Greetings,

We have 75KVA XFMR that seems to have developed a mind of it's own.

It's primary function is to supply power to a variety of band and cartridge heaters on one of our extrusion lines.

It's 480 to 230 ,3ph no neutral. On any given day I get varied readings. The line side never fluctuates. It is always 270 to ground on any leg and 480 between any 2.

The 230 side is the issue. At times its 115vac to ground on any leg and 230 between any 2 orrrrrrrrrrrr 230 to ground on lines 1 and 2 and 6vac to ground on 3. Even at 6 vac to ground on 3 if I read between 3 and line 1 or 2 it gives me 230VAC. I don't get it! I get the same reading on any device (band or cartridge htr) that is attached to the line 3 leg. 6 volts to ground- or 230 between the two leads.

I swapped the load lines supplying the devices from L3 to L2 and L2 to L3 and after powering up the issue persisted on L3 only as if it were the XFMR.

I am told if it's a delta config the voltage will float due to an unbalanced load, problem is I have a wye output.

Has anyone seen this before? Keep in mind I could go take readings right now and it could be completely normal. If the loads are disconnected and the xfmr and it is powered up, I get 115 to grnd on each leg. it's only when the load is applied that this issue comes and goes.

Thanks,

Bruce

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Perplexed With a Delta/Y Transformer

01/16/2014 9:27 AM

It sounds like an unintentionally corner-grounded transformer (i.e., ground fault). If the output is nominally 230 and balanced, each leg to ground should be ~133 volts.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Score 1 for Good Answer
Commentator

Join Date: Sep 2011
Location: Rhode Island
Posts: 58
Good Answers: 1
#5
In reply to #1

Re: Perplexed With a Delta/Y Transformer

01/16/2014 1:15 PM

I discovered the xfmr is relying on the nipple to the cabinet for bonding. There is no equipment ground. Not even from the 480 feed panel.

Register to Reply
Commentator

Join Date: Sep 2011
Location: Rhode Island
Posts: 58
Good Answers: 1
#34
In reply to #1

Re: Perplexed With a Delta/Y Transformer

01/18/2014 6:41 AM

I just reread this and and was curious to if it applied but it appears that this is referencing a delta config. My Primary is Delta but my secondary is a Wye. Both line and load sides of the xfmr are ungrounded.

http://static.schneider-electric.us/docs/Circuit%20Protection/Molded%20Case%20Circuit%20Breakers/2700DB0202.pdf

Register to Reply
2
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#2

Re: Perplexed With a Delta/Y Transformer

01/16/2014 10:19 AM

"...it's only when the load is applied that this issue comes and goes..."

If so then the easiest way to find the problem is to isolate it to one particular load. Why not open the breakers on all the loads and start closing them one-by-one, sooner or later you will close a breaker and your problem will appear.

Most likely you have a load with a high impedance arcing fault, a winding that shifts then lightly touches the steel, or a resistance heater that is starting to burn through and is touching the sheath. Please let us know what you find.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Good Answer (Score 2)
Commentator

Join Date: Sep 2011
Location: Rhode Island
Posts: 58
Good Answers: 1
#6
In reply to #2

Re: Perplexed With a Delta/Y Transformer

01/16/2014 1:19 PM

I am going to load test 1 pair of devices at a time this sat AM. I will remove them all and reconnect one at time along with some basic tests. I'm thinking a mhegger my come in handy.

Register to Reply
Guru

Join Date: Apr 2012
Posts: 732
Good Answers: 17
#3

Re: Perplexed With a Delta/Y Transformer

01/16/2014 10:57 AM

So on the wye side you have no neutral, yet you are referencing individual phases to ground?

What is the reference if you have nothing set? I assume the wye side is at least grounded? Is the equipment grounded/bonded? What is the grounding arrangement for your factory if you use no neutrals? (it sure sounds like you have single-phase loads, though).

How about providing a 1-line for your lineup?

