No Load Excitation Current of Synchronous Generator Increased

02/23/2014 1:03 PM

We have 300 MW Thermal Power plant..The Rated No load excitation current( before synchronization) is 875 Amp DC..(Static Thyristor Controlled Excitation ,AVR)..Suddenly last time before Synchronization The no load Excitation current increased to 1160 Amps..What might be the cause?? Plant is running since then , but what could be the ill effects at long term??

Register to Reply
Pathfinder Tags: excitation
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#1

Re: No Load Excitation Current of Synchronous Generator Increased

02/23/2014 2:32 PM

How did you synchronize then? The no load terminal voltage should have shot up also, making it impossible to match voltages with the incoming bus. If that did not happen then there is something wrong with the current transducer circuitry or the field winding.

If the plant synchronized successfully and there was such a large difference in voltages then someone would have noticed the bump. You need to recheck all your controls, metering and relaying settings, plus the generator field and stator windings on the next outage.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Participant

Join Date: Jan 2014
Posts: 4
#3
In reply to #1

Re: No Load Excitation Current of Synchronous Generator Increased

02/24/2014 1:57 AM

See , our Generator terminal voltage is 20 KV..It was so that to get 20 kv during voltage build up before synchronization, the excitation current needed was more than 1160Amps as against normal 875 amps...Is this the case of core saturation or some people sayings may be end ring short...please help me

Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#7
In reply to #3

Re: No Load Excitation Current of Synchronous Generator Increased

03/03/2014 6:04 AM

If your rotor amps metering is by a resistance shunt and moving coil indicator direct in parallel with shunt, it is unlikely to be telling more current than you actually have. If it is electronic, then high reading due to indicator fault is probable.

You have not given the excitation voltage. If you need 20% more DC excitation current, it suggests shorted turns in the rotor - so a lower resistance.

Resistance = voltage/current.

Assuming your rotor temperature is similar at two run-ups, volts/amps for each run-up will give you the resistances to compare. If you have a rotor temperature indicator, you can calculate the resistances at a standard temperature before comparison.

Are you also seeing greater excitation currents on-load at rated output current and power factor than before????

67model

Register to Reply
3
Commentator
India - Member - New Member Engineering Fields - Electrical Engineering - New Member Technical Fields - Technical Writing - New Member

Join Date: Dec 2009
Location: India
Posts: 68
Good Answers: 4
#2

Re: No Load Excitation Current of Synchronous Generator Increased

02/23/2014 10:33 PM

Have you Synchronise the Genset when the Excitation Current was High ??

High Excitation Amp necessarily means high terminal Voltage, if the Aletrnator has not reached Saturation ..

If the Metering and Measurement system is showing correct readings, then this high Excitation current Means some thing wrong with the Excitation Circuit.

Please chcek the following for the Root Cause -

1. Healthyness of Excitator Stator and Exciter Rotor Winding - Measure Resistance & compare with the Catalogue Resistance (Cold Condition) and Megger these windings to check the Insulation Resistance.

2. Healthyness of Rectifier Circuit between Exciter and Main Rotor- All the Rectifiers should be Healthy, if one rectifier is failed in test. Remember to replace all Rectifiers.

3. Check Healthyness of Main Rotor - Measure Resistance & compare with the Catalogue Resistance (Cold Condition) and Megger the winding to check the Insulation Resistance.

If anything of above is not healthy, the Terminal Voltage may not shoot up with this high excitation.

If the Terminal Voltage is Shooting up heavily then please look into the Control Circuit associated with the Excitation ( AVR etc)

The best way is to call the competent person from the Alternator Manufacturer and let him investigate the problem...

Regards,

Register to Reply Good Answer (Score 3)
Participant

Join Date: Jan 2014
Posts: 4
#4
In reply to #2

Re: No Load Excitation Current of Synchronous Generator Increased

02/24/2014 1:58 AM

See , our's Generator terminal voltage is 20 KV..It was so that to get 20 kv during voltage build up before synchronization, the excitation current needed was more than 1160Amps as against normal 875 amps...Is this the case of core saturation or some people sayings may be end ring short...please help me

Register to Reply
Power-User

Join Date: May 2013
Posts: 351
Good Answers: 22
#5
In reply to #4

Re: No Load Excitation Current of Synchronous Generator Increased

02/24/2014 3:57 AM

You have one of two problems.

1. The reading is incorrect either when it was reading 875 or when it was reading 1160 due to a problem in the monitor circuit. Not uncommon reading DC amps. Shunts are most reliable but not all that accurate but will not read high unless part of it is burnt out. Hall effect transducers are fairly accurate but may be affected by outside fields.

2. The excitation winding or connections to it have a short. Unlikely to be in the slip rings, but those can frequently be observed while in operation.

If this were my unit, I would look for the soonest (like right now!) I could pull an outage and then start checking. It could be something simple in the monitoring circuit that will not cause problems but if it is in the excitation winding itselt, it could cause a lot more expense to wait. Infrared camera monitoring might show something. I used to carry a large clip on DC amp meter with me when I worked on exciters. Usually it was metering but I have had shorts, usually in the excitation winding itself. Only once was it in the leads from the slip rings to the winding. Never was it in the slip rings.

Register to Reply Score 1 for Good Answer
Member

Join Date: Feb 2014
Posts: 6
#6
In reply to #5

Re: No Load Excitation Current of Synchronous Generator Increased

02/24/2014 9:11 AM

Yes, assuminmg the generator is running ok and no signs of overheating or vibration, certainly looking like instrumentation problem, what is the on load field current and how does this compare with the normal figures?

Register to Reply
Participant

Join Date: Jan 2014
Posts: 4
#8
In reply to #6

Re: No Load Excitation Current of Synchronous Generator Increased

03/03/2014 11:51 AM

onload rated fld current is 2075Amps..ie, at 300 MW...But the amps going near 2000 even at 250 MW..

Register to Reply
Register to Reply 8 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

4wsilver (1); 67model (1); RAMConsult (1); santanuantara (3); ukeagle (1); vishram lele (1)

Previous in Forum: 230/7.5kV Transformer   Next in Forum: Formula About Minimum Phase-Earth Distance

Advertisement