Transformer Temperature Trip

03/11/2014 4:02 AM

Hello Engineers,

In our site compact substation, The 5 MVA Dry-Type Transformer got tripped due to over temperature rise. i have checked the TF Temp relay it shows L1 = 130, L2 = 55, L3 = 53. what could be the resaon for temp rise in single phase? is it due to unbalance loading?

i already checked cooling fan and ventilation fan, its all working fine.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#1

Re: Transformer Temperature Trip

03/11/2014 5:03 AM

I wouldn't know without measuring the current on each phase, Uncle. You could do that.

__________________
Good moaning!
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#2

Re: Transformer Temperature Trip

03/11/2014 2:33 PM

Shorted winding on L1 inside the transformer itself perhaps.

Your unlikely to find it with a standard meter but a specialised meter that can detect shorted windings should be able to. I don't know what their proper name is, but you can hire them.

__________________
jack of all trades
Register to Reply
Commentator

Join Date: Jul 2013
Posts: 56
Good Answers: 1
#14
In reply to #2

Re: Transformer Temperature Trip

03/12/2014 8:52 AM

I believe it is called a TTR meter? (Transformer turns ratio). We got a temp pad mount xformer once that was giving funny voltage reading. Turned out to be a 385V instead of 480V nameplate was wrong. They used one to find out what it was.

Register to Reply
Guru
India - Member - Sensors Technology Popular Science - Cosmology - Dream, Think and Act United Kingdom - Member - New Member United States - Member - New Member Canada - Member - New Member

Join Date: Aug 2006
Location: AM-51, Deen Dayal Nagar, Gwalior, Madhya Pradesh, MP 474001, India
Posts: 3418
Good Answers: 32
#3

Re: Transformer Temperature Trip

03/11/2014 11:45 PM

sethuamanj:

Core saturation and harmonics can do such a wonderful job of transforming transformer into an oven. How much temperature did you notice?

__________________
Prof. (Dr.) Shyam, Managing Director for Sensors Technology Private Limited. Gwalior, MP474001, India.
Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#4

Re: Transformer Temperature Trip

03/12/2014 1:52 AM

is it due to unbalance loading?

Highly probable.

As already suggested. Measure the loading on each phase and then conclude or delve deeper.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Commentator

Join Date: Jan 2014
Location: Korba, Chattisgarh, India 495450
Posts: 64
Good Answers: 2
#5

Re: Transformer Temperature Trip

03/12/2014 3:05 AM

THERE COULD BE MORE THAN ONE REASONS FOR THE PROBLEM.

FIRST THE UNBALANCED LOAD, FOR WHICH YOU NEED MEASURING LOAD CURRENT AND ANALYSE.

SECOND IT COULD BE COIL SHORT CIRCUITING.. YOU MAY HAVE TO MEASURE TURNS RATIO IN COILS AND NOTE ABNORMALITY. THIS CAN EVEN BE MEASURED BY OUTPUT VOLTAGES IN ALL THE PHASES.

THIRD COULD BE HARMONICS IN INPUT SUPPLY.

AND FOURTH I AM NOT SURE SOME ONE TALKED OF MAGNETIC SATUARTION OF CORE. MAY BE IT RESULTS FROM ALL THE THREE ABOVE...

SOME FUNNY THINGS LIKE LOOSE CONTACTS AT THE TERMINATION COULD SOMETIMES MAY BE THE CAUSE. CHECK THEM TOO.

__________________
Let us discuss the practical issues not the classroom.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#7
In reply to #5

Re: Transformer Temperature Trip

03/12/2014 5:19 AM

Sssssshhhhhhhhhhhhhhhhhhhhhhhh!

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#8
In reply to #7

Re: Transformer Temperature Trip

03/12/2014 5:25 AM

HUH???

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply Off Topic (Score 5)
Power-User

Join Date: Jun 2012
Posts: 123
Good Answers: 7
#9
In reply to #8

Re: Transformer Temperature Trip

03/12/2014 5:41 AM

He means you should turn off "Caps Lock" on your keyboard.

Register to Reply Off Topic (Score 5)
Active Contributor

Join Date: Mar 2013
Posts: 14
#17
In reply to #5

Re: Transformer Temperature Trip

03/12/2014 10:17 PM

hello sir,

First thanks for your response.. As you suspect coil short circuit. Is they is any chance for getting coil short circuit when transformer working normally for more than 6 months continuously.

Register to Reply
Power-User

Join Date: Jun 2012
Posts: 123
Good Answers: 7
#6

Re: Transformer Temperature Trip

03/12/2014 4:03 AM

Just a guess.

Most of the possible causes of high temperature have been suggested.

However, does the L1 temperature sensing device output in fact conform to the actual temperature at its probe?

Register to Reply Score 1 for Good Answer
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#10

Re: Transformer Temperature Trip

03/12/2014 6:11 AM

Give more details from name plate like vector group,voltage,current & type of temperature trip & what other protective relays are installed.

__________________
pnaban
Register to Reply
Active Contributor

Join Date: Mar 2013
Posts: 14
#16
In reply to #10

Re: Transformer Temperature Trip

03/12/2014 10:07 PM

hello,

It is 5MVA 22kv/11kv Dry-Type transformer, vector group = dyn11, temp relay is a china made with PT100 sensor. thanks for ur response.

Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#18
In reply to #16

Re: Transformer Temperature Trip

03/12/2014 10:32 PM

Check the relay or replace with another & see. You didn't mention nameplate current.

__________________
pnaban
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#11

Re: Transformer Temperature Trip

03/12/2014 6:32 AM

How about a telephone call to the transformer manufacturer's Technical Helpline?

What does it say on the equipment's maintenance records?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Member

Join Date: Dec 2012
Location: Chennai, Tamil Nadu, India
Posts: 8
#12

Re: Transformer Temperature Trip

03/12/2014 7:23 AM

Mr, Iyengar has correctly predicted the cause.

To repeat it may be due to one of these reasons

1) an inter turn short , which may not be detected by differential protection depending upon where short circuit accured in the winding.

2) May be due to magnetic circuit fault (I.e., imperfection or damage on insulation of core) resulting in local eddy current circulation.

Both of these diffect can be identified by conducting a magnetic balance test.

Register to Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#13

Re: Transformer Temperature Trip

03/12/2014 8:48 AM

You may have a loose, or high resistance xfmr connection that is causing the temperature rise.

Scanning the connections and windings during operation with a camera or other non-contact thermal scanning device should help identify where the issue is originating.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply
Commentator

Join Date: Nov 2011
Posts: 56
Good Answers: 1
#15

Re: Transformer Temperature Trip

03/12/2014 9:52 PM

Very unlikely high windingtemp due to winding / load faults to be picked up by just one temp sensor whereas the temp rise had not spread to the neighbouring windings through the core.Probably the thermocouples or senseing units are questionable .

Register to Reply
Active Contributor

Join Date: Dec 2013
Posts: 10
#19

Re: Transformer Temperature Trip

03/12/2014 10:47 PM

the fegure you mention, is this vlotage reading or current reading?

Register to Reply Off Topic (Score 5)
Commentator

Join Date: Jan 2014
Location: Korba, Chattisgarh, India 495450
Posts: 64
Good Answers: 2
#20

Re: Transformer Temperature Trip

03/13/2014 12:13 AM

Now that various suggestions have come qand many agree that all the probable causes are listed out there, Better start from doubting the sensor reading. Once ensure that the readinbg is actual and ok then proceed to rest seeing easier one first unless you are more than sure that it is noit the fault by your local and situationjal decisions.

__________________
Let us discuss the practical issues not the classroom.
Register to Reply
Participant

Join Date: Jun 2014
Posts: 1
#21

Re: Transformer Temperature Trip

06/04/2014 1:50 AM

Transformer heating is a result of higher impedance, which is due to higher DC loads connected to xmer.

Register to Reply
Register to Reply 21 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Apol (1); Crabtree (1); jack of all trades (1); justthecowboy (1); M.R.Iyengar (2); nath (1); panneerselvam (1); pillay (1); pnaban (2); PWSlack (2); sethuamanj (2); SHOCKHISCAN (1); Shyam (1); Wal (2); Zvi (2)

Previous in Forum: Voltage Drop Calculation for Overhead Lines   Next in Forum: Discrimination Charts with XT Range of ABB MCCBs

Advertisement