I have searched for phase angle regulator but it is said that it controls the flow of real power only. i need the operation of PAR(phase angle regulator ) which compensates the reactive power in a power system
Re: Diagram and operation of phase angle regulator which compensates reactive power
01/11/2014 10:44 PM
I'm not sure where you are looking to achieve power factor correction. The closest I'll guess is that you need a brushed synchronous motor used as a synchronous condenser.
__________________
"Don't disturb my circles." translation of Archimedes last words
Re: Diagram and Operation of Phase Angle Regulator Which Compensates Reactive Power
01/15/2014 6:52 PM
Karthiga,
I assume that this was an interview question. It is designed to test
your knowledge of how power flows in a grid can be controlled, something
only an experienced power engineer (or a really, really diligent
student) would know.
Think of it this way, there are two components to Apparent Power (S),
Real Power (W) and Reactive Power (VAR); therefore, there are only two
control actions that can be taken to affect these two quantities. We can
change the phase angle between two points which changes the real power
flow, or we can change the voltage which changes the reactive power
flow, or any combination of both. Two variables, four degrees of
freedom, four quadrants of operation.
At a generating station changing the fuel supply affects the
phase/torque/power angle, while changing the rotor current affects the
voltage level. On the grid the PAR and reactive elements such as LTC (Load Tap Changer), synchronous condensers, capacitors, etc.
perform the equivalent functions.
7anoter4,
From your Wiki article: "...A phase angle regulating transformer, phase angle regulator (PAR, American usage), phase-shifting transformer, or quadrature booster (quad booster, British usage), is a specialised form of transformer used to control the flow of real power..."
Real power, not reactive power; there is no such thing as a PAR significantly affecting VAR flow, only reactive elements such as LTC (Load Tap Changer), synchronous condensers, capacitors, etc. do that.
Class dismissed,
Alan