Zero Sequenec Current & Zero Sequence Voltage Derivation in Numerical Relays

01/10/2014 8:34 AM

In the modern era of numerical protection relays, I understand that in a three input current operated relay, the relay is capable of calculating the zero sequence current or the earth fault current from the three phase current inputs itself, without a specific need for any residually connected CT input or a neutral CT input or a CBCT input.

Similarly, in voltage input relays, one need not give a voltage input from an open delta VT Secondary for calculating the zero sequence voltage. The relay would derive the same from the phase voltage input itself.

Is my above understanding correct? If so, is it true for all makes & types of numerical protection relays?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#1

Re: Zero Sequenec Current & Zero Sequence Voltage Derivation in Numerical Relays

01/10/2014 1:13 PM

You are correct in general. However, you would need to consult the manufacturer's instruction book for your specific relay regarding what they expect to have done with the Vn input (if it exists) in the case of an open delta connection. There may also be setting(s) that need to be adjusted to define the type fo voltage input connection, so the relay knows what it is looking at.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply
2
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#2

Re: Zero Sequenec Current & Zero Sequence Voltage Derivation in Numerical Relays

01/11/2014 1:23 PM

In a numerical relay, the phase currents are sampled regularly, the residual current is simply calculated as i1 + i2 + i3, with signs +/-. So there is no need for a physical summing by residual connection and its input to a relay. I would, however, investigate whether i1 - i3 were sampled simultaneously.

However, I understand that residual current is less sensitive than a dedicated neutral or earth current CT [where possible] because the transient and saturation errors of three CTs limit sensitivity and speed, noting that they will usually handle different current levels and "point on wave" instants.

Remember that switching transients on power transformers differ greatly between zero voltage and peak voltage connection, causing flux doubling or worse, depending on residual flux and are always different between phases. This also affects errors of iron core CTs.

For voltage measurement and calculation of residual voltage, there does not seem to be any similar error.

I would not assume all numerical relays are the same. Electronically, one can have independent A/D for each phase, with synchronised sampling or one A/D switched between phases or three synchronised "sample and hold" analog circuits with a common A/D, apart from different samples per cycle of AC and A/D bit size. Once the numbers are digitised, the processing that can be done will depend on the processor power and, finally, how well the algorithms discriminate real faults from transients.

Register to Reply Good Answer (Score 2)