Dear Gents
During Reverse Power trip simulation of diesel Generator ,observed that the KW meter showing negative KW , still Reverse power trip did not activated. The reverse power relay settings on HIMAP is 0.0%, ,5 Sec .
Would appreciate , someone could tell me , the causes of not activating reverse power trip due to Wrong adjustment of Fuel rack.Governor Linkage.
Re: Generator Reverse Power Trip Failure
04/08/2014 3:18 PM
Of course. The tech service department at the equipment manufacturer's will be glad to help you.
Good Answers: 122
04/09/2014 9:31 AM
My WAG would be:
Test set leads not connected properly.
Trip circuit(s) was/are "lifted" / defeated.
Faulty relay.
Improper test sequence.
Reverse Power Relay not "armed".
"Anti-pump" circuit (If present) active.
04/09/2014 11:33 AM
Was the diesel fuel gauge rising during this time?