Earth Fault Protection Coordination of Star-Star Transformer

01/08/2014 4:29 AM

In one of my application Grid Power is imported through a transformer of rating 40/50MVA, 66kV/34.5kV, YNyn0. Both side neutral is solidly grounded. Down the line 33kV network is little large and earth fault anywhere in this network gets reflected in 66kV side. Relay settings in the Grid substation are sensitive enough to trip immediately (within 200msec) for 33kV side earth faults and authorities there are refusing to reconsider their settings. And due to this I am suffering power loss quite frequently. I am thinking of keeping the neutral of 66kV in open condition so that earth faults may not get reflected.

Is it feasible to do so or is there any other alternative?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: Earth fault protection coordination of star-star transformer

01/08/2014 6:44 AM

You can't run the system with no earth. I can't believe you've even considered this, it's suicidal!

From the scant information you give a NER springs to mind coupled to REF and inverse time EF.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Associate

Join Date: Mar 2013
Posts: 31
#2
In reply to #1

Re: Earth fault protection coordination of star-star transformer

01/08/2014 7:08 AM

opening of 66kV side neutral will not make system unearthed since it is further supplied from 220kV/66kV YNyn0 where 66kV is earthed.

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#5
In reply to #2

Re: Earth fault protection coordination of star-star transformer

01/08/2014 10:54 PM

Sorry but you weren't clear that you wanted the 66KV Y→E link removed. I assumed it was the 33KV you wanted to remove.

It is entirely at the discretion of the supply authority. But I'll be honest I can't see a reason for them to do so. As PWS has said, you need to sort your system out.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: Earth Fault Protection Coordination of Star-Star Transformer

01/08/2014 9:02 AM

The best alternative is to remove the source(s) of the earth fault(s).

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Associate

Join Date: Mar 2013
Posts: 31
#7
In reply to #3

Re: Earth Fault Protection Coordination of Star-Star Transformer

01/10/2014 2:26 AM

PWSlack

Are you trying to tell that if vehicle is punctured then I should fly it!

Register to Reply
Participant

Join Date: Jan 2014
Posts: 3
#4

Re: Earth Fault Protection Coordination of Star-Star Transformer

01/08/2014 10:54 AM

Rather than grounding or opening the neutral, why don't you go for differential protection?

Register to Reply
Associate

Join Date: Mar 2013
Posts: 31
#6
In reply to #4

Re: Earth Fault Protection Coordination of Star-Star Transformer

01/10/2014 2:23 AM

transformer differential is already in place, but what if earth fault takes place in out zone as entire plant distribution is on 33kV!

Register to Reply
Participant

Join Date: Jan 2014
Posts: 3
#9
In reply to #6

Re: Earth Fault Protection Coordination of Star-Star Transformer

01/11/2014 10:52 AM

I agree with your thought, but, if one of the side of the transformer is grounded then it is already preventing the flow of zero sequence currents....

Register to Reply
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#8

Re: Earth Fault Protection Coordination of Star-Star Transformer

01/10/2014 4:12 AM

I agree that opening of 66kV neutral will make the grid side earth fault protection not see the faults in 33kV system.

But, since the 66kV winding will be without any earth reference, the neutral point that is floating may assume undesirable potential that can harm the insulation.

I am not sure if the winding with graded insulation (IEC requires only transformers up to 33kV to be uniformly insulated) can handle that well!

__________________
Raghunath
Register to Reply Score 1 for Good Answer
Register to Reply 9 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

adee2007 (2); PWSlack (1); raghun (1); TonyS (2); vyral2311 (3)