the distinction unless they can only plug into 20 amp plugs because they are the only receptacles that will work period. Maybe some fire department will get hot on this idea or insurance company.

__________________
If they want holy water, tell them to boil the hell out of it.
Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#4
In reply to #3

Re: Burnt Outlet Revisited

01/06/2014 4:18 PM

slow down, I don't think you get it, a 20A receptacle is just that, a receptacle rated to handle a continuous 20 amp current flow.so it will handle 1,2,3,4,5,6 etc. there is no receptacle rated to match 12.5 exactly.

Register to Reply Score 1 for Off Topic
Guru

Join Date: May 2009
Location: Wolfe Island, ON
Posts: 1357
Good Answers: 109
#5
In reply to #4

Re: Burnt Outlet Revisited

01/06/2014 4:42 PM

I understand. The receptacle is not the problem, it is the device. Oscar went on to further explain:

"I would classify your heater as a continuous load, so the branch circuit should have an allowed ampacity of not less than 125 percent of that load, or 12.5 amps (from rely #5) * 125% = 15.625 amps; so

  • a 15 ampere circuit would be inadequate §210.19(A)(1)(a), and
  • a 15 ampere rated receptacle would be inadequate §210.21(B)(2)."

With a proper 20 amp plug on a device that has high amperage on continuous duty, there will be no mistake about where to plug the unit. A DIYer will still be able to use 14 gauge wire and a 20 amp receptacle alas. But at least someone would not be able to plug it into most outlets found in houses. The rules for industrial devices is very different but should be the same for devices used in residential houses.

__________________
If they want holy water, tell them to boil the hell out of it.
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#6
In reply to #5

Re: Burnt Outlet Revisited

01/06/2014 8:44 PM

Actually, neither. The fault lies with the NEC wording, a piece of fixed equipment; i.e., hard-wired, is considered a continuous load, while a piece of portable equipment is not (never mind that either piece could be left on "continuously" for more than 3 hours).

Unfortunately if heater manufacturers were forced to put on a 20amp plug most homeowners couldn't plug them in, the result would be that the manufacturers would simply cut the current back to 11 Amps to allow the use of a 15 Amp plug/outlet. Worst still, our uneducated DIYer will simply purchase a 20 Amp outlet and replace the 15 Amp one. Another Darwin Awardee in the making.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Score 1 for Good Answer
Guru
Safety - Hazmat - New Member Engineering Fields - Retired Engineers / Mentors - New Member Engineering Fields - Piping Design Engineering - New Member Hobbies - DIY Welding - New Member Fans of Old Computers - PDP 11 - New Member

Join Date: Feb 2007
Location: Stronger Than The Storm
Posts: 2394
Good Answers: 203
#12
In reply to #6

Re: Burnt Outlet Revisited

01/07/2014 1:36 PM

Also not only would homeowners replace the 15 amp socket with a 20 amp, but if they were cheap and had some "ingenuity" they would take a pair of pliers and bend the one blade of the plug so that it formed the parallel shape of the 15 amp plug.

Somehow electricity draws "Darwin Awardee's" like lights to bugs and sweaty skin to a mosquito. Unfortunately scratching it just makes it get worse with little relief.

Good Luck, Old Salt

__________________
Any day on the green side of the grass is a GREAT DAY!, --- me +++++++++. I believe creativity is an inherent part of everyone. --- Kermit T. Frog
Register to Reply
Guru
Popular Science - Cosmology - Let's keep knowledge expanding Engineering Fields - Retired Engineers / Mentors - Hobbies - HAM Radio - New Member

Join Date: Dec 2006
Location: North America, Earth
Posts: 4528
Good Answers: 106
#10
In reply to #5

Re: Burnt Outlet Revisited

01/07/2014 12:39 PM
__________________
“I would rather have questions that can't be answered than answers that can't be questioned.” - Richard Feynman
Register to Reply
Guru

Join Date: May 2009
Location: Wolfe Island, ON
Posts: 1357
Good Answers: 109
#11
In reply to #10

Re: Burnt Outlet Revisited

01/07/2014 1:18 PM

The case as described was really a 15 amp (14 gauge wire) service with a 20 amp breaker creating the first problem and a no/no if OscarP is correct. The second no/no, as I see it, was that the device was under-rated but that was likely because it was portable. As such it had a standard 120 volt 15 amp plug and no rules were necessarily broken by the manufacturer. When I worked in a lab, portable lab heaters were equipped with specialized plugs on 120 volt but could only be used at certain outlets. I never understood why until later but a lab code is more stringent than a residential wiring code. All portable devices in the lab were considered continuous duty. My background is not in electrical but I would err on the side of caution when it came to using portable devices. It has been cold recently in our area and many portable heaters are in use. But how does one know when to use a 20 amp plug if the manufacturer sends it out with a 15 amp plug? I think that is the point OscarPhilips was making.

