Failure of Transformer Incomer Without a Fault Indication

01/11/2014 9:13 PM

One of our transformer 2.4kV/460v, Incomer breaker failed without any fault indication. We did a through investigation in the transformer and could not find out any reason for the failure . Reenergised the transformer and it is running normal What could be the reason for failure?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Failure of Transformer Incomer without a fault indication

01/11/2014 9:21 PM

Did you send the faulty breaker back to the manufacturer for failure analysis?

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: Failure of Transformer Incomer without a fault indication

01/11/2014 10:07 PM

Evil pixies.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Participant

Join Date: Jan 2014
Posts: 4
#3

Re: Failure of Transformer Incomer without a fault indication

01/11/2014 10:37 PM

Suddenly a high voltage surge might have attacked and the circuit would have tripped to avoid damage

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#4

Re: Failure of Transformer Incomer without a fault indication

01/11/2014 10:54 PM

Initially I would suspect the breaker or a loose connection....I would check the operating temperature of the breaker with an infrared thermometer....and also all the wiring connections....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#5

Re: Failure of Transformer Incomer without a fault indication

01/11/2014 11:16 PM

Record the waveform of the current when switching on and check from CB manufacturer whether it can withstand the inrush current.

__________________
pnaban
Register to Reply Off Topic (Score 3)
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#6
In reply to #5

Re: Failure of Transformer Incomer without a fault indication

01/12/2014 12:56 AM

The answer must be Yes, because when they turned it back on, it is running normally now.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#7

Re: Failure of Transformer Incomer Without a Fault Indication

01/13/2014 12:18 AM

old age!

__________________
The square root of nothing is what you make it!
Register to Reply
Commentator

Join Date: Jan 2011
Posts: 84
Good Answers: 4
#8

Re: Failure of Transformer Incomer Without a Fault Indication

01/13/2014 3:33 AM

Make an analysis for the following:

How long this breaker was in service?

How many such incidents the breaker had before?

If the breaker has a UV relay in the protective circuit, check the set values for voltage minimum/maximum and the withstand time;

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#9

Re: Failure of Transformer Incomer Without a Fault Indication

01/13/2014 8:38 AM

May be "the hand of god"?

Register to Reply
Guru

Join Date: Nov 2012
Posts: 633
Good Answers: 13
#10

Re: Failure of Transformer Incomer Without a Fault Indication

01/13/2014 9:11 AM

Did it correspond to the arrival of the latest CME (Thurs.)?

Register to Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#11

Re: Failure of Transformer Incomer Without a Fault Indication

01/13/2014 10:14 AM

Did the breaker fail? Or did it perform correctly and trip/open?

Don't know about your location but we suffer inadvertent trips all too often caused by human error when they are troubleshooting or calibrating protective equipment and get into the wrong circuit or forget to disable the trip circuit.

Once this happens it is difficult and in most cases impossible, to find out what actually happened due to the fear of reprimand by management.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply
Power-User

Join Date: Jun 2010
Location: Kolkata, West Bengal, India
Posts: 172
Good Answers: 1
#12

Re: Failure of Transformer Incomer Without a Fault Indication

01/22/2014 3:53 AM

The Breaker might have been tripped due to sudden under-voltage in incoming power supply system. Please check setting and operation of under-voltage relay.

Regards,

Manindra.

__________________
Manindra
Register to Reply