Alternator

01/08/2014 10:51 AM

causes of motoring action in alternators

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Alternator

01/08/2014 10:55 AM

Terminal voltage exceeds generated voltage?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Participant

Join Date: Jan 2014
Posts: 3
#5
In reply to #1

Re: Alternator

01/11/2014 10:48 AM

Low generating frequency is also one of the reason for motoring action.

Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: Alternator

01/08/2014 10:57 AM

Other parallel alternators producing a higher voltage than the alternator in question, thereby causing current flow into it (rather than out of it) and thus making it a motor.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#3

Re: Alternator

01/08/2014 1:05 PM

Uh-oh, common misconception here! Unlike DC machines, raising the voltage on the terminals of a grid connected alternator only changes the VAR flow, not the Watt flow (ok, a little bit to overcome the change in copper losses, usually ignored though).

An AC alternator "motors" because the prime mover is no longer capable of putting enough torque out to overcome the mechanical losses plus the electrical load on the generator; i.e., power (Watts) is flowing into the alternator instead of out of it.

In power engineering terms the alternator's power/torque angle (not to be confused with the power factor angle) is lagging behind the grid's.

btw- it's a bad situation for an alternator to become a motor since it spins the turbine with inadequate steam flow to cool the blade tips, or a diesel engine is receiving input power on its output shaft.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Reply Score 1 for Good Answer
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#4

Re: Alternator

01/08/2014 4:17 PM

It is having an identity crisis. It is confused about its real function.

Identity Crisis - DC

Reply
Reply to Forum Thread 5 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

adee2007 (1); lyn (1); PWSlack (1); RAMConsult (1); Tornado (1)