__________________
If they want holy water, tell them to boil the hell out of it.
Register to Reply
2
Guru
Safety - Hazmat - New Member Engineering Fields - Retired Engineers / Mentors - New Member Engineering Fields - Piping Design Engineering - New Member Hobbies - DIY Welding - New Member Fans of Old Computers - PDP 11 - New Member

Join Date: Feb 2007
Location: Stronger Than The Storm
Posts: 2394
Good Answers: 203
#7

Re: Burnt Outlet Revisited

01/06/2014 10:01 PM

NotUrOrdinaryJoe-

I personally don't "Thank goodness for electrical inspectors"; I thank goodness for good electrical inspectors. As with many trades and professions there are great ones, good ones and terrible ones. The terrible ones are the ones who catch all the attention while the others diligently try to advance the level of their profession/trade. I personally have seen some really dumb ones in both my personal dealings and especially in my tenure in industry and engineering. No discrimination or disparaging remarks intended towards anyone but there are some out there that are a shame to all the good ones. Fortunately they are not the majority.

"All of the comments to the previous thread meant well and beat all around the bush" is an inaccurate, untrue and damning statement about the answerers and their postings and is uncalled for. If the past thread is reviewed it will be seen that the plug issue with improper connections between the prongs and the wire were discussed several times. "But, I don't think anybody mentioned the root cause" should be reviewed. I know I and several others described the plug as a potential problem. I stated: Check the wiring on the heater and the plug. Molded plugs very often only have a simple mechanical connection to the wiring which causes it to heat due to the resistance of the poor wire/blade connection. Replace the wire and replace the plug with one that has screw connections to the wire." This was not the only posting to broach the subject; several others mentioned these poor connections.

As personal testimony to the plug problem, I had to replace a wall socket yesterday (done as an overly cautious potential problem) and the plug on my wife's iron. She companied that there was a puff of smoke when she unplugged her iron and the plug was warm. I knew immediately what the root cause and the remediation was. She doesn't turn the iron off when she pulls the plug out of the outlet by the cord. Molded plugs don't have much strain relief to them. Socket was replaced because I might have been wrong and a socket is much cheaper than a new house.

Yes, the National Electrical Code was started by the National Fire Protection Association, now called section 70 of the codes. It is also the longest standard there is of NFPA's. They started it but wisely they chose to have most of the members of the section 70 committee from the electrical profession. As a firefighter, I wouldn't want to have any of my fellow firefighters wiring my house nor would I want an electrician or electrical inspector putting out a fire if they were untrained in it. This is also the reason why firefighter training includes NOT pulling the meter due to adverse conditions or arc flash. NFPA standards are not written as laws, they are a standards writing organization and their standards are only law when they are adopted by the local governing bodies.

Yes, too much information can cause confusion but that is one of the hazards of using a forum such of this as a "bible of electricity". The OP asks a question of hundreds of individuals and gets numerous varied answers, some excellent and some not so good. It is the OP's responsibility to pick the good ones out and reject the not so good ones.

This posting is not intended as a personal attack on you or anyone else. That does not have a place on CR4. I would suggest revisiting the previous thread to refresh what had been submitted. I know there are many times I would like to retract some part or all of a posting or that I could have been clearer on what I was intending to say. I know I am human with my faults and weaknesses, just ask my wife she can spend at least several hours listing them. Most of your posts in the past have been extremely good and helpful to the OP's. Again, this is not intended to be an attack on you or anyone else. It is intended to be constructive comment.

Good Luck, Old Salt

__________________
Any day on the green side of the grass is a GREAT DAY!, --- me +++++++++. I believe creativity is an inherent part of everyone. --- Kermit T. Frog
Register to Reply Good Answer (Score 2)
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#8
In reply to #7

Re: Burnt Outlet Revisited

01/07/2014 8:52 AM

This posting is not intended as a personal attack on you or anyone else.

and

Most of your posts in the past have been extremely good and helpful to the OP's.

Hey Old Salt,

WTF? Were you a lawyer or maybe a Judge before you became a firefighter? OK, I admit that I scanned over most of the jumping to conclusions in the innumerable responses and missed some details. And you seem to always give good answers, so let me be clear in my next statement that I intended no harm to you or anybody else that may have responded with nonsense. I simply get tired of all the misfits responding with their useless babble. There seems to be no shortage.

I never qualified myself as an expert and I really don't care if anybody takes my advise or not. In fact, I have grown tired of this mockery of a blog.

I think I'll go home and burn down my house out of spite. Excuse me for living!

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Register to Reply Score 1 for Off Topic
Guru
Safety - Hazmat - New Member Engineering Fields - Retired Engineers / Mentors - New Member Engineering Fields - Piping Design Engineering - New Member Hobbies - DIY Welding - New Member Fans of Old Computers - PDP 11 - New Member

Join Date: Feb 2007
Location: Stronger Than The Storm
Posts: 2394
Good Answers: 203
#9
In reply to #8

Re: Burnt Outlet Revisited

01/07/2014 11:22 AM

NotUrOrdinaryHoe-

I personally did not want to invoke a response like your most recent. This blog can only be as good as people, such as you and I, make it. Yes, if all the misfits, idiotic and deceitful persons could be eliminated it would be a great blog. Fortunately they are a small minority and most are intelligent, helpful and nice people who want to assist another one as best they can. The blog is only as good as the participants make it. As with you sometimes I'm sure, I become extremely frustrated with some of the content of it.

Also WTF! I was not a lawyer or judge prior to becoming an engineer and also a volunteer firefighter. I'm just another guy who tries to make the world a little better here on earth until I breathe my last breath on earth. As I see it I post many more that are not good answers than those that are good. I often see where I could have said something so it is more understandable, more accurate, etc. Many times I regret submitting any answer at all but I will stand by any of them until someone shows me where I was wrong or leads me to a better understanding. I too am tired of the misfits and babble although some others think I am one of them.

Please do not reduce your participation in this blog. You have a lot to continue to contribute and it would be a loss to others to have you leave.

Please don't burn your house out of spite. 80% of the firefighters in the USA are volunteer and we all have many other things to do in our lives. Besides it is a very disturbing feeling when I see what people go through when they have lost all their possessions and keepsakes. The hard part to me is to see what it does to the people and not the destruction.

Good Luck, Old Salt

__________________
Any day on the green side of the grass is a GREAT DAY!, --- me +++++++++. I believe creativity is an inherent part of everyone. --- Kermit T. Frog
Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#13
In reply to #7

Re: Burnt Outlet Revisited

01/08/2014 9:21 AM

Well... that certainly contributed allot to this forum.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Guru
Safety - Hazmat - New Member Engineering Fields - Retired Engineers / Mentors - New Member Engineering Fields - Piping Design Engineering - New Member Hobbies - DIY Welding - New Member Fans of Old Computers - PDP 11 - New Member

Join Date: Feb 2007
Location: Stronger Than The Storm
Posts: 2394
Good Answers: 203
#14
In reply to #13

Re: Burnt Outlet Revisited

01/08/2014 11:30 AM

North by 60-

Well...it certainly contributed a lot to this forum. I answered a posting that was directed to me. The reply was done this way instead of by direct CR4 mail because the original was observed to any, and possibly all, participants of this blog. Therefore if anyone had any concerns or interest in his original posting to me they could also share in this reply to it.

No, this is not my preferred way to use this forum but neither is it to make any sarcastic remarks to or about other's postings. Perhaps there is some confusion concerning a "Re: Burnt Outlet Revisited" and "Re: A Question About 3-Phase Delta". My memory is certainly not perfect, very very far from that, but I seem to recall a similar situation there.

Therefore does "Well... that certainly contributed allot to this forum" contribute anything constructive to this forum? Remember you are the one who initiated these. I have no desire to continue this wasteful correspondence initiated by a sarcastic comment. I have neither the time, inclination or desire to waste my energies in this sarcastic manner on dribble and babble.

Good Luck, Old Salt

__________________
Any day on the green side of the grass is a GREAT DAY!, --- me +++++++++. I believe creativity is an inherent part of everyone. --- Kermit T. Frog
Register to Reply
Active Contributor

Join Date: Dec 2013
Location: Ohio, USA
Posts: 15
Good Answers: 4
#15

Re: Burnt Outlet Revisited

01/09/2014 1:41 PM

In your post you stated:

But, I don't think anybody mentioned the root cause. And that was, poor quality control at the factory that molded the original heater plug.

This is a jump, to assume that the factory molded plug was bad. After some 53 posts in that thread, we never did find out what the real problem was. The original poster, DirtyPhoenix, has only ever posted to this web site 3 times, all in relation to the original Burnt Outlet discussion.

His posts we learned

  • Year and half ago a new outlet on its own breaker was installed
  • The landlord paid a licensed electrician to do the work
  • Last week the posted smelled smoke and noticed the outlet and front of cord were "burnt" and really hot.
  • The posted noticed that the breaker is 20amp, the outlet is 15amp, and the wire is 14 gauge.
  • The posted used the outlet to run a register type space heater in the winter, so it sees a bit of use and
  • heater is 12.5 amps and 1500 watts

The original posted never provided any additional information or assessment of the actual appliance cord or plug.

Register to Reply
Register to Reply 15 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Fredski (2); kevinm (3); North of 60 (1); NotUrOrdinaryJoe (1); old salt (4); OscarPhilips (1); RAMConsult (2); StandardsGuy (1)

Previous in Forum: Search By Triaxial High Voltage Cable   Next in Forum: Inverter Output - Handling phase-neutral aspects

Advertisement