Anonymous Poster #1

The Role of Copper Tape and Semi Conductor in HT Termination

04/08/2014 10:47 AM

pls. let me know the purpose of copper tape and semi conductor in ht cable termination, the copper tape to be earthed or not in single core 3.3kV cable termination side. our cable is 1Cx500sq.mm 3nos. 3.3kV, CU/SC/XLPE/SC/CUT/PVC/AWA/PVC. Thanks,

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15608
Good Answers: 983
#1

Re: the role of copper tape and semi conductor in ht termination

04/08/2014 11:23 AM

Wow. You are working on a 3.3kV system and you describe a mysterious circuit as a copper tape a semiconductor and the cabling material. I don't even know where to start. I am speachless.

Talk to your job supervisor, union representative or better yet, talk the job engineer about your question. Try not to kill someone.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply
Guru

Join Date: Apr 2012
Posts: 732
Good Answers: 17
#5
In reply to #1

Re: the role of copper tape and semi conductor in ht termination

04/08/2014 3:16 PM

You had enough guts to respond...

...I couldn't even make it there

Their personal situation will sort itself out when the system is commissioned.

__________________
common knowledge...less common than common sense
Reply Score 1 for Off Topic
Anonymous Poster #1
#10
In reply to #5

Re: the role of copper tape and semi conductor in ht termination

04/09/2014 12:52 AM

I am sorry, it seems this forum is only for hitech engineers and experienced proffessionals of minimum 15years of experience and not for beginners or for avarage guys. I am regretting to joined with you, and pls. do understand that no one is hundred percent. if all are 100percent no need of such a forum. and note that there are thousands of members in this forum and only 8people are responded, that means all the rest are not like you or not having any idea about the subject. be proud about what you have god bless you all, i shall come back when i achieve 15years experience insha allah

Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1694
#11
In reply to #10

Re: the role of copper tape and semi conductor in ht termination

04/09/2014 12:58 AM

Bye. See ya in 15 years.

Write if you get work.

Oh, never mind, we won't know who you are, since you posted anonymously.

Reply Score 2 for Off Topic
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#12
In reply to #10

Re: the role of copper tape and semi conductor in ht termination

04/09/2014 7:52 AM

Close the door quietly please.

__________________
The reports of my death are greatly exaggerated.
Reply Score 1 for Off Topic
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#13
In reply to #10

Re: the role of copper tape and semi conductor in ht termination

04/09/2014 8:31 AM

actually in order to join this club we only have a single prerequisite....you have to spell "professional" correctly.other than that anyone is welcome to contribute

Reply Score 1 for Off Topic
Guru

Join Date: Apr 2012
Posts: 732
Good Answers: 17
#14
In reply to #10

Re: the role of copper tape and semi conductor in ht termination

04/09/2014 10:32 AM

__________________
common knowledge...less common than common sense
Reply Score 1 for Off Topic
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#15
In reply to #10

Re: the role of copper tape and semi conductor in ht termination

04/09/2014 3:31 PM

You are really mistaken to assume that in this forum does not entertain questions of freshers . In fact members even give proper answers to non technical people,students and armatures . Then you must be having a feeling why my question is not answered properly. Firstly members here are not very happy with Anonymous posting. Secondly when members feel that you have put up a thread with out understanding the basics.Members really try to pull up the PO to bring out the thread more clearly so that a meaningful answer can be given. Take the case of your thread you have not specified what type of cable you want to terminate and what kind of jointing kit you are using . Unless you specify it correctly can any one give a proper answer.Yes I can understand some of the reply is taunting but you should not have reacted like this . If you do not come again in this forum only you will be missing some good discussions and replies. Better become a member and put more threads and get noticed by other members and that should be the correct spirit.

Reply Score 1 for Good Answer
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#2

Re: the role of copper tape and semi conductor in ht termination

04/08/2014 11:25 AM

heres a hint, the copper is far more conductive than varnished cambric.

Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1694
#3

Re: the role of copper tape and semi conductor in ht termination

04/08/2014 11:35 AM
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#7
In reply to #3

Re: the role of copper tape and semi conductor in ht termination

04/08/2014 7:07 PM

Quite.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#4

Re: the role of copper tape and semi conductor in ht termination

04/08/2014 12:31 PM

Read this cable installation manual, and be sure to heed this warning before proceeding:

"...The information contained herein is intended for evaluation and use by technically skilled and appropriately trained persons... You should always consult a trained professional for the most current industry practices and procedures unique to your application...", in other words "Don't attempt this yourself!!!"

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Reply
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#6

Re: The Role of Copper Tape and Semi Conductor in HT Termination

04/08/2014 4:01 PM

Cable jointing is a specialised job to be carried out by a trained and experienced jointer.Consult a reputed jointer and purchase the correct cable jointing kit as per his advice and get the jointing done by him. If you want more knowledge about cable jointing , attend a training course which is conducted by the reputed cable joint kit manufacturers like Raychem India or CCI (Cable Corporation of India) . You may get all your doubts cleared by them .You do not seem to have even the basic idea of various types of Cables and cable jointing kits.The manufacturers give all the technical information about their products and you can choose the correct material as per your requirement from local Electrical market.

Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8

Re: The Role of Copper Tape and Semi Conductor in HT Termination

04/08/2014 7:09 PM

Is there truly no-one locally who could answer the question? Like a HT Electrical Jointer, perhaps?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#9

Re: The Role of Copper Tape and Semi Conductor in HT Termination

04/08/2014 8:32 PM

Get the termination of the screen wrong and there's going to be a big bang. Mind you 3.3KV isn't a difficult one to do. Once you get to 11KV and above the jointers skill really comes in to its own.

__________________
The reports of my death are greatly exaggerated.
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#16

Re: The Role of Copper Tape and Semi Conductor in HT Termination

04/10/2014 11:21 AM

Er, why can't a local HT Electrician say, without reference to this forum?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15608
Good Answers: 983
#17
In reply to #16

Re: The Role of Copper Tape and Semi Conductor in HT Termination

04/10/2014 4:43 PM

Because we are not dealing with a qualified HT Electrician. The OP is closer to Sweeney Todd than they are to Dr. William James Mayo.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply
Reply to Forum Thread 17 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); Fredski (2); lyn (2); PWSlack (3); RAMConsult (1); redfred (2); The.Tinkerer (2); TonyS (2); V.I.Abraham (2)

Previous in Forum: Turning Whatever into Electricity   Next in Forum: Generator Reverse Power Trip Failure