Protection Relay Settings

03/14/2014 2:57 PM

Hi All I want to know that what are the general setings for protection relays. Relays as below Under overvoltage Under over freq Reverse power Diff realay Ground fault curent Overcurent

Register to Reply
Pathfinder Tags: protectin
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#1

Re: protection relay settings

03/14/2014 3:11 PM

They're whatever the general says they should be. That is unless you're on a ship. Then it depends on whatever the admiral says.

Removing the jocularity from my point, it all depends on where and how these relays are used. That is exactly why these relays can be adjusted.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: Protection Relay Settings

03/14/2014 4:17 PM

Co-Pilot Roger Murdock (to Capt. Oveur): We have clearance, Clarence.

Capt. Oveur: Roger, Roger. What's our vector, Victor?


Dr. Rumack: Captain, these passengers don't have much time. How soon can we land?

Oveur: I can't tell.

Dr. Rumack: You can tell me, I'm a doctor.

Oveur: What I mean is, I don't know.

Dr. Rumack: Well can't you take a guess?

Oveur:...Not for another two hours.

Dr. Rumack: You can't take a guess for another two hours?

Oveur: No what I'm saying is we can't land for another two hours.

Register to Reply Score 2 for Off Topic
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#3

Re: Protection Relay Settings

03/14/2014 5:59 PM

Sure! Undervoltage relay shall be set lower than the Overvoltage relay, Overvoltage relay shall be set higher than the Undervoltage relay; Underfrequency relay shall be set lower than the Overfrequency relay, Overfrequency relay shall be set higher than the Underfrequency relay; Reverse Power relay shall be set in the opposite direction of other relays; Differential relay shall be set differently than the other relays; Ground Fault relay shall be set to detect who's at fault; Overcurrent relay shall be set higher than the past relays.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Score 1 for Good Answer
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#4
In reply to #3

Re: Protection Relay Settings

03/14/2014 8:56 PM

The 4X100 meter relay will require careful baton settings.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Score 1 for Off Topic
Active Contributor

Join Date: Feb 2014
Posts: 11
#5
In reply to #4

Re: Protection Relay Settings

03/15/2014 12:20 AM

Dear Fred,

We have old 10.2 MW generator & we have to recommission the generator. Kindly help me & suggest me the protection relays settings...

Register to Reply
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#11
In reply to #5

Re: Protection Relay Settings

03/15/2014 8:57 AM

Hey don't all you guys have that service manual in your back pocket. Now what did he say the make, model and serial number was anyway.

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#15
In reply to #5

Re: Protection Relay Settings

03/16/2014 2:32 PM

What protection relays are you using?

Given your previous questions it would be better and safer to hire a consultant who can analyse your application and provide you with the correct settings. Any opinion (other than the most basic generalisation) we post here is unlikely to be correct due to the complete lack of information.

__________________
jack of all trades
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#16
In reply to #15

Re: Protection Relay Settings

03/16/2014 3:06 PM

You can lead a horse to water, but you can't change his spots. lyn

Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#17
In reply to #16

Re: Protection Relay Settings

03/16/2014 3:14 PM

Totally off topic, I got to use my previous boss's one he used on clients at work last week.

"You can lead a horse to water but you shouldn't be expected to suck on its ass to get it to drink"

It made my point then by the way.

__________________
jack of all trades
Register to Reply Off Topic (Score 4)
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#18
In reply to #17

Re: Protection Relay Settings

03/16/2014 9:40 PM

LOL ROFL I'm going to steal that line in the not too distant future.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Off Topic (Score 5)
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#19
In reply to #18

Re: Protection Relay Settings

03/16/2014 10:23 PM

Really helps to put the stops on an argument so you can get your point across if the other person just isn't listening, especially if the other person isn't expecting it from you.

It pays to have all your facts straight thou so you can talk your way out after saying it. Use it only for good my young Padawan.

__________________
jack of all trades
Register to Reply Off Topic (Score 5)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#21
In reply to #5

Re: Protection Relay Settings

03/17/2014 10:05 AM

If it's a recommission, then the settings should be the same as they were before the work leading to the recommission started. What do the original commissioning records say?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#22
In reply to #5

Re: Protection Relay Settings

03/17/2014 10:24 AM

5 if(it's broken or not working) then 8 else 20

8 gosub 1000

10 if(you buggered about with it) then 100 else 20

20 rem you got away with it

30 end

100 rem you idiot

105 gosub 1000

110 if(someone saw you bugger about with it) then 200 else 120

120 rem you're in luck

130 dump it in the skip

140 end

200 rem you idiot

205 gosub 1000

210 if(you can blame someone else) then 130 else 300

300 rem you are really in deep doodoo

305 gosub 1000

310 if(you can hide it) then 320 else 130

320 no problem

330 end

1000 subroutine panic

1010 panic

1020 return

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#24
In reply to #22

Re: Protection Relay Settings

03/17/2014 10:51 AM

AND IF IT MOVES, SALUTE IT; IF IT DOESN'T MOVE PAINT IT.

They never speak softly in the military.

Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#26
In reply to #22

Re: Protection Relay Settings

03/17/2014 11:40 PM

What a beautiful ballad....made me laugh and cry.....poetic logic.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Power-User

Join Date: Jul 2013
Location: Faridabad Near New Delhi India
Posts: 240
Good Answers: 34
#23
In reply to #5

Re: Protection Relay Settings

03/17/2014 10:43 AM

Is this complete or you require any accessory or control panel or AVR panel, protections or PLC or any other help. We are specialized in this field. In 2007-08 we did similar services for a 5MW 6.6kV MAN BCC (now ABB) Steam Turbine Generator set bought by Asian Biggest Mushrooms Farm in India.

Register to Reply
Active Contributor

Join Date: Feb 2014
Posts: 11
#6
In reply to #3

Re: Protection Relay Settings

03/15/2014 12:22 AM

very funny you should be serious in this forum to attract epople to use this forum & if anyone is new in this field so do not make fun of him...

Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#9
In reply to #6

Re: Protection Relay Settings

03/15/2014 3:47 AM

Friend,

Learn to relax and don't panic.

Humour is better than a box about the ears to demonstrate how vacuous your request for help was.

The recommissioning of a 10.2MW genset is not a minor undertaking. There will be documentation that specifies what the nominal operating parameters should be, aka "what you want", and what permissible deviation from this ideal, aka "what you really don't want" is acceptable for your location and most likely very specifically for the installation that is now in your face.

Big job for a newbie. Enjoy the challenge.

Sumairali, what documentation/records/specs/scope of works/surveys/audits.... do you have? What have you Googled so far? What colour is the turbo encabulator

Where are you?

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#8
In reply to #3

Re: Protection Relay Settings

03/15/2014 3:30 AM

True humour.

OP seems to have been dropped in the deep end.

He will must learn fast or drown.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#7

Re: Protection Relay Settings

03/15/2014 12:29 AM

If you have the correct manuals and operating instructions available, you should not have to ask these questions.

Do you have these manuals and instructions?

Have you read them?

Do you understand then?

Do you have anyone on staff who understands them?

Have you sought professional help?

Have you asked the manufacturer?

What have you done?

No one here can help you unless you give them some useful information, which you have not done, so far.

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#12
In reply to #7

Re: Protection Relay Settings

03/15/2014 11:54 PM

"Have you sought professional help?"

If I hang around this forum much longer I think I'll be needing professional help!

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#13
In reply to #12

Re: Protection Relay Settings

03/15/2014 11:57 PM

Enter forewarned.

The post you read here may be hazardous to your sanity.

Register to Reply
Commentator

Join Date: Sep 2011
Location: Durban South Africa
Posts: 75
Good Answers: 2
#10

Re: Protection Relay Settings

03/15/2014 5:13 AM

try this: http://www.gedigitalenergy.com/Multilin/notes/artsci/index.htm

Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#14

Re: Protection Relay Settings

03/16/2014 11:17 AM

You won't go wrong if you follow the cardinal rule that the relays should not trip at normal values and must trip at when they reach dangerous levels. You are in the best position to judge hwat are dangerous levels, nobody here can help i think. For example, if the normal voltage is 415V and, if it becomes 430V the situation becomes dangerous, then the relay must trip before 430V, preferably say 420V.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
2
Power-User

Join Date: Jul 2013
Location: Faridabad Near New Delhi India
Posts: 240
Good Answers: 34
#20

Re: Protection Relay Settings

03/17/2014 5:49 AM

For Under Voltage, Over voltage, Under Frequency and Over Frequency Protections are set to rating of equipment.

That means look at data sheets of equipment connected.

Assume that Voltage Limit is +/-10% and Frequency is +/-3% (which are normal parameters).

If your protection relays are 2 element, set first element at above limits with time delay as back up and second element at 15% more with time delay of few seconds (Less than 4 to 5 Secs). Best is to see the recovery time of DG Set at block loads. This time delay is to avoid nuisance tripping.

The reverse power relay shall be set at 80% of mechanical efficiency of the Diesel engine. You need Rev Power only if the DG set is synchronized with any other source. If single operation leave it by passed.

Mechanical efficiency means the losses (which is equal to power required to turn the Engine without load), when the Engine is rotated without producing any work - It is mostly friction losses.

Time delay of Rev Power is set to avoid nuisance tripping just after synchronized and can be 10 Sec or more.

If you do not find data above mechanical efficiency of engine - set it at 3% of DG rating 10 Secs.

Generator Earth Fault relay (Restricted Earth Fault relay) shall be set at lowest possible setting and time - normally it is instantaneous relay (max. 20 m secs - 1 cycle for 50HZ). Reason being that probability of Earth Faults is maximum and shall be cut out in minimum of time to avoid any damage.

The DG you are talking appears to be having Neutral grounded through resistance - in this case earth fault is very low and needs accurate CTs (Toroidal CTs at either end to sense fault).

Over current relays are set as a back up to outgoing feeders. That means operating time of O/C relay shall be at least 100 to 120 mSec more than feeder protection.

I do not know which country you are in. I am in India and I supply control synchronizing and protection panels for power plants. Our recent job was in supply installation and commissioning of similar panels for power plant in Sudan for EL Genena and El Fasher Power Plants. You can contact us for any help.

Register to Reply Good Answer (Score 2)
Active Contributor

Join Date: Feb 2014
Posts: 11
#25
In reply to #20

Re: Protection Relay Settings

03/17/2014 2:17 PM

Thanks alot ok i wil contact u if required...

Register to Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#27

Re: Protection Relay Settings

03/20/2014 9:44 AM

Protection relay settings are dependent on the system design, system condition, and equipment requirements.

Suggest you contract with a competent, systems protection enigneering analyst before proceeding to identify your application needs/requirements.

Failure to do this can and will result in severe equipment damage and/or personal injury possibly death.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#28

Re: Protection Relay Settings

06/10/2024 9:47 AM

It would help to know the equipment manufacturer's telephone number. That would enable some calls to be made for advice (invitation declined).

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 28 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

beentheredonethat (1); jack of all trades (3); kvsridhar (1); lyn (5); ozzb (1); powersolutionsFBD (2); PWSlack (3); RAMConsult (1); redfred (3); SHOCKHISCAN (1); sumairali (3); TonyS (1); Wal (3)

Previous in Forum: What is the Difference Between Bkw & kw   Next in Forum: Powerfactor of LED Lamps

Advertisement