Powerfactor of LED Lamps

03/14/2014 10:56 PM

LED lighting era has set in and as the prices come down, more of LED lamps will be deployed for lighting. However, there is a feeling that LED lamps available now have very low pf - say, below 0.5.

Can we get expert's opinion in this pf matter?

__________________
NT Nair, EKL
Register to Reply
Pathfinder Tags: LED lamps powerfactor
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Powerfactor of LED Lamps

03/14/2014 10:59 PM

They're DC. The power factor is 1.

Or do you mean the power supply that is AC?

Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#9
In reply to #1

Re: Powerfactor of LED Lamps

03/16/2014 5:27 AM

GA

True, but has anyone checked the mains versions?

I have loads of 230VAC ones with the GU10 base connector, they are AC......

My personal take (guess really) that they are probably more "capacitive", so may actually "improve" the PF of any normal installation.....I see no inductance inside opened LED lights, but with SMD that may not be completely true.....

Just a thought!!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#2

Re: Powerfactor of LED Lamps

03/14/2014 11:09 PM
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#5
In reply to #2

Re: Powerfactor of LED Lamps

03/15/2014 9:54 AM

The oscilloscope images from this article demonstrates my point about the harmonic content and not the power factor will be the problem that ubiquitous LED lighting will produce. The CFL current draw waveform looks similar to a sine wave but the current is in phase with the voltage waveform. The current waveform of the LED circuit shows a leading current draw (peak current happens before peak voltage) that charging a capacitor will produce. This current spike looks nothing at all like the voltage sine wave.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#10
In reply to #2

Re: Powerfactor of LED Lamps

03/16/2014 5:30 AM

Great link, thanks.

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Associate

Join Date: Mar 2014
Location: Baroda Gujarat India
Posts: 30
Good Answers: 1
#3

Re: Powerfactor of LED Lamps

03/15/2014 4:37 AM

Most LED lamps are "plug in", they come with a built in power supply.

Therefore the pf or power factor would be the connected load. Since it is not a pure resistive load ( due to the power supply ) power factor correction is built in in the control ic. In well made units.

The cheaper one are usually Constant voltage with a resistor for current control.

__________________
MAJMUDAR
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#4

Re: Powerfactor of LED Lamps

03/15/2014 9:33 AM

IMHO The power factor loading an LED assembly will impose onto the grid is the "red herring" problem they will affect onto the grid. The non-linear load of these supplies and diodes will produce much higher harmonic content to the currents in the grid. This will increase the core losses in the power distribution transformers and some what from skin effect of the transmission lines for the same amount of power delivered. Fortunately the efficiency loss will be accompanied by a reduction in total power drawn so this effect will probably just be an academic exercise at first. Eventually this will have the consequence of MV/LV transformers overheating at lower total power levels.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Score 1 for Good Answer
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#6

Re: Powerfactor of LED Lamps

03/15/2014 10:36 AM

DC doesn't vary, there is no reactance

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#7
In reply to #6

Re: Powerfactor of LED Lamps

03/15/2014 10:53 AM

Quite true, which is why the problem lies in the power supply circuitry that drives the LED and not the LED itself.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Score 1 for Good Answer
4
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#8

Re: Powerfactor of LED Lamps

03/15/2014 11:52 AM

Maybe the answer is for us, as a collective modern society, to get off of our collective modern asses and get off of the dendence on AC power utilization for everything, then converting it to DC inside of appliances. Think of how many of the things we use every day are now including that non-linear power supply inside, or if it's a motorized appliance, is using a Universal Motor (which will accept AC or DC). All of those things could just as easily use DC input and forego the converters.

Of course, AC still has the distribution and voltage transformation benefits that made our modern society possible, but is it still necessary to run that all the way down to every single point of use, and THEN change it to DC? Maybe it's time for a new paradigm. Bring AC into a location, then separate it by allowing some AC to go to things like resistive heating and other strictly AC loads, but split off to feed a single large active front end converter with Active Harmonic Elimination (AHE) techniques that then presents a clean sine wave use profile to the source at .95 or better PF. On the DC side then, one could much more easily add in Solar supplements, small BLDC wind generators, small Fuel Cells, batteries, even flywheel storage systems, without all the losses through conversion in every point of use device. Larger appliances such as AC units, washing machines and refrigerators could at first be adapted using VFDs (they can all accept DC input) but over time, be upgraded with E-Motors.

If I get a chance to build a house again in my lifetime, I am going to do it this way, just to prove the point.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 4)
Guru

Join Date: Jan 2006
Location: Tamworth, UK.
Posts: 1782
Good Answers: 45
#11
In reply to #8

Re: Powerfactor of LED Lamps

03/16/2014 7:26 AM

My narrowboat is 12vdc. With an inverter to supply 230vac for equipment not available in dc format.

__________________
When arguing, remember mud-slinging = lost ground.
Register to Reply
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#12
In reply to #8

Re: Powerfactor of LED Lamps

03/17/2014 12:37 PM

I've always wondered why we can't find more appliances with a DC alternative feed. I know that a few manufacturers provide this to cater to boat and camper owners but nearly every device in the home uses DC. And a lot of the AC to DC supplies just barely do the job for any specific device.

The best DC supplies you will find on the market (for your average home) are typically used for personal computers. They provide your 0.95 to 0.99 power factor depending on loading, etc. And for the various levels above or below your standard level there is always the DC-DC converter that has a high efficiency rating.

Maybe we'll get there some day. I believe that it will take an effort from some big companies to get that ball rolling.

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Register to Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#13
In reply to #8

Re: Powerfactor of LED Lamps

03/17/2014 3:47 PM

Well, it is a conspiracy to have all those loose ends waving around in AC, isn't it?

Or mainly speaking, it is just more profitable for the power generators and distributors.

I totally agree with your concept. Nothing bad at all about DC circuits at close range, although the higher power ones might need larger conductors even within a house?

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#14

Re: Powerfactor of LED Lamps

03/20/2014 9:51 AM

Most of the LED lighting I have installed over the last 5 years has been rated at .8 PF.

Some that I have not elected to buy is rated well below the .8 PF and is not an option to purchse for my applications.

A significant amount of LED fixtures lose efficiency due to overheating issues usually related to poor design, cheap components, and power issues.

Buyer beware!

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply
Power-User

Join Date: Jan 2009
Posts: 250
Good Answers: 7
#15
In reply to #14

Re: Powerfactor of LED Lamps

03/20/2014 10:13 AM

LEDs (components) and fluorescent lamps (tube only) have some similarities in their current vs. voltage curves: a zero or small current at lower voltages, a steep increase in current at some voltage threshold. A sinusoidal applied voltage will cause a "lagged" current, which a PF meter will see as low-PF.

Early economy-lamp ballasts used to show a low PF. Nowadays the current consumption shows a high frequency current (rich in harmonics) with a nearly sinusoidal envelope, hence a PF close to 1.

SPS circuits for LED lamps should benefit from prior experience with CFLs.

LEDs have a higher efficiency with pulsed current as compared with pure DC.

Register to Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#16
In reply to #14

Re: Powerfactor of LED Lamps

03/20/2014 10:14 AM

So, this power factor rating is right on the box?

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Register to Reply 16 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Andy Germany (2); Fredski (1); horace40 (1); James Stewart (2); JRaef (1); lyn (1); majmudar (1); NotUrOrdinaryJoe (1); redfred (3); SHOCKHISCAN (1); Snel (1); wareagle (1)

Previous in Forum: Protection Relay Settings   Next in Forum: Post Insulators

Advertisement