Formula About Minimum Phase-Earth Distance

02/24/2014 4:50 AM
hi,

I need your help about distance of phase-earth on a HV tower formula.

here L = (U/150)+0,05

for 170 kV L= 118 cm

obviously it is not enough because of arcing traces on silicon insulator at the pictures.

What does your local code say about that in your country ????

__________________
Either exist as you are or be as you look. Rumi
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Formula about Minumum Phase-Earth Distance

02/24/2014 6:48 AM

What if that were the last evidence of a large seagull that got a bit too close?

Why one insulator and not the other?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Off Topic
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2
In reply to #1

Re: Formula about Minumum Phase-Earth Distance

02/24/2014 7:11 AM

And why in different places instead of the whole insulator?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Off Topic
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3
In reply to #2

Re: Formula about Minumum Phase-Earth Distance

02/24/2014 7:15 AM

And what sort of numpty would install insulators on a 170kV line that were not up to the job?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9910
Good Answers: 1141
#17
In reply to #1

Re: Formula about Minumum Phase-Earth Distance

02/25/2014 8:25 AM

Could have been a lightening strike or some knothead released a mylar party balloon!

Register to Reply
Guru

Join Date: Jun 2010
Posts: 1296
Good Answers: 104
#4

Re: Formula about Minumum Phase-Earth Distance

02/24/2014 8:22 AM

Seems like in 2 years, you would have worked this out.

Register to Reply
Power-User

Join Date: Mar 2010
Posts: 105
#8
In reply to #4

Re: Formula about Minumum Phase-Earth Distance

02/24/2014 12:01 PM

yes, you are right but I couldn't find its answer. They always tease

__________________
Either exist as you are or be as you look. Rumi
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#5

Re: Formula about Minumum Phase-Earth Distance

02/24/2014 9:05 AM

The local code in my country says that you should know what you are doing before working with anything over 120 V.

That disqualifies you.

Register to Reply
Power-User

Join Date: Mar 2010
Posts: 105
#10
In reply to #5

Re: Formula about Minumum Phase-Earth Distance

02/24/2014 1:22 PM

do u know everything?

at least I could have learned that I don't know. What about you!!!!

__________________
Either exist as you are or be as you look. Rumi
Register to Reply
Guru
India - Member - Sensors Technology Popular Science - Cosmology - Dream, Think and Act United Kingdom - Member - New Member United States - Member - New Member Canada - Member - New Member

Join Date: Aug 2006
Location: AM-51, Deen Dayal Nagar, Gwalior, Madhya Pradesh, MP 474001, India
Posts: 3418
Good Answers: 32
#16
In reply to #5

Re: Formula about Minumum Phase-Earth Distance

02/24/2014 10:42 PM

Lyn;

Why 120V won't cause any accident? I have seen one engineer shorted 6V and wire sleeve melted in his hand and he had to go to hospital finally.

I think, few million electrons one may swallow but be careful with lots of charge anywhere. Remember that post in which the entire house was burnt due to spark in the wiring.

I think it might have happened in some kind of acid rain when conductive water simply zipped the heavy arc. Water will simply drip over and there may be some dust accumulated over the insulator. They are supposed to be cleaned. This looks more reasonable. Some bird or bat getting hit is also possible.

I think there must some life also for these insulators after which they are to be replaced.

That black thing looks from safety arc electrodes through some dust in the air or perhaps something in ir due to local fire or chemical release. That is why it is on one side where over voltage protection arc electrodes are.

__________________
Prof. (Dr.) Shyam, Managing Director for Sensors Technology Private Limited. Gwalior, MP474001, India.
Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6

Re: Formula About Minumum Phase-Earth Distance

02/24/2014 10:47 AM

It is not possible to tell whether the equation works for free air or for a particular composition of insulator. Where did it come from, please?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
3
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#7

Re: Formula About Minumum Phase-Earth Distance

02/24/2014 11:56 AM

"...obviously it is not enough because of arcing traces on silicon insulator at the pictures...", not really so obvious. You are making the assumption that those dark spots are due to clearance problems, if that were the case the insulators would always be glowing.

What is probably happening is that the ambient atmosphere has heavy pollution or is near a body of saltwater that is laying deposits on the insulator strings. During times of rain or fog those deposits become decent conductors and you get your flashovers, especially if there are any nearby lightning strikes or switching surges that significantly spike the voltage momentarily.

You're also wondering why the arcing tips aren't diverting the surge, that's because moist air is still a better insulator than moist salt or dust. What you're observing is "tracking" which often requires an increased creep distance that is solvable by using deep skirt insulator strings, special insulator coatings/finishes, or by using live-line insulator washing techniques.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Good Answer (Score 3)
Power-User

Join Date: Mar 2010
Posts: 105
#9
In reply to #7

Re: Formula About Minumum Phase-Earth Distance

02/24/2014 1:07 PM

hi RAMConsult,

Thanks for your noble answer. I am also wondering that value creep distance for 170 kV should be. Could you calculate it for me?

You don't look like PWSlack.

Thanks again..

__________________
Either exist as you are or be as you look. Rumi
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#11
In reply to #9

Re: Formula About Minumum Phase-Earth Distance

02/24/2014 1:24 PM

I am sure if you ask nicely RAMConsult will direct you to the relevant American HV insulator standard where the values can be obtained.

You want the values applicable for American insulators right?

__________________
jack of all trades
Register to Reply
Power-User

Join Date: Mar 2010
Posts: 105
#12
In reply to #11

Re: Formula About Minumum Phase-Earth Distance

02/24/2014 1:29 PM

et tu brutus ?

__________________
Either exist as you are or be as you look. Rumi
Register to Reply
Power-User

Join Date: Mar 2010
Posts: 105
#13
In reply to #11

Re: Formula About Minumum Phase-Earth Distance

02/24/2014 1:32 PM

yes please. assume that I asked nicely.

sorry for english barrier.

but try to say a hi, just hi in my language...

__________________
Either exist as you are or be as you look. Rumi
Register to Reply
Guru

Join Date: Aug 2009
Location: Glen Mills, PA.
Posts: 2385
Good Answers: 114
#14

Re: Formula About Minumum Phase-Earth Distance

02/24/2014 4:59 PM
__________________
In a time of universal deceit, telling the truth is a revolutionary act. George Orwell
Register to Reply
4
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#15

Re: Formula About Minumum Phase-Earth Distance

02/24/2014 6:09 PM

"Noble answer"??? Sorry, they cost real dollars. For free you get to do your own work (but the education is priceless).

I like this particular catalog because it answers your question, but only after you have truly educated yourself on the task before you (never mind that it's for post insulators, you'll get the idea). Hint: as you will discover after reading the material, you have left out a very critical piece of information, the BIL (Basic Impulse/Insulation Level), something which cannot be determined from here.

When you're done check out this paper and this catalog, they deal directly with your situation. There's lots more available via Googling, especially from the IEEE and CIGRE.

Work your way through the details and compare your current insulator string to others. You probably won't like the answer, but it brings renewed meaning to the phrase, "How come there's never time (money, etc.) to do it right the first time, but always plenty of time (money, etc.) to do it over."

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Good Answer (Score 4)
Guru
India - Member - Sensors Technology Popular Science - Cosmology - Dream, Think and Act United Kingdom - Member - New Member United States - Member - New Member Canada - Member - New Member

Join Date: Aug 2006
Location: AM-51, Deen Dayal Nagar, Gwalior, Madhya Pradesh, MP 474001, India
Posts: 3418
Good Answers: 32
#19
In reply to #15

Re: Formula About Minumum Phase-Earth Distance

02/25/2014 9:10 PM

RAMConsult;

Dirt or contamination estimation and maintenance by cleaning supposed to be an integrated part of cost effective plan. There is nothing like a design totally fool proof protected forever.

Most interesting event was when lightning stuck the base of the Moscow Tower leaving all top electrode purposeless for the event. Corona path is also statistical and there is a probability that all calculations that were buried in under estimation may actually happen as some nasty surprise. These are risk factors known to all designers and are somehow accepted as rare "sudden death" events / hazards.

I think micro corona currents can be easily measured in zones and then cleaning procedure can be initiated at times earlier than scheduled under regular plan as some kind of emergency procedure as catastrophe preventing.

__________________
Prof. (Dr.) Shyam, Managing Director for Sensors Technology Private Limited. Gwalior, MP474001, India.
Register to Reply
Guru

Join Date: Feb 2013
Posts: 2004
Good Answers: 31
#18

Re: Formula About Minimum Phase-Earth Distance

02/25/2014 1:44 PM

Firstly what were the conditions at time of the failure? 2nd. Looking at the polymeric shed, this did not happen over night. This was a long term condition and the first thing that pops to mind if that the polymeric were very dirty from deposits of dust, salt or another conductive dust.

What does the surrounding area comprise of, industry wise? Where is this tower located? Open space, near a cement factory, heavy industry etc. Do the corona rings have carbonising on the surfaces? Look closer and I think you may discover that they failed due to poor maintenance, (cleaning), and damp air, (fog, humidity, rain). If the insulators were clean the flash over would have flashed over the arcing horns rather than a leap over the rain shed. Least path of resistance was down the polymeric and this can only be caused by dirt on the shed.

The left hand side top poly looks grimy and dirty where the right side one is slightly cleaner looking.

Just an educated guess without all the details and it is a good place to start looking. What do the other line insulators look like?

Register to Reply
Power-User

Join Date: Mar 2010
Posts: 105
#20

Re: Formula About Minimum Phase-Earth Distance

02/26/2014 3:12 AM
__________________
Either exist as you are or be as you look. Rumi
Register to Reply
Guru
India - Member - Sensors Technology Popular Science - Cosmology - Dream, Think and Act United Kingdom - Member - New Member United States - Member - New Member Canada - Member - New Member

Join Date: Aug 2006
Location: AM-51, Deen Dayal Nagar, Gwalior, Madhya Pradesh, MP 474001, India
Posts: 3418
Good Answers: 32
#29
In reply to #20

Re: Formula About Minimum Phase-Earth Distance

03/05/2014 1:48 AM

englis;

They look pretty dirty.

__________________
Prof. (Dr.) Shyam, Managing Director for Sensors Technology Private Limited. Gwalior, MP474001, India.
Register to Reply
Power-User

Join Date: Mar 2010
Posts: 105
#21

Re: Formula About Minimum Phase-Earth Distance

02/26/2014 3:15 AM
__________________
Either exist as you are or be as you look. Rumi
Register to Reply
Power-User

Join Date: Mar 2010
Posts: 105
#22

Re: Formula About Minimum Phase-Earth Distance

02/26/2014 3:17 AM
__________________
Either exist as you are or be as you look. Rumi
Register to Reply
Power-User

Join Date: Mar 2010
Posts: 105
#23

Re: Formula About Minimum Phase-Earth Distance

02/26/2014 3:20 AM
__________________
Either exist as you are or be as you look. Rumi
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#24

Re: Formula About Minimum Phase-Earth Distance

02/26/2014 7:52 AM

Thanks for the pictorial feedback! Obviously the wrong choice of insulator type for the environmental conditions. The flat undersurface and lack of deep skirts/sheds allows for an easy path through any material that collects on those surfaces. I'll bet removing those insulator strings from service cost a few bucks.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Power-User

Join Date: Mar 2010
Posts: 105
#25
In reply to #24

Re: Formula About Minimum Phase-Earth Distance

02/26/2014 8:21 AM

My fellow man, thanks for your serious replies.

__________________
Either exist as you are or be as you look. Rumi
Register to Reply
Guru

Join Date: Feb 2013
Posts: 2004
Good Answers: 31
#26

Re: Formula About Minimum Phase-Earth Distance

02/27/2014 5:50 AM

I would guess that the budget is now set for insulator cleaning on this line?

Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#27

Re: Formula About Minimum Phase-Earth Distance

03/03/2014 12:46 AM

In my opinion what do you need it is the recommended creepage path. See IEC 60071-2 Table 1 - Recommended creepage distances

__________________
Julius
Register to Reply
Power-User

Join Date: Mar 2010
Posts: 105
#28
In reply to #27

Re: Formula About Minimum Phase-Earth Distance

03/05/2014 1:15 AM

I don't have that is why if you have that as pdf, can u send me ?

__________________
Either exist as you are or be as you look. Rumi
Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#30
In reply to #28

Re: Formula About Minimum Phase-Earth Distance

03/10/2014 2:22 AM

engilis, I am sorry, I cannot send you the standard-first of all in my Microsoft Office it is not Acrobat software and second this will be against the forum rules. So I check the creepage path for 170/sqrt(3) kV, for very polluted atmosphere =31*170/sqrt(3)=3042 mm.

Most of composite [silicon+] for this voltage present more than 4000 mm. So I don't know what could be your problem. You have to consult the insulator Manufacturer, I guess.

__________________
Julius
Register to Reply
Register to Reply 30 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: