Series Capacitor 3p Motor Starting

02/06/2014 6:45 PM

say we have a 3p direct starting motor which have problem with the cable laid since it is a small cross-section one given the fact that a motor has a high start-up current. If I insert a capacitor in series with the motor circuit and after start up I remove this off the circuit, then does it eliminate the voltage drop if I size this capacitor suitably? I mean if this capacitor acts as an assisting voltage supply at the start-up stage, or behaves in assistance to the high rush current in an adverse effect regarding what I intend?

__________________
jinxnao
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#1

Re: series capacitor 3p motor starting

02/06/2014 8:50 PM

Change the cable...

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#2

Re: series capacitor 3p motor starting

02/06/2014 10:02 PM

No. Replace the cable or consider adding a soft starter circuit to reduce the startup current and hence the voltage drop.

__________________
jack of all trades
Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#3
In reply to #2

Re: series capacitor 3p motor starting

02/06/2014 10:46 PM

By changing the cable... I meant to replace it with one large enough to eliminate voltage drop as an issue. I should have explained that I guess.

Oh... you were saying no to his question. I thought you meant no to my statement about changing the cable...

Long day...

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Guru

Join Date: Jun 2010
Posts: 1296
Good Answers: 104
#4

Re: series capacitor 3p motor starting

02/06/2014 11:39 PM

How did this cable come to be too small? Was the motor up-sized, long cable run, high-inertia load, ??? jack has recommended a soft starter, which could work. If the problem is high inertia load, some type of mechanical clutch might work. I was thinking y-delta starting, but then you would need to run 3 more conductors, so you might as well up-size the ones you have, plus avoid additional contactors. If the cable is just outright undersized, replace it.
In any case, forget the capacitor idea.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5

Re: Series Capacitor 3p Motor Starting

02/07/2014 8:44 AM

Replace the cable, otherwise the overcurrent protective device(s) will be ineffective in clearing a fault before the cable melts. Cable sizing protocols are given in British Standard 7671.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#6

Re: Series Capacitor 3p Motor Starting

02/08/2014 12:40 AM

Use a shunt capacitor for starting/pfc.

__________________
pnaban
Register to Reply Score 1 for Off Topic
Power-User
Belgium - Member - New Member

Join Date: May 2007
Location: Flanders (Belgium)
Posts: 343
Good Answers: 21
#12
In reply to #6

Re: Series Capacitor 3p Motor Starting

02/09/2014 5:24 PM

Good idea, I used a shunt capacitor and a soft starter on a 11 kW motor with a input supply 3 x 25A 400V and it is working alreasy 13 years without troubles.

Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#13
In reply to #12

Re: Series Capacitor 3p Motor Starting

02/09/2014 9:26 PM

and the size of cable you are using is?

__________________
The square root of nothing is what you make it!
Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#7

Re: Series Capacitor 3p Motor Starting

02/08/2014 2:15 AM

change the cable.. as already stated! Forget any type of capacitors, unless you want a fire!

Change the cable if you want to avoid a fire, damage to property, loss of production and loss of life. You also need to find out WHO sized the cable and shoot him!

Now someone will come up with " use a VSD!" NO! The cable must be sized to handle the in-rush current regardless of how you start it!

You might say the cable is buried, it will be hard to replace/change.. Rubbish! If you want to, there is ALWAYS a way! There are no options or quick fix solutions to your problem. Cost of replacing the cable.. who cares when you compare it to the cost of lost production, loss of and damage to building/property and what about the cost of a life?

__________________
The square root of nothing is what you make it!
Register to Reply
Power-User

Join Date: Nov 2011
Posts: 286
Good Answers: 15
#8

Re: Series Capacitor 3p Motor Starting

02/08/2014 4:40 AM

You haven't given us the size of the motor or the size and length of the cable - all of this would affect the answer.

Your motor can take 8 times the full running current when it starts. You would need the fuse / mcb sized so as not to trip when you start the motor but also sized to protect your cable.

If its a small installation then likely the right answer is change the cable but get someone to look at your calculations first. If its a particularly long start up time then you can use a soft starter and limit the current.

If the volt drop is too great at start up chances are you have cattled the motor or certainly on the way.

Register to Reply Score 1 for Off Topic
Power-User
United Kingdom - Member - Not quite retired Member

Join Date: Aug 2012
Location: Up an araucaria araucana tree, South London, United Kingdom
Posts: 132
Good Answers: 7
#9

Re: Series Capacitor 3p Motor Starting

02/08/2014 5:54 AM

Have a look at http://www.gwm4-3phase.com/uands/static1.htm to see how to connect a capacitor to run a three-phase motor from a single-phase supply. It's perfectly possible but it does not give full torque. The capacitor stays connected when running. You need to have a professional calculate the value

Moreover, it doesn't limit the starting current and it doesn't generate the torque. The problem is that the phase voltage of a three-phase supply is ✓3 times the neutral to line voltage of the same supply. So, in UK, a 415v motor on a single-phase hookup will have only about a 230v supply. That may mean that the motor can be near stalling and it may draw excessive current and overheat both motor and cable.

We need details of both motor and supply cable (size and length) to go further. If the job is worth it there are available electronic three-phase inverters.

Register to Reply Off Topic (Score 5)
Power-User
United Kingdom - Member - Not quite retired Member

Join Date: Aug 2012
Location: Up an araucaria araucana tree, South London, United Kingdom
Posts: 132
Good Answers: 7
#10
In reply to #9

Re: Series Capacitor 3p Motor Starting

02/08/2014 6:01 AM

I may have misunderstood the question. Careful with series capacitors, resonance might be a problem.

may result in high volages.

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#11

Re: Series Capacitor 3p Motor Starting

02/08/2014 2:32 PM

The concept you are proposing is a long established solution to this sort of problem, especially in large medium voltage motors. You can research it further by doing a web search on "capacitor assisted motor starting". But there are very significant risks in this, some of which are the risk of resonance and over voltage mentioned by member . But most importantly, it only addresses a SYMPTOM of the problem, not the problem itself.All of the suggestions of increasing the conductor size would be the real solution to the PROBLEM. However, that is not always possible.

If you must continue to pursue the cap-assisted starting angle, be aware that is requires very PRECISE timing of when you turn the caps OFF. For this to have any appreciable effect, the capacitors must be very GROSSLY over sized compared to Power factor Correction Capacitors. If you think about this, a PFCC system is used to add VARs to the circuit to correct a lagging PF of 0.8 to around 0.95, so by maybe 10-15%. To assist in starting a motor, these caps must correct a PF that is in the area of 0.1 to 0.2, to the caps must supply 80-90% of the motor kVA as kVARs!

If those caps are left connected once the motor PF drops to normal, at about 80% speed, then you will be SEVERELY over exciting the circuit. That will then cause a severe over voltage, motor heating and a very high probability of over exciting other connected loads and causing resonance with any other capacitors in use, as in EVERY form of Switched Mode Power Supply now found in nearly all electronics.

So to safely accomplish Cap-Assisted Starting, you must use a precise method of determining motor speed and, in conjunction with contactor interrupt time, make sure the capacitors are removed from the circuit at 80% of motor speed. I have seen people "guess" on this and be off by just a second or two, which causes a severe voltage spike in the line that has destroyed other connected equipment. Bottom line, it is NOT worth pursuing on most LV motors. The reason people use this on MV motors is because the other alternatives are far far more expensive in MV.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Participant

Join Date: Feb 2014
Posts: 1
#14

Re: Series Capacitor 3p Motor Starting

02/11/2014 6:02 AM

First of all kindly check your cable if can carry the running current of the motor. If the cable is ok. Then the cheapest solution is to take another power source of control supply. To avoid voltage drop of your control circuit during starting. If you have ligthing power source is more than enough to supply the motor contactor.

We expercience same problems here in Saudi Arabia.

Register to Reply
Power-User
Turkey - Member - New Member

Join Date: Mar 2007
Posts: 310
#15

Re: Series Capacitor 3p Motor Starting

02/20/2014 4:43 AM

in fact, I wonder if this in series capacitor has a positive boosting task in the circuit. I do not ask it practically (İn practice a resonance is always a risk). If we use an inductor in series with the motor this will have a drop effect on the start up. If we use capacitor then can we say this will have a reverse effect so that the motor will start more easily.

By the way, shunt capacitor seems reasonable,but do not we have a resonance risk here also? .Also since the effective impedance of these two guys during a high frequency start up condition, then does this not mean that start up current will tend to increase?

__________________
jinxnao