Sprinkler In Operation Rooms In Hospitals?

01/13/2014 10:48 AM

sprinkler in operation rooms is a must ?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Jun 2013
Location: Central Canada
Posts: 677
Good Answers: 28
#1

Re: Sprinkler In Operation Rooms In Hospitals?

01/13/2014 12:16 PM

YES.

__________________
Smart as a post and twice as fast.
Register to Reply
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#2

Re: Sprinkler In Operation Rooms In Hospitals?

01/13/2014 1:05 PM

Yes and no. Other fire suppression equipment is used when in use. And several of the staff on hand are trained in it's use. In the chance of a fire you don't go dumping water on the patient and get it into an open surgical procedure. The water from sprinkler heads is not sterile. You also don't want to spray water on the equipment keeping them alive and monitoring them.

I believe there is an activation switch once the patient is removed to safety if the other means of suppression does not extinguish it.

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#4
In reply to #2

Re: Sprinkler In Operation Rooms In Hospitals?

01/13/2014 1:40 PM

Capsule-based sprinkler heads operate individually based upon temperature at the head, there are no other initiating means. They are also placed around the periphery of the operatory and their locations and spray patterns are chosen so that they do not drip (if leaking) on equipment and/or patient, also they may be required inside cabinets housing flammable materials/equipment.

If activated it means that there is a heat source in the vicinity the head that is heating the air to above 135°F. One would hope that no one is still in the room at that point, unless there is a flash-fire, the spray would be welcome relief to everyone.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#5
In reply to #4

Re: Sprinkler In Operation Rooms In Hospitals?

01/13/2014 2:56 PM

One would hope while doing surgery the team would not let the fire get to the point that the sprinkler heads go off. As I understand an saline solution is available to put out any fires on or around the patient. That CO2 is available to fight fire on equipment.

Limiting the direction of the spray is questionably effective. Does little good if the heat source that set it off is behind the spray pattern of the head.

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#3

Re: Sprinkler In Operation Rooms In Hospitals?

01/13/2014 1:38 PM

CO2 would be a bad idea , its a dangerous area, it requires fire suppression, yes

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#6

Re: Sprinkler In Operation Rooms In Hospitals?

01/13/2014 3:54 PM

You should not be in this line of work! I suggest that you purchase and read the specifications you want others to provide.

NFPA Requirements for Generator Rooms

"will u specify the artical in NPFA 72, stating particularly requirements in generator rooms"

NPFA 72 - Smoke or Heat Detectors in Generator Rooms

"Can anybody specify the artical in NPFA 72, stating detector(smoke or heat) requirements in generator rooms?"

"does anyone can help, which article in nfpa 72 states that detectors required in generator rooms"

Fire Detection for Transformers and Generators

"What is the recommended type of fire alarm detectors in transformar's and generators"