__________________
common knowledge...less common than common sense
Register to Reply Score 1 for Good Answer
Commentator

Join Date: Sep 2011
Location: Rhode Island
Posts: 58
Good Answers: 1
#7
In reply to #3

Re: Perplexed With a Delta/Y Transformer

01/16/2014 1:29 PM

Yes, that is true...keep in mind I'm a little green with transformers. The neutral is not being utilized. I have 3ph 480 in 3ph 230 out. Grounding? heh i just determined that there is no grounding! This is my first order of business! I know that this xfmr has been here for 10 plus years and whoever installed it didn't even run a bond to it's adjoining cabinet, it has no ground coming from the distribution center either. I'm glad no one has died from this thing yet.

All we are doing is balancing lets say (30) 2 wire elements rated at 230V between 3 phases. On start up (cold) each phase draws appx 100 amps until they reach our desired temp setting with a controller that speaks to an thermal coupling and an ssr for each zone.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#10
In reply to #7

Re: Perplexed With a Delta/Y Transformer

01/16/2014 2:40 PM

A qualified Electrician, working in the UK to BS7671, would at least measure the earth loop impedance on the secondary side of the transformer before sanctioning its energising so as to have a high level of confidence that the circuit protective device(s) operate so as to disconnect any fault. The problem appears, from here, to be insufficient or missing bonding between the secondary neutral terminal on the transformer and local earth/ground. In its absence, a single phase-to-earth fault would do two things:

  1. It would not cause a circuit protective device to operate and disconnect the fault, and
  2. It would raise the voltage-to-earth on the other two phases, putting additional stress on the insulation of all conductors connected to each of those phases.

This is not an issue for persistent exclamation marks. Get it fixed before it causes injury/fatality/property damage. If in doubt, consult a qualified Electrician without delay/now/this morning/before tea break.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Commentator

Join Date: Sep 2011
Location: Rhode Island
Posts: 58
Good Answers: 1
#41
In reply to #3

Re: Perplexed With a Delta/Y Transformer

01/18/2014 4:03 PM

It was definitely caused by not having XO (Neut) Grounded. As we had device failures downstream it would make the voltage flip flop between 1 and 3. This was a beauty! Thanks for your help, i really appreciate it :)

Register to Reply
2
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#4

Re: Perplexed With a Delta/Y Transformer

01/16/2014 1:09 PM

For testing purposes I would recommend putting a fused jumper between the secondaries Wye center point and the system common/ground point and do your line side voltage and current testing from there.

Start out with a 5 - 10 amp fuse and see what you get. If that blows right away you have a line side short to the common/ground of the systems that needs immediate attention and correction.

Register to Reply Good Answer (Score 2)
Commentator

Join Date: Sep 2011
Location: Rhode Island
Posts: 58
Good Answers: 1
#8
In reply to #4

Re: Perplexed With a Delta/Y Transformer

01/16/2014 1:30 PM

I am going to do this ...thank you!

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#11
In reply to #8

Re: Perplexed With a Delta/Y Transformer

01/16/2014 2:51 PM

If it does blow, it may indicate a neutral/ground fault downstream of the transformer, which is what will give the varying phase voltage described earlier. Once that fault is disconnected, make the bond permanent, then re-energise each circuit one at a time. The one that blows the individual circuit protective device is the circuit that needs remedial action; simply remove the neutral-to-ground fault, then re-energise.

Once that is done, consider installing a residual current circuit breaker in the leads between the transformer and the individual circuit protective devices.

If in doubt, consult a qualified Electrician.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Commentator

Join Date: Sep 2011
Location: Rhode Island
Posts: 58
Good Answers: 1
#13
In reply to #11

Re: Perplexed With a Delta/Y Transformer

01/16/2014 3:38 PM

I'm going to do this testing this Saturday. Thank you for your feedback.

Register to Reply
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#9

Re: Perplexed With a Delta/Y Transformer

01/16/2014 2:23 PM

The problems in the secondary of the transformer not the devices it powering. At some time the output of L3 is shorting to chassis ground. That's when you get your readings of 230V to ground from L1 & L2 and L3 reads the 3V. The short sounds like the heat in that winding under load is expanding something to cause the short. By the voltages given I would check wire at the terminal board.

Warning if it is shorted to chassis ground the device is not bonded to earth ground or it should have trip out. So be aware that there is the chance of a shock from touching any metal on the transformer.

