Greetings,
We have 75KVA XFMR that seems to have developed a mind of it's own.
It's primary function is to supply power to a variety of band and cartridge heaters on one of our extrusion lines.
It's 480 to 230 ,3ph no neutral. On any given day I get varied readings. The line side never fluctuates. It is always 270 to ground on any leg and 480 between any 2.
The 230 side is the issue. At times its 115vac to ground on any leg and 230 between any 2 orrrrrrrrrrrr 230 to ground on lines 1 and 2 and 6vac to ground on 3. Even at 6 vac to ground on 3 if I read between 3 and line 1 or 2 it gives me 230VAC. I don't get it! I get the same reading on any device (band or cartridge htr) that is attached to the line 3 leg. 6 volts to ground- or 230 between the two leads.
I swapped the load lines supplying the devices from L3 to L2 and L2 to L3 and after powering up the issue persisted on L3 only as if it were the XFMR.
I am told if it's a delta config the voltage will float due to an unbalanced load, problem is I have a wye output.
Has anyone seen this before? Keep in mind I could go take readings right now and it could be completely normal. If the loads are disconnected and the xfmr and it is powered up, I get 115 to grnd on each leg. it's only when the load is applied that this issue comes and goes.
Thanks,
Bruce