Chiller Efficiency

04/05/2014 4:18 PM

We had a Chiller of 15 tr capacity (water cooled condensor). I want to know the water flow required for the condensor and also for evaporator to get the maximum efficiency Out from the Chiller. Refrigerant used is r 22 , 15 kw motor is connected to the reciprocating compressor.

__________________
When Emotions runs high ,Intellectual wont work
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: Chiller efficiency

04/05/2014 4:27 PM

Roughly speaking 2-3 GPM per ton....

"There are countless design parameters that influence this design issue. Each must be identified and defined in order to accurately make a comparison of 2 versus 3 gpm per ton condenser water flow. No matter how carefully these design parameters are selected, they would never all apply to every installation and any attempt to quantify the impact of each parameter would only confuse the issues. "...

http://www.districtenergy.org/06CampConfProceeding/Track_A/6A1_Liegois%20.pdf

http://www.engineeringtoolbox.com/heat-condenser-evaporator-d_881.html

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: Chiller efficiency

04/05/2014 5:17 PM

This is déjà-vu all over again. The most common rule of thumb I've seen is 3 GPM/TR, but you could do some intersecting-curve balances if enough performance data are available.

Perhaps more to the point in your case is to determine if the refrigerant charge is correct.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3

Re: Chiller efficiency

04/05/2014 5:56 PM

Look at the specifications of the chiller.

I'd think the maker would make the chiller as efficient as they could.

Why do you think you could make it better, when you have little understanding of the process?

Hire someone!

Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#4

Re: Chiller efficiency

04/05/2014 7:43 PM

when you call the manufacturer (eyes rolling)besides chilled water flow rate ask them about CFM parameters for your cooling coils so you move the correct amount of air over them in your quest for maximum efficiency.

Register to Reply
Guru

Join Date: Jun 2008
Location: Oman
Posts: 612
Good Answers: 14
#5

Re: Chiller Efficiency

04/06/2014 12:29 AM

Thumb rule for chiller circuit is 3 GPM per ton and for condenser circuit it is 4 GPM per ton. Efficiency of chiller and cooling tower depends upon many factors. I suggest you to read any good HVAC books and also read the O & M of the plant for its proper operation.

Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member India - Member - New Member

Join Date: Aug 2008
Location: City of destiny, INDIA
Posts: 775
Good Answers: 67
#6

Re: Chiller Efficiency

04/07/2014 4:55 AM

What the O & M Manual say? You will also get tips there for getting maximum efficiency.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#7

Re: Chiller Efficiency

04/07/2014 3:21 PM

What do the commissioning records say?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 7 comments
Copy to Clipboard

Users who posted comments:

Fredski (1); lyn (1); mrswamy (1); pritam (1); PWSlack (1); SolarEagle (1); Tornado (1)