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Register to Reply
Commentator

Join Date: Sep 2011
Location: Rhode Island
Posts: 58
Good Answers: 1
#12
In reply to #9

Re: Perplexed With a Delta/Y Transformer

01/16/2014 3:32 PM

I think your right.

Register to Reply
Commentator

Join Date: Sep 2011
Location: Rhode Island
Posts: 58
Good Answers: 1
#14
In reply to #12

Re: Perplexed With a Delta/Y Transformer

01/16/2014 4:00 PM

Why would they use a delta/wye when the are not using the neutral? Is this the right transformer for this application?

Register to Reply
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#15
In reply to #14

Re: Perplexed With a Delta/Y Transformer

01/16/2014 4:07 PM

Just because someone hooked up some wires and things sort of worked afterwards does not make them a knowledgeable electrician.

They may have been licensed but that in itself still does not mean they knew what they are doing.

Register to Reply Score 1 for Good Answer
2
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#16
In reply to #14

Re: Perplexed With a Delta/Y Transformer

01/16/2014 4:29 PM

It most certainly is the right type of transformer. The issue is not the transformer, it is how that transformer was installed.

Whether you use the neutral or not, the star point of the secondary should have been grounded and the bonding system established at that point.

If it would have been grounded, you would have blown fuses by now and found your shorted load.

The other way this could have been done was to... leave the secondary un-grounded (I would not do so) and install ground fault indication equipment (required by code) on the secondary to indicate the presence of a ground fault.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply Good Answer (Score 2)
Commentator

Join Date: Sep 2011
Location: Rhode Island
Posts: 58
Good Answers: 1
#17
In reply to #16

Re: Perplexed With a Delta/Y Transformer

01/16/2014 4:59 PM

The chassis is grounded and we haven't had any issues with blown fuses unless a device literally shorts out which they do. in that case we do blow a fuse.

There is a bonding strap that connects the chassis to the isolated inner framework of the transformer cores. There is nothing else connected other than the 3 Line feeds and the 3 output feeds. Not even a ground wire.

These installers were hacks. The primaries were run 300ft with no ground and it looks like the voltage is most likely floating because the xfmr is wired incorrectly. This is most likely it's way of reacting to an unbalanced laod. This xfmr may have been like this since it's inception 20 years ago.

Register to Reply
Guru

Join Date: Apr 2012
Posts: 732
Good Answers: 17
#20
In reply to #17

Re: Perplexed With a Delta/Y Transformer

01/16/2014 8:43 PM

This is just stunning! Even if the downstream panels are all bonded "correctly" you are risking great hazard by having this system powered. Since there is no reference to the separately derived system your over-current protection devices will not function as intended. There is no way that the ground and neutral which should be delivered to each panel is going to work effectively. Conduit bonding? Worthless.

__________________
common knowledge...less common than common sense
Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#22
In reply to #20

Re: Perplexed With a Delta/Y Transformer

01/16/2014 9:15 PM

Ya... hard to believe. I still have a hard time seeing runs with no bonding conductor pulled in. Using the raceway as a bond is pretty much no better than wishing it was bonded.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
2
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#23
In reply to #22

Re: Perplexed With a Delta/Y Transformer

01/16/2014 9:56 PM

Could be worse.

At one of my first jobs as a service techs at a pasta plant I had a manager who knew everything about everything. Or so he thought. His brilliant idea was to internally bond our shop welders negative output to the machines common and body earth grounding leads.

His brilliant reasoning was that every machine in the plant was within 400 feet of the welder and was electrically tied to the same common and earth ground buss point.

By that reasoning all we needed to do any repair work inside the plant was run a single welding lead from the shop out to whatever machine we were working on.

Hey it did work.

Register to Reply Good Answer (Score 2)
Guru

Join Date: Apr 2012
Posts: 732
Good Answers: 17
#36
In reply to #23

Re: Perplexed With a Delta/Y Transformer

01/18/2014 2:47 PM

That's awesome good ole days stuff.

__________________
common knowledge...less common than common sense
Register to Reply
Guru

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1271
Good Answers: 27
#33
In reply to #9

Re: Perplexed With a Delta/Y Transformer

01/17/2014 1:54 PM

When transformers are wound it is normal to find that certain leg winding to be closer to the ground plane than the rest of the windings.. Unless it is a specially designed and manufactured to be a well balanced in terms of interwinding capacitance, insulations, etc., like those specially built low-leakage isolation transformers!

This leakage problems becomes more pronounced when its core or casing is grounded! Leakage current due to (stray capacitances) the physical construction of the winding /and its insulation as well as with the laminated core when inserted into the coil form!

Therefore, It is very possible that there is really no electrical short in the transformer in question! The erroneous voltage terminal readings maybe cause by an increased current leakage of the transformer? Increased leakage capacitance, due to accumulated dirt, surrounding humidity where the transformers are located? Intermittent voltage levels may not only be due to the poorly grounded casing or ungrounded wye, but may also be due to the kind of tester being used?

__________________
vsar
Register to Reply
Commentator

Join Date: Sep 2011
Location: Rhode Island
Posts: 58
Good Answers: 1
#18

Re: Perplexed With a Delta/Y Transformer

01/16/2014 5:08 PM

After checking the grounds and finding that i do have decent continuity from each cabinet and transformer to ground I'm not fearing electricution. I notified management that we need to pull a ground from the distribution center to the secondary and ground and bond each piece of equipment individually.

I'm still a little foggy on whats next but I'm going to isolate the loads and do some testing before reconnecting them one at a time.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#19
In reply to #18

Re: Perplexed With a Delta/Y Transformer

01/16/2014 5:29 PM

If in doubt, consult a qualified Electrician.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
2
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#21
In reply to #18

Re: Perplexed With a Delta/Y Transformer

01/16/2014 9:04 PM

What you should do next is...

1) Run a bonding conductor from the source to the transformer case. Under Canadian rules, the size of the bonding conductor would be based on the size of the overcurrent device feeding the primary. Table 16 of the CEC would then tell you the size of the bonding conductor to use.

2) Check and make sure that the overcurrent device properly protects the primary. If there is no secondary overcurrent device, the primary device will also protect the secondary. The CEC also has rules that speak to that condition. Make what ever changes are required in the overcurrent device and the conductors for the primary to meet the code in effect in your jurisdiction. The NEC has similar tables to what the CEC has, that speak to these issues.

3) Run a grounding conductor from the star point of the secondary direct to your grounding system. Note: not the bonding system. Under the Canadian code, this would be a minimum of a #6 copper conductor. This conductor should connect to your other grounding conductors.

4) Run a bond from the star point to the transformer case. Size this bonding jumper based on the ampacity of the secondary. Again... Table 16 of the CEC (or then NEC equivalent).

5) Check the size of the secondary conductors and change as required.

6) Run bonds to the heater equipment.

That is what I would do.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply Good Answer (Score 2)
Active Contributor

Join Date: May 2011
Posts: 23
Good Answers: 2
#24
In reply to #18

Re: Perplexed With a Delta/Y Transformer

01/17/2014 3:28 AM

Hi Laurz,

If your transformer is good it is definitely the neutral output is not connected or connected well --this is common problem it will show good on low to no amps then will spike when you put a draw on it I once got a thousand volts on my 220 line from an ungrounded new utility side 4160 transformer with delta primary wye secondary.

The system all tested normal on my side with lights and small outlets but when I started running a 20 hp motor to open my doors (Lets just say they were Real big doors, wherever they were) it spiked and cooked half of my devices.

Expat 07

Register to Reply Score 1 for Good Answer
Guru

Join Date: Apr 2012
Posts: 732
Good Answers: 17
#37
In reply to #18

Re: Perplexed With a Delta/Y Transformer

01/18/2014 2:54 PM

As far as fearing electrocution you would still need a fault, but that would be easy to come across...but the cabinet of the SDS xfmr is not referenced to the center tap. Until that is fixed (like you said), you won't be good.

Regardless, The system should be recomissioned by a qualified electrician.

__________________
common knowledge...less common than common sense
Register to Reply Score 1 for Good Answer
2
Power-User

Join Date: May 2013
Posts: 351
Good Answers: 22
#25

Re: Perplexed With a Delta/Y Transformer

01/17/2014 7:47 AM

In the past, in a lot of American factories, the neutral was intentionally left ungrounded on LV systems. The grounding was done by 6 incandescent light bulbs in the electric shop. 2 bulbs on each phase in parallel to ground. When the system was operating correctly, the bulbs glowed dimly and everybody was happy. When a line to ground fault occurred then one phase light bulbs went out, the others glowed brightly, and the electricians would go out and find and repair the fault, but the factory could keep running in the meantime. It actually worked well. The reason for 2 light bulbs was in case one burnt out, so it could be simply replaced without losing the ground. The system was really grounded but through the resistance of the light bulbs. There are reasons for resistance grounded systems and they work on LV, but no system should be totally ungrounded. If it is totally ungrounded the whole system could theoretically float to quite a high voltage to ground.

Register to Reply Good Answer (Score 2)
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#27
In reply to #25

Re: Perplexed With a Delta/Y Transformer

01/17/2014 11:58 AM

That was common in Canada also - but it was restricted to industrial environments with full time electrical staff.

Variable speed drive systems until the last few years where also ungrounded Y secondaries. It has just been the last 10 years or so that code changes require solidly grounded (preferred) or ground fault protection and ground fault indication.

Before slapping on a neutral ground connection, I would suggest testing the transformer. Disconnect primary power, disconnect all three secondaries at the transformer, measure the resistance from each leg to ground. It should indicate meg ohms. If it is a couple ohms, then buy yourself a new transformer. If it checks out OK, connect the neutral to ground. Now check the outgoing phases from the transformer. They should also all read meg ohms to ground. If phase 3 reads low, then you need to troubleshoot the downstream equipment to find your ground fault.

If you ground the neutral, I recommend secondary line fuses - then in the future you know which downstream phase shorts to ground. It also provides better fault protection for your cables.

Remember - disconnect power first!

If you use a megger, be sure to have all personnel away from the associated equipment - it can be shocking.

- This is electrical installation work - and by many jurisdictions requires a certified or licensed journeyman to work on the equipment.

(I had one customer who could not understand that the electrical engineer had to design and specify the equipment, but was not allowed to install the equipment, but had to certify the equipment was correctly installed. By the time the job was finished both the electrical installer and engineer were frustrated with the customer complaining they where milking it for money.)

Register to Reply Score 1 for Good Answer
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#28
In reply to #27

Re: Perplexed With a Delta/Y Transformer

01/17/2014 12:56 PM

I pretty much agree with what you have said.

I have worked in a few facilities with such ground fault indication systems. A serious problem was when a ground fault was indicated and not investigated right away. A subsequent fault, if and when it happened would be of much greater impact as it would end up as a phase to phase fault and not a phase to neutral fault.

You said...

"If it checks out OK, connect the neutral to ground. Now check the outgoing phases from the transformer. They should also all read meg ohms to ground".

Once the neutral of the secondary is tied to ground, an ohmeter check of the outgoing phase connection to ground will now read the resistance of the secondary winding. Which will be way lower then the megohm range you mentioned.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#29
In reply to #28

Re: Perplexed With a Delta/Y Transformer

01/17/2014 1:05 PM

Ok I had some confusion in the instructions - the secondary leads where disconnected for the first test, and I thought they were still open, so the test was to check the out going leads while disconnected from the transformer.

Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#30
In reply to #29

Re: Perplexed With a Delta/Y Transformer

01/17/2014 1:18 PM

Perhaps my error then... I thought you wanted the check done from the outgoing phase connection on the transformer to the ground.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Commentator

Join Date: Sep 2011
Location: Rhode Island
Posts: 58
Good Answers: 1
#31
In reply to #30

Re: Perplexed With a Delta/Y Transformer

01/17/2014 1:41 PM

So as it stands, my neutral is floating. You are both suggesting that I should connect the secondary neutral bus to ground? It makes sense.

I will let you know tomorrow.

My plan is to isolate the xformer and meg the primary and secondary in and out feed terminals.

Depending on the results I will run a ground wire and do some bonding then reconnect the existing wiring including a wire from the neutral bus to ground.

I will also test each input leg to the loads with an ohmmeter for general purposes.

This does seem like the most logical approach. I think once the neutral is connected to ground it should stabilize the load line output voltage. It appears that the load may be unbalanced and that is what is causing this issue. God only knows how long it's been like this.

I have quoted out a new transformer and have a Rockwell Service dude coming in on monday.

Register to Reply
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#43
In reply to #31

Re: Perplexed With a Delta/Y Transformer

01/19/2014 2:39 AM

Yikes $$$$$$

Register to Reply
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#32
In reply to #30

Re: Perplexed With a Delta/Y Transformer

01/17/2014 1:42 PM

No problem, we are on the same page.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#26

Re: Perplexed With a Delta/Y Transformer

01/17/2014 8:38 AM

Yes, the "Y" connection (starpoint) on the secondary side either has a loose connection or other high impedance fault.

In a "Y" xfmr the "B" phase voltage will be very unstable if the starpoint is not grounded properly.

This is known as a "wild leg" transformer condition.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply Score 2 for Off Topic
Commentator

Join Date: Sep 2011
Location: Rhode Island
Posts: 58
Good Answers: 1
#40
In reply to #26

Re: Perplexed With a Delta/Y Transformer

01/18/2014 4:00 PM

Exactly what was wrong!

Register to Reply
Commentator

Join Date: Sep 2011
Location: Rhode Island
Posts: 58
Good Answers: 1
#35

Re: Perplexed With a Delta/Y Transformer

01/18/2014 11:19 AM

I have isolated everything.

I megged the xfrm and it's looking good. Once I make repairs on the load side I will connect the neutral to ground with a fused jumper. At present when I meg XO to grnd it is isolated. Starting with a fused jumper should be a profitable attempt for a test.

So far I have found 2 Extruder Barrel heaters that are shorted with no blown fuse. Of course the meg-ohmmeter could be reading potentials in the wiring etc.

I also found a short in the 230vac side of the xfmr in the Die. Time for some repairs and I'll return with my report!

thanks for all your help guys!

Register to Reply
Guru

Join Date: Apr 2012
Posts: 732
Good Answers: 17
#38

Re: Perplexed With a Delta/Y Transformer

01/18/2014 3:04 PM

This is a classic thread with tons of good responses.

__________________
common knowledge...less common than common sense
Register to Reply
2
Commentator

Join Date: Sep 2011
Location: Rhode Island
Posts: 58
Good Answers: 1
#39
In reply to #38

Re: Perplexed With a Delta/Y Transformer

01/18/2014 3:43 PM

Viola!

After the repairs my secondaries stabilized somewhat on 1,2 & 3. 3 was running high at 157. I connected the neutral to ground and yep..you guessed it!! 130 vac across all 3.

That device has been running that way for 20 years. The next matter at hand is the ground home run back to the distribution center.

I'm so grateful for all of your shared experience and knowledge. You made me look good :) Much appreciated!

Register to Reply Good Answer (Score 2)
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#42
In reply to #39

Re: Perplexed With a Delta/Y Transformer

01/18/2014 11:05 PM

Make sure there is no fuse permanently in the jumper between the XO and the grounding conductor back to your ground grid or in the bonding conductor between the XO and the frame/case of the transformer.

Glad you appear to have been helped by the back and forth on this thread. There is a good group of folk here with vast knowledge, even if we do get rangy by times and argue among ourselves... CR4 is a great resource.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Commentator

Join Date: Sep 2011
Location: Rhode Island
Posts: 58
Good Answers: 1
#44
In reply to #42

Re: Perplexed With a Delta/Y Transformer

01/20/2014 9:23 AM

Yea,

The fuse is history, I made up a 1/0 jumper and closed it up. She's runnin good today!

Register to Reply
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#45
In reply to #44

Re: Perplexed With a Delta/Y Transformer

01/20/2014 7:27 PM

Nice work!

Management will be along shortly to write you up for actually having done something that solved one problem while exposing several others.

Register to Reply
Register to Reply 45 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

4wsilver (1); EXPAT07 (1); GW (4); Lauruz (16); North of 60 (6); ozzb (1); PWSlack (3); RAMConsult (1); SHOCKHISCAN (1); tcmtech (4); The.Tinkerer (5); Tornado (1); vsar (1)

Previous in Forum: Battery V/C   Next in Forum: Question About Electrical Problem in My House

Advertisement