MCCB Types C and D?

04/05/2014 2:46 PM

Hi everyone!Nice folks on this forum. I cannot say I know it all because God is the all knowing. But I do have a small question regarding the MCCB's and its types. Type C devices are design to trip at 5-10 times In? 1) If that is true, then why I read so many contributors sizing main MCCB for motor either less or very high than In. 2) How would you size MCCB when the load current happens to be 399 A for any application and then a motor application. I know how is done but I would like to see how is done by you? I would just get to select the next standard size of MCCB, even it be to close to I(L). 3) MCCB Type C must be taking care of the high inrush or start up current? It is designed to handle that? what else? I am forgetting it. Sorry!

__________________
--
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User
Engineering Fields - Power Engineering - New Member

Join Date: Feb 2011
Location: Pakistan
Posts: 126
#1

Re: MCCB Types C and D?

04/05/2014 3:26 PM

Protective devices means MCB or MCCB, therefore I selected MCCB's rather since 399 A is a higher load than 100 A. When a load current is higher than a 100 A, then MCCB is to be used. That's why I am using MCCB. Otherwise, the regulation says MCB rather. So when the load current for a 3 phase motor would come up to 399 A, my next standard size breaker would be selected 400 A. How is that?

__________________
--
Register to Reply
2
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2
In reply to #1

Re: MCCB Types C and D?

04/05/2014 3:34 PM

Motor wiring is sized at 1.25 x FLC; inverse-time circuit breakers can be sized at 2.5 x FLC. (This is in the U.S. NEC, but may differ in your jurisdiction). It also may depend on starting method, and may need consideration of time-to-trip curves for proposed CB selections.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Good Answer (Score 2)
Power-User
Engineering Fields - Power Engineering - New Member

Join Date: Feb 2011
Location: Pakistan
Posts: 126
#4
In reply to #2

Re: MCCB Types C and D?

04/06/2014 4:49 AM

Tornado writes:
>Motor wiring is sized at 1.25 x FLC;
It isn't the case in Abu Dhabi, UAE though.

__________________
--
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#26
In reply to #4

Re: MCCB Types C and D?

04/26/2014 3:08 PM

Then what is the case in Abu Dhabi? In an international forum such as this, weird local schemes must be explained.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Power-User
Engineering Fields - Power Engineering - New Member

Join Date: Feb 2011
Location: Pakistan
Posts: 126
#29
In reply to #26

Re: MCCB Types C and D?

04/27/2014 8:28 AM

Tornado writes after a long time:

>In an international forum such as this, weird local schemes must be explained.

Read the followings. It must not be same but identical. This is the best code thus far that I have come across. It is based on British Standards, I think.

Abu Dhabi old regulations (2007-09) has it,which is still valid and good:

"To ensure protection against overload, Circuit conductors must be sized taking into account the time-current characteristic of the Protective Device.

[Note: in order to provide adequate protection against overload the Protective Device nominal rating must be more than the maximum rating of the Circuit for which overload protection is required, ...]"

__________________
--
Register to Reply
Power-User
Engineering Fields - Power Engineering - New Member

Join Date: Feb 2011
Location: Pakistan
Posts: 126
#12
In reply to #2

Re: MCCB Types C and D?

04/08/2014 10:58 AM

Tornado writes:

>Motor wiring is sized at 1.25 x FLC; inverse-time circuit breakers can be sized at 2.5 x >FLC. (This is in the U.S. NEC, but may differ in your jurisdiction).

My apology in advance. As per regulations, we OUGHT to protect the cable. Then why the MCCB can be sized 2.5 times FLA? I must explain myself again. The full-load current (FLA) comes up to be 399 A. I would like to size my MCCB for the following protections:1) Overload 2) Short-circuit So the normal load current is 399 A. My MCCB size is the next standard CB (higher than FLA) = 400 A. Why would I need 2.5 times?

> It also may depend on >starting method, and may need consideration of time-to-trip curves for proposed CB >selections.

Agree in here. During motor initial stage of starting, it draws a higher current than the normal FLA? Right. That is known as starting current which results in a voltage drop. We use starters to keep the starting currents within the limits. For e.g. the regulation has a chart which states that a motor of rating between 37.3 KW to 112 KW would have max. permissible starting current of 1.5 times FLA. In our case: FLA = 399 A; MCCB = 400 A; Max P Starting C almost = 1.5 x 399 A = 598.5 A or approx. 600 A. But I am shooting to use the type C (MCCB if it is there in the market) which should have a starting current = 10 x FLA = 10 x 399.3 amost = 4000 A. Shouldn't that handle the starting issue when in fact one use a starter with that capacity? I mean if you read above the max. permissible starting current issue of 600 A?I don't find the answer thus far that I am hoping or looking for. It isn't me but that fellow in the other thread would need it. Some one down below talks about breaking current of MCCBs. Well, MCBs has a breaking current too, but in fact lower than MCCBs. That would be in kA rather. It would depend how it would be cascaded? If the motor is directly connected to the LV panel (45-50 kA), then it should have a MCCB (breaker) with 35 kA breaking capacity or so...

__________________
--
Register to Reply Score 1 for Off Topic
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#13
In reply to #12

Re: MCCB Types C and D?

04/08/2014 11:07 AM

The motor is (usually) protected by an overload device (relay, heaters, etc.) In case of "small" overcurrents, this device also protects the wiring. The CB is principally for short circuits, ground faults, or other "large" overcurrents.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Commentator

Join Date: Jan 2011
Posts: 84
Good Answers: 4
#16
In reply to #12

Re: MCCB Types C and D?

04/20/2014 5:50 AM

Appreciate your concern abasins,

The overcurrent due to inrush current is not considered. This magnetizing currend will be 10 to 13 times Full Load Current of the motor. This maximum magnetizing current exists only in the initial cycle (within 20 milliseconds - since UAE frequency is 50Hz) and reduces into the starting current then to the normal load current. The normal instantaneous tripping time of 400A MCCB is 10 ms to 1 ms (for the breaker with 5 to 10 In). If the peak value of the current also is considered for the inrush, it will be increased by another factor of 1.4. The 400A MCCB can not withstand this instantaneous current and hence it will be interrupted definitely.

Another point to be considered is that the 400A rated capacity of the breaker is at standard lab temperature. De-rating should be considered for grouping factor or in a closed cabinet and for ambient temperature. Eventhough the electrical rooms in the UAE are air conditioned, the breakers are derated to 45C for coordination reasons.

Register to Reply
Power-User
Engineering Fields - Power Engineering - New Member

Join Date: Feb 2011
Location: Pakistan
Posts: 126
#17
In reply to #16

Re: MCCB Types C and D?

04/21/2014 2:12 PM

Musthafa writes:

[Appreciate your concern abasins,

[The overcurrent due to inrush current is not considered. This magnetizing current will [be 10 to 13 times Full Load Current of the motor. This maximum magnetizing current [exists only in the initial cycle (within 20 milliseconds - since UAE frequency is 50Hz) [and reduces into the starting current then to the normal load current. The normal [instantaneous tripping time of 400A MCCB is 10 ms to 1 ms (for the breaker with 5 to [10 In). If the peak value of the current also is considered for the inrush, it will be [increased by another factor of 1.4. The 400A MCCB can not withstand this [instantaneous current and hence it will be interrupted definitely.

[Another point to be considered is that the 400A rated capacity of the breaker is at [standard lab temperature. De-rating should be considered for grouping factor or in a [closed cabinet and for ambient temperature. Eventhough the electrical rooms in the [UAE are air conditioned, the breakers are derated to 45C for coordination reasons.

I thank Muthafa for his generous and kind response. Can you read the following and then conclude about why won't the The 400A MCCB withstand this instantaneous current and hence it will be interrupted definitely? The Instantaneous Adjustable trip (breakers) are designed for such. It would trip only when the over current exceeds the maximum set value?

Some more points that would be useful for the topic under discussion:

Cut 'n paste .1:

The instantaneous or "magnetic" pickup was made adjustable, so it could be set above the motor inrush. This was a significant improvement over the fixed instantaneous thermal-magnetic breaker.

<Instantaneous adjustable trip (breaker)>

Cut 'n paste .2:

Circuit Breaker Curves

The following curve illustrates a typical thermal magnetic molded case circuit breaker curve with an overload region and an instantaneous trip region (two instantaneous trip settings are shown). Circuit breaker time-current characteristic curves are read similar to fuse curves. The horizontal axis represents the current, and the vertical axis represents the time at which the breaker interrupts the circuit. When using molded case circuit breakers of this type, there are four basic curve considerations that must be understood. These are: 1. Overload Region 2. Instantaneous Region 3. Unlatching Time 4. Interrupting Rating 1. Overload Region: The opening of a molded case circuit breaker in the overload region is generally accomplished by a thermal element, while a magnetic coil is generally used on power breakers. Electronic sensing breakers will utilize CTs. As can be seen, the overload region has a wide tolerance band, which means the breaker should open within that area for a particular overload current. 2. Instantaneous Region: The instantaneous trip (I.T.) setting indicates the multiple of the full load rating at which the circuit breaker will open as quickly as possible. The instantaneous region is represented in the following curve and is shown to be adjustable from 5x to 10x the breaker rating. When the breaker coil senses an overcurrent in the instantaneous region, it releases the latch which holds the contacts closed. The unlatching time is represented by the curve labeled "average unlatching time for instantaneous tripping." After unlatching, the overcurrent is not halted until the breaker contacts are mechanically separated and the arc is extinguished. Consequently, the final overcurrent termination can vary over a wide range of time, as is indicated by the wide band between the unlatching time curve and the maximum interrupting time curve. The instantaneous trip setting for larger molded case and power breakers can usually be adjusted by an external dial. Two instantaneous trip settings for a 400Abreaker are shown. The instantaneous trip region, drawn with the solid line, represents an I.T. = 5x, or five times 400A= 2000A. At this setting, the circuit breaker will trip instantaneously on currents of approximately 2000Aor more. The ± 25% band represents the area in which it is uncertain whether the overload trip or the instantaneous trip will operate to clear the overcurrent. The dashed portion represents the same 400Abreaker with an I.T. = 10x, or 10 times 400A= 4000A. At this setting the overload trip will operate up to approximately 4000 amps (±10%). Overcurrents greater than 4000A(±10%) would be cleared by the instantaneous trip. The I.T. of a circuit breaker is typically set at its lowest setting when shipped from the factory.

3. Cut 'n paste:

As current increases the magnetic field strength increases, which aids in opening the contacts. This circuit breaker has an adjustable instantaneous trip point from 900 A to 2000 A, which is 4.5 to 10 times the 200 A trip unit rating. If the trip point adjustment is set to minimum (900 A), and a fault current of 900 amps or greater occurs, the breaker will trip within 1 cycle (16.8 ms). If the trip point setting is set to maximum (2000 A), and a fault current of 900 amps occurs, the breaker will trip between approximately 12 and 55 seconds.

A greater fault current will cause the breaker to trip faster.

__________________
--
Register to Reply
Commentator

Join Date: Jan 2011
Posts: 84
Good Answers: 4
#18
In reply to #17

Re: MCCB Types C and D?

04/22/2014 7:58 AM

Detailed provided by OP is self explanatory. OP can look at the curve which is referred in the post. I will add a small math here:

Full load current is 399A. The instantaneous value of this will be 564 (1.414x399A). Now the transient inrush during starting will be 7332 (13x564). If OP looks at the curve, the unlatching time is between 3 & 4 milliseconds.

BTW, why OP is so stringent to use MCCB as an over load protection?. Even though soft start is used as starting method, the breaker is under thermal stress because of the current is at its threshold of 399A.

Register to Reply
Power-User
Engineering Fields - Power Engineering - New Member

Join Date: Feb 2011
Location: Pakistan
Posts: 126
#19
In reply to #18

Re: MCCB Types C and D?

04/23/2014 4:18 AM

Musthafa,

Regarding the math and then my concern is to withstand the initial starting current since MCCB is the first protective device to let through the current. Please read on as I cut 'n paste and explain? :)

< cut and paste from CR4 as mentioned above and below?

{

ii) MCCB + Contactor + Overload Relay

While selecting an MCCB for motor application, it MUST be ensured that the Instantaneous Release setting in the MCCB is set to a value higher than the highest anticipated magnetising inrush current, while switching-on the motor.

How to calculate this value?

Typical Magnitude of Staring Current (Ist): 6 to 8 times the motor rated current (IrM)

Tolerance for Locked Rotor Current as per IS 325 (Table-1): + 20%.

So, the maximum anticipated starting current: 1.2 x 8 = 9.6 IrM

Transient inrush current (peak): √2 x 9.6 IrM = 13.57IrM

Also, vide IS/IEC 60947-2, Clause 7.2.1.2.4, there is a tolerance of +/- 20% in the values of current for tripping of the circuit breaker by short-circuit releases. This means that, even with the -20% tolerance, the MCCB shall not trip for the above magnitude of the magnetising inrush current. This also means that the effective setting of the instantaneous release setting in the MCCB should be above 13.57 / 0.8 = 16.96 IrM; But, this is peak value. Whereas the instantaneous setting in the MCCB is in RMS value. Hence, the above value has to be converted to RMS value; (i.e.) 16.96 / 1.414 = 11.99 IrM; Thus, the instantaneous setting in the MCCB has to be above 11.99 IrM or say, it should be 12 IrM. Assuming that the rated operational current (In) of the MCCB is the same as that of the rated full load motor current (IrM), then, the instantaneous setting in the MCCB shall be set to 12 In.

}

From above and even previous posting under the thread here:

For 400 A MCCB = 10 x In = 10 x 400 = 4000 A

OR: 12 x In = 12 x 400 = 4800 A

It would show the maximum capacity?

As I have posted above:

For 6 x In = 6 x 400 = 2400

For starting current = 5 x 399 = 1995A, it shall not trip. If it is set at lower I.T, then it would trip on 2400 A or above. But if it is adjusted on upper 4000 A, then the I.T would occur when it reaches that level or above. It is shown that it would withstand the initial starting current and won't trip since it is the first protection device. It must allow the required current for the rest electrical circuit (along the motor) to properly function. The MCCB is the first protective device in the circuit. And it is to protect the cable and NOT the motor. The issue of starting current and its reduction as I quote the regulation, "The motor starting current and resulting Voltage drop is reduced when motor starters employing current limiting starting equipment are used." So, I am not concern much about that equipment except to know what I know already i.e. the peak value.

__________________
--
Register to Reply
Commentator

Join Date: Jan 2011
Posts: 84
Good Answers: 4
#20
In reply to #19

Re: MCCB Types C and D?

04/23/2014 8:00 AM

abasins:

<if it is set at lower I.T> You mean the Interruption Time?

Is the MCCB you are referring with selectable time set? If so, it can override the tripping condition by suitably selecting the timing. Again because of thermal stress by the load current of 399 A, it is not recommended. If you are confident about it, try it.

Register to Reply
Power-User
Engineering Fields - Power Engineering - New Member

Join Date: Feb 2011
Location: Pakistan
Posts: 126
#21
In reply to #20

Re: MCCB Types C and D?

04/23/2014 8:29 AM

Musthafa,

I thank you for carrying out meaningful discussion. I.T means Instantaneous trip. Again, you might be very right about the thermal stress but the breaker manufacturer must guarantee that. If you are talking about something else, like my concerns would be (which I am shooting for sizing my breaker) to worry about the temp. rise when current increase in the cable. Due to that heat, the breaker must trip. The cable I would select or size should be rated for 399 A. Beyond that, I would like to protect my cable from overheating and possible damaging, thus the right size MCCB to trip.

__________________
--
Register to Reply
Commentator

Join Date: Jan 2011
Posts: 84
Good Answers: 4
#22
In reply to #21

Re: MCCB Types C and D?

04/24/2014 6:12 AM

Abasins,

We are advised by our forefathers to select the cable for 1.25 times the load current. This is concluded by them form their experiences in vast area. You are just focusing the normal load current FLA of your motor. Normally, you have to select next higher size; how higher is 400 from 399? Not only that, you need to assume a service factor to the motor as 1.1. Then a prolonged positive voltage variation in the distribution system. Again, the star/delta starters in common usage are open transition. During star to delta changing over time, some time the instantaneous peak between the voltage of delta supply to the stator and the generated voltage of the rotor (cause, during transition period rotor is working as generator) will be much higher than the system 400 V. All these factors leads to increase the current beyond the normal load current.

Register to Reply
Power-User
Engineering Fields - Power Engineering - New Member

Join Date: Feb 2011
Location: Pakistan
Posts: 126
#23
In reply to #22

Re: MCCB Types C and D?

04/24/2014 7:43 AM

OK, selecting the CABLE but not the breaker? These are two different things. One would depend on the other...Hahahahaha....I cannot argue with what your forefathers taught you Vs. Abu Dhabi Wiring Regulations...I would follow the regulation until...Just a joke Musthafa and by God no implications as it is truly a slang in my culture, the Pukhtun (Pakistani one)...It says that the animosity of camel is expensive...Likely to the end??? Why is that? Another saying is that the tale seems longer as the fart of a camel? OR, your tale is so long which amounts to be a fart of a camel? Why is that? My apology in advance as enjoyed your humor...

__________________
--
Register to Reply
Commentator

Join Date: Jan 2011
Posts: 84
Good Answers: 4
#24
In reply to #23

Re: MCCB Types C and D?

04/26/2014 6:54 AM

If the cable can be selected for 1.25 x In (=500A),why the breaker can not be 500A, since it is is used for cable circuit protection only. Does the utility provider, ADDC not allow you to use 500A MCCB with 2 nos 150sq.mm cable as feeder ?

Register to Reply
Power-User
Engineering Fields - Power Engineering - New Member

Join Date: Feb 2011
Location: Pakistan
Posts: 126
#25
In reply to #24

Re: MCCB Types C and D?

04/26/2014 2:43 PM

Musthafa writes:
>If the cable can be selected for 1.25 x In (=500A),why the breaker can not be 500A,
Musthafa, you may be right in your ways, but "In" is the current the breaker is rated with. You cannot use it twice "In" i.e once 400 A & then 500 A. I don't use or buy that formula, even it might come closer to the my results though. Remember, the I (load) = 399 A; and we selected the next standard size breaker = 400 A. Now having said that, you can certainly select a 500 A MCCB if you think you would like. (1) First of all, there isn't a standard 500 A MCCB here in UAE, that I know of. (2) After the MCCB 400 A size, the next standard size could be 630 A. You may select a 630 A instead.
>since it is is used for cable circuit protection only. Does the utility provider, ADDC not >allow you to use 500A MCCB with 2 nos 150sq.mm cable as feeder ?
They may allow it. I don't know about that since I never worked for ADDC. I have only passed their competency exam to be a qualified electrical engineer. It must be filled by Arab engineers :) I could explain further but at this time I would refrain from two cables MCCB etc. Let me paste the part of regulations if I could find about sizing diff...

__________________
--
Register to Reply Score 1 for Off Topic
Commentator

Join Date: Jan 2011
Posts: 84
Good Answers: 4
#27
In reply to #25

Re: MCCB Types C and D?

04/26/2014 11:49 PM

First of all, my congratulation in passing ADDC competency exam.

630A breaker with adjustable (80 to 100%) thermal setting is available.

BTW, jokes are good for health; and remembering old proverbs always enlighten your ways.

Register to Reply
Power-User
Engineering Fields - Power Engineering - New Member

Join Date: Feb 2011
Location: Pakistan
Posts: 126
#28
In reply to #27

Re: MCCB Types C and D?

04/27/2014 4:03 AM

>First of all, my congratulation in passing ADDC competency exam.

Thanks a bunch. You are the first one (Arab or non-Arab) greeting me on this forum. The ones, Arabs, on my last job were about to fight me, out of jealousy up on hearing on my success, despite the fact I called KFC delivered to them out of joy. It serves me no purpose as it does for the Arabs. The Arabs get to open company with it, registered it, get higher salaries with it, and make more opportunities for themselves by passing this exam etc. And I am still at it in the country of my dear religious brothers and the land of hospitality and opportunity...

>630A breaker with adjustable (80 to 100%) thermal setting is available.

>BTW, jokes are good for health; and remembering old proverbs always enlighten your >ways.

I enjoyed. No hard feelings please!

__________________
--
Register to Reply Off Topic (Score 5)
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#3

Re: MCCB Types C and D?

04/05/2014 10:52 PM

An MCCB is not a motor protector.

MCCBs protect the conductors and should be sized in accordance with the conductor sizing.

Conductor sizing is selected according to the load, acceptable voltage drop on load and fault current levels.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Power-User
Engineering Fields - Power Engineering - New Member

Join Date: Feb 2011
Location: Pakistan
Posts: 126
#5
In reply to #3

Re: MCCB Types C and D?

04/06/2014 4:58 AM

Wal writes:

>An MCCB is not a motor protector.

Yes. I said it is a Protective Device only.

>MCCBs protect the conductors and should be sized in accordance with the >conductor sizing.

>Conductor sizing is selected according to the load, acceptable voltage drop on >load and fault current levels.

It isn't the case when you write according thee load in Abu Dhabi, UAE though.

Actually, that motor problem in that other thread I am trying to post. The problem with 210 KW etc. Hahahaha...

So the load current comes out to be 399 A and my selection of MCCB would be 400 A. To make it more simpler, I must add to it by saying that the starting current for type C would get to be = 10 x FLA = 10 x 399.3 amost = 4000 A

I am still waiting on ....Hehehehe...

__________________
--
Register to Reply
2
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#6
In reply to #5

Re: MCCB Types C and D?

04/06/2014 5:29 AM

Well, it is nice to see that you are humorous.

A 210kW motor requires good, sophisticated protection. Against overloads, unbalanced supply voltage, single-phasing (an extreme case of unbalanced voltage), clogged airflow passages, overheated rotor (if it is a squirrel cage motor), so on. There are very good motor protection relays which protect the motor agains all these. You can use such a relay, which in conjunction with a good contactor, provides good protection.

An MCCB or an MCB (i can't decide which one you are talking about, since B/C/D curves refer to MCBs, not MCCBs) is mainly meant for short-circuit protection. Such a fault is not internal to the motor, and occurs outside it generally. If a motor develops a short-circuit within itself, obviously there is no point in protecting it! You need to protect the source and the cables, controlgear etc form damage, for which purpose an MCB / MCCB is used. So, you need not size the MCCB precisely to the motor characteristics. You need to size it for the circuit. It must not nuisance-trip when the motor starts of course, but it should not be expected to protect the motor.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply Good Answer (Score 2)
Power-User
Engineering Fields - Power Engineering - New Member

Join Date: Feb 2011
Location: Pakistan
Posts: 126
#7
In reply to #6

Re: MCCB Types C and D?

04/06/2014 6:25 AM

kvsridhar wites:
>An MCCB or an MCB (i can't decide which one you are talking about, since B/C/D curves >refer to MCBs, not MCCBs) is mainly meant
The following link has it. The CB 250 A cannot be MCB? Right? 250 A must be MCCB rather...Read on...
Magnetic Tripping Characteristics

http://static.schneider-Thermal-magnetic circuit breakers 250 A frame and larger have an instantaneous magnetic trip which in most cases is adjustable from 5 to 10 times the circuit breaker's ampere rating. A single magnetic adjustment on the face of each circuit breaker sets the limits of the magnetic trip mechanism, which simultaneously adjusts all poles of the two or three pole breaker to the same magnetic trip level.
telectric.us/docs/Circuit%20Protection/Molded%20Case%20Circuit%20Breakers/0100-400%20A%20Frame%20FA-LA/FA-FC-FH/0600DB0105.pdf

__________________
--
Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#9
In reply to #7

Re: MCCB Types C and D?

04/06/2014 8:28 AM

i have not heard an MCCB characteristic refeered to as B, C or D though it may follow the same curves. Maybe in your area it is the pratice. Not important, it is an inconsequential point.

The main point is that the motor needs a motor-protection relay, while the whole circuit needs sc protection by an MCCB.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Power-User
Engineering Fields - Power Engineering - New Member

Join Date: Feb 2011
Location: Pakistan
Posts: 126
#8
In reply to #3

Re: MCCB Types C and D?

04/06/2014 7:30 AM

Wal writes:

>An MCCB is not a motor protector.

Wal, it is to protect the cable. I know that...:)

>MCCBs protect the conductors and should be sized in accordance with the >conductor sizing.

>Conductor sizing is selected according to the load, acceptable voltage drop on load >and fault current levels.

Remember I quoted from the regualtions the other day. So, here we go again:

The CROSS-SECTION of cables MUST be slected according to the EXPECTED LOAD, Voltage drop, ambient TEMP and ....

__________________
--
Register to Reply
Associate

Join Date: Apr 2014
Posts: 51
#10

Re: MCCB Types C and D?

04/07/2014 12:22 AM

You should be clear that if rated current is 399 A then whether its motor application or any other load application you may not go for 400A MCCB as it can't be able sustain high inrush current.

Also there is no specifications of C or D type in MCCB.

In MCCB there is breaking current which will be decided after calculating fault current.

You Might getting confused between MCB and MCCB.

Register to Reply Score 1 for Good Answer
Power-User
Engineering Fields - Power Engineering - New Member

Join Date: Feb 2011
Location: Pakistan
Posts: 126
#15
In reply to #10

Re: MCCB Types C and D?

04/18/2014 9:04 AM

The information that I am referring to is here, the following. I found it in CR4 old archives. The last line has it (resembles the MCB type C characteristics):

{Reply # 7}:

B the user, electricalexpert65;

Re: MCCB Tripping While Star to Delta Changeover

<stuff deleted>

Selection of MCCB: Now, assuming that the user selects a conventional feeder protection MCCB - the instantaneous release setting in these MCCBs range from 3 In to 9 In. Even with MCCBs with modern Electronic / Numerical Protection Releases, the instantaneous setting range is 6 to 10 In. Thus, there is a chance that the MCCB might trip during switching ON of the motor, due to the inrush current, even if kept at the maximum possible instantaneous setting.

It is to be noted that such spurious tripping might not happen all the times. Depending upon the instant of switching and the residual flux in the motor, if the inrush current is more than the instantaneous setting made in the MCCB, then only it would trip. Otherwise, it wouldn't. Hence, one might hear complaints from the user about this strange "arbitrary" tripping behaviour of the MCCB's during motors starting ("sometime it trips, sometime it doesn't").

To ensure that the MCCB wouldn't trip at all for the above inrush conditions, one must select an MCCB, whose instantaneous release setting is more than the worst case magnetising inrush current, as calculated above. One might opt for a special Motor Protection Type MCCB, whose instantaneous setting is fixed at 12 In.

__________________
--
Register to Reply Off Topic (Score 5)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#11

Re: MCCB Types C and D?

04/07/2014 5:28 AM

The design technique to be applied is called 'co-ordination', and the methodology is all in British Standard 7671.

The usual approach is to use fuses to protect the cable, and a motor overload device to protect the motor.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Associate

Join Date: Apr 2014
Posts: 51
#14

Re: MCCB Types C and D?

04/10/2014 1:26 AM

If you want to know more details about MCB'S then visit at link below:-

http://electrialstandards.blogspot.in/2014/04/mcb-characteristics-and-applications-of.html

Register to Reply
Associate

Join Date: Mar 2014
Location: Mumbai, India
Posts: 25
#30

Re: MCCB Types C and D?

07/31/2014 10:28 AM

a) Somebody referred if 500A then thermal adjustment can be done 0.8-1.0 In (Set at 0,8 In of 630A MCCB), however what we have been taught is that for a motor feeder, MCCB has to be used with only S/C Protection (There should not be any overload protection in MCCB) and Overload relay to be used for Overload protection.
b) When it comes to star delta, yes, issues regarding changeover form star to delta comes in picture when both voltages applied in delta mode and induced EMF of motor may come together and picture can be more damaging
c) Swithgear Manufacturer's publish Type 2 Charts (Proven, Tested with Third Party Certification) and have made life easy for users, why debate on that. Just select HP Rating of Motor (IE1 or IE2) and refer type 2 charts for Selection of Switchgear Components.

Register to Reply
Register to Reply 30 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: