Anonymous Poster

Transformer selection, Fault Current calculation

06/10/2007 3:47 AM

Hi Everybody,

I have joined as Electrical Design Er. in a Consultant.

Can anyone tell me how to size the transformer & DG. How to Calculate Maximum Demand.

Also Fault level calculation.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Associate

Join Date: May 2007
Posts: 27
#1

Re: Transformer selection, Fault Current calculation

06/10/2007 5:34 AM

Firstly,

Not being horrible but how did you get that job if you can't do these simple formulas

Secondly

We need more information on what you are trying to achieve in order of you to get better and more relating anwsers to your question??????????

________________

Thank you and good night

Reply
Anonymous Poster
#5
In reply to #1

Re: Transformer selection, Fault Current calculation

06/15/2007 2:37 AM

Dear Sir,

I dont think this to be HORRIBLE to get this job. As a fresher I am very curious to know from the experienced people in this field. In current trend most Engineering graduates coming out from college are jumping into IT field. So atleast appreciate me for my curiousity rather than discouraging me by saying it as horrible.

Cheers

Reply
Participant

Join Date: Dec 2007
Location: Palestinian living in Dubai
Posts: 2
#6
In reply to #5

Re: Transformer selection, Fault Current calculation

12/19/2007 5:07 AM

Dear Fresh Engineer...
What i gonna tell you is that go ahead and with a little time you will be an expert in your field...I came to work in Dubai as an electrical engineer one and half a year ago from Palestine...i have no experience at all as i spent 2 years after graduation from college working as a project cordinator with Cooperazione Italiana in Palestine..i am trying to conduct you to the fact that no one is born educated.... Another thing i have to tell you if the system you are working in is just like the system in Dubai, it is that i do not prefer any fresh engineer to start his working life as a consultan since he must work as a contractor or simply in the fields or sites, by this he will be able to learn easily and rapidly than beeing a consultant.....My little opinion!!!
Rami Bahlaq
-------------------------------------------------
Sebastia.....You are always in mind!!!!!!!

__________________
Sebastia......You are always in mind!
Reply Off Topic (Score 5)
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#2

Re: Transformer selection, Fault Current calculation

06/10/2007 4:14 PM

Hi guest ,

Don't worry .You have started only . Do not get panic. Everybody starts the job with lot of educational background and Will to learn. So start. First you must know what is your requirement. Find that out first. So start from the beginning. Do not jump to start designing. Your load assessment , regular requirement ,Type of load continuous process, intermittent load ,jerk load like metal, cutting, press, welding etc.

Next step availability of power , Distance from the source, From where the power to sourced ,either the supplier will provide power at site, what should be the incoming voltage , what is the load voltage.Above all what is the financial capacity of the company who give the order to you. Make an initial paper comprising all this and tell me then I shall tell you how to go ahead .Best of luck .Start your job

Reply
Participant

Join Date: Jan 2009
Posts: 1
#10
In reply to #2

Re: Transformer selection, Fault Current calculation

01/07/2009 8:52 AM

Hi,

Vi Abraham, I have read some of your postings and they look very knowledgeable. Would you mind sending me your e-mail add so that if i also have a question i will be sure to get in touch with you. I am in protection engineering...South Africa.

Reply
Anonymous Poster
#3

Re: Transformer selection, Fault Current calculation

06/10/2007 11:51 PM

It's a little difficult to answer all of your questions but here are a couple of items:

1) There are tables in the NEC that provide data on how to estimate the demand of a facility. For example, the estimated demand of a school would be: Building square feet x 15 VA/square foot. (49,000 S.F bldg X 15 VA/S.F = 735 KVA)

2) The transformer to feed this load would be the next standard size of commercial transformer, assuming a 3 phase supply, this would be 750 KVA transformer.

3) The per phase current available from this transformer would be

2040 A for a line-to-line voltage of 208V, 902 A for a line-to-line voltage of 480V, etc.

4) The distributed generation would be sized similarly.

5) A simple short-cut for calculating short circuit, assume an infinite source bus, the maximum fault current available at the secondary terminals of a 150KVA 13.8KV-480V transformer with a 2% impedance can be calculated by:

Short Circuit Current = (150,000VA)/(sqrt(3)*480*(2/100))= 9,022 A

You should really get your hands on a copy of the IEEE Buff Book "The IEEE Recommended Practice for the Protection and Coordination of Industrial and Commercial Power Systems" to develop a solid understanding of fault current calculations.

Reply Score 1 for Good Answer
Guru
Engineering Fields - Systems Engineering - New Member Hobbies - Model Rocketry - New Member

Join Date: Dec 2006
Location: Long.92E,Lat.26N
Posts: 1336
Good Answers: 14
#4

Re: Transformer selection, Fault Current calculation

06/11/2007 2:43 AM

Congrats!!

Please LIST THE CONNECTED LOADS(KW's+ load descriptions in time)

A description -what runs at same time,what loads are ON, all the time.

You are talking of Transformer & DG- you want to feed which loads from Diesel Genset?

Do you want to rate the Transformer for full utilization NOW or less- or keep Reserve for growth? How much reserve?

Fault level of Transformer/Line incoming/Of DG ?

Reply
Anonymous Poster
#7

Re: Transformer selection, Fault Current calculation

01/04/2008 12:20 AM

There are various parameters for T/F selection

main are given below

1. Voltage level

2. Frequency

3. type of load

4. For genration / distribution

5. Indoor / out door

6. temperature

7. overload timings

8. Fault level

As far as DG size is concerned you can take help from this relation

KVA = E x I / 1000 ---------- Single phase

KVA = E x I x 1.73 / 1000 --------- 3 phase

You can calculate fault level KVA or MVA rating Divided by % impedance

Remember that Fault level is nothing but the amount of current that flows in the network during fault or short circuit

---Jazsy Dhariwal

Reply
Anonymous Poster
#8

Re: Transformer selection, Fault Current calculation

01/30/2008 9:22 AM

Transformer , motor and breaker MVA fault current calculation sent to me.

Reply Off Topic (Score 5)
Anonymous Poster
#9

Re: Transformer selection, Fault Current calculation

07/18/2008 4:45 AM

Dear Sir

pls tell impendence selction on transformer 2500 kva ,11/0.440 kv. if we go on higher side impendence what is benfit or loss

Reply
Anonymous Poster
#11

Re: Transformer selection, Fault Current calculation

04/03/2009 5:53 AM

Hi,.

The Transformer sizing will depend upon the nature of the load that is resistive ,inductive like motors then calculate the toatal current consumed by all the load in running condition and then use the formula P= sqrt3*.433* current calculated that will be the KVA of the Transformer ,also if the load are variable or intermittent than u have take consideration of the starting condition of the largest motor also.

Reply
Participant

Join Date: Jan 2010
Posts: 2
#12

Re: Transformer selection, Fault Current calculation

01/30/2010 11:11 AM

Hi Every One,

I have following questions to this forum

What is the maximum & minimum fault lavel of a 400KV S/s? How it is calculated? If we know the Phase to phase & phase to ground fault MVA of a S/s how can we calculate maximum & minimum fault of the S/s?

It will be help full if any one reply.

Reply
Reply to Forum Thread 12 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (6); Dubai Engineer (1); MUKULMAHANT (1); RROY (1); Snakemike (1); tonietonies (1); V.I.Abraham